APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-26 03:01 AM . Last Modified: 2024-01-31 02:57 AM
In the Data Log, TIambF (ambient temperature probe) ranges correctly from 69 to 73, but TupsF (internal temp) ranges from 626.0 to 657.5.
UPS > Status > Internal Temperature correctly displays 94.55°F.
Administration > General > Preferences > Temperature Scale is set to Fahrenheit °F.
Can anyone explain or help me with this discrepancy?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-26 03:02 AM . Last Modified: 2024-01-31 02:56 AM
i will have to go ahead and investigate and possibly log a bug on the issue. give me a day or so to do that but if it is not too much trouble, can you get me one last copy of the event.txt, data.txt, and config.ini from the latest firmware version? that way when i look into it, the files indicate the latest firmware. a screenshot of the value in the web interface may not hurt either.
thanks!!
EDIT - my unit was doing that here so i just got the files from that. to be completely honest with you, i am not sure if there will be any additional NMC firmware released for this unit. the embedded NMC is a mini AP9617 and that was recently discontinued because we now have NMC2. it'd be up to the product manager for the product whether or not we would address this in a future revision for that particular UPS. i notified the product manager about this issue with the NMC firmware.
i did log it as an issue though for you.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-26 03:01 AM . Last Modified: 2024-01-31 02:57 AM
In the Data Log, TIambF (ambient temperature probe) ranges correctly from 69 to 73, but TupsF (internal temp) ranges from 626.0 to 657.5.
UPS > Status > Internal Temperature correctly displays 94.55°F.
Administration > General > Preferences > Temperature Scale is set to Fahrenheit °F.
Can anyone explain or help me with this discrepancy?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-26 03:01 AM . Last Modified: 2024-01-31 02:57 AM
no its not. i notified the appropriate people responsible for this unit at APC so they are now aware of the issue.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-26 03:01 AM . Last Modified: 2024-01-31 02:57 AM
the value in the data log is the ambient temperature from the temperature probe connected to the back of your S20BLK.
the value you see under UPS->Status section is the internal temperature of the S20BLK AV UPS itself.
Under the Environment Tab is where you'd see the temperature probe readings that you are seeing from the data log.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-26 03:02 AM . Last Modified: 2024-01-31 02:57 AM
Internal temperatures in Fahrenheit are 94.55, but are being logged as 657.5, while ambient temps are being logged correctly.
I've attached the log file.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-26 03:02 AM . Last Modified: 2024-01-31 02:57 AM
oh LOL
sorry, i missed it in the first post. i apologize. i see what you mean now.
can you tell me what firmware you have on that NMC? it will be under the administration->general->About section. you should see an AOS version and APP version. 3.x.x. please let me know what you see there. in the meantime, i did not see any known issues with this or anything. another thing i'd like to know from that About section is the uptime of the NMC. I wonder if it does this when it has been up after a while.
thanks!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-26 03:02 AM . Last Modified: 2024-01-31 02:57 AM
Hardware Factory
Serial Number: QB1029......
Hardware Revision: 04
Manufacture Date: 09/18/2010
Management Uptime: 0 Days 22 Hours 34 Minutes
Application Module
Name: sumx
Version: v3.5.8
Date: 11/05/2008
Time: 15:08:57
APC OS (AOS)
Name: aos
Version: v3.6.1
Date: 08/13/2008
Time: 18:49:49
About UPS
Model: S20 AV UPS
Serial Number: QB1029......
Firmware Revision: 750.G1 .D
Manufacture Date: 09/18/10
Unit has been up since installation 4 days ago.
I considered firmware, but assumed as long as this product has been out, combined with its recent manufacture, that an issue like this would have cropped up and been resolved long ago.
Attached new Data Log that is easier to read.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-26 03:02 AM . Last Modified: 2024-01-31 02:57 AM
you'd think.
for some reason, you are one firmware version behind.
can you try to upgrade to SFSUMX372 from the software and firmware section of apc.com and check that version? you can start from this page and choose firmware upgrades - network management card and choose the SFSUMX372 to download -> http://www.apc.com/tools/download/index.cfm
upgrade instructions can be found here: http://nam-en.apc.com/app/answers/detail/a_id/768
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-26 03:02 AM . Last Modified: 2024-01-31 02:56 AM
After the firmware upgrade, which was both painless and successful, I rebooted the UPS, only to discover that the problem is not corrected.
So what's next?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-26 03:02 AM . Last Modified: 2024-01-31 02:56 AM
i will have to go ahead and investigate and possibly log a bug on the issue. give me a day or so to do that but if it is not too much trouble, can you get me one last copy of the event.txt, data.txt, and config.ini from the latest firmware version? that way when i look into it, the files indicate the latest firmware. a screenshot of the value in the web interface may not hurt either.
thanks!!
EDIT - my unit was doing that here so i just got the files from that. to be completely honest with you, i am not sure if there will be any additional NMC firmware released for this unit. the embedded NMC is a mini AP9617 and that was recently discontinued because we now have NMC2. it'd be up to the product manager for the product whether or not we would address this in a future revision for that particular UPS. i notified the product manager about this issue with the NMC firmware.
i did log it as an issue though for you.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-26 03:02 AM . Last Modified: 2024-01-31 02:56 AM
So I should keep checking for a firmware update for the AP9617 NMC?
Thanks for your help [i picKed a winna|http://www.apc-forums.com/profile.jspa?userID=2541].
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-26 03:02 AM . Last Modified: 2024-01-31 02:56 AM
well, i got people talking about investigating an update. so i cant say for sure what will happen but you can check once in a while. feel free to PM me if you are looking for an update incase i forget to come back and inform you about one.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.