Runtime Calibration Smart UPS RT 3000 XL
Send InviteCancel
Posted: 2022-01-2011:16 AM
I have placed a new battery pack in the UPS. But whatever I do I do not get the UPS to re-calibrate the runtime.
1. Via the comm port i have several times tried "a Runtime Calibration" with a steady 35% load. However all times the calibration ends prematurely with "Bad Input Voltage", though I am sure the input voltage is almost not changing at all.
2. I have tried manually by removing the input power and let the UPS run to 0%, with a steady 35% load. Also no result.
Both times after first charging the UPS fully.
See the photos attached of the menu choices and results.
What can I do to have the UPS calibrate the runtime correctly again?