Runtime 1 Minute

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Runtime 1 Minute
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 06:05 AM . Last Modified: ‎2024-03-19 12:21 AM

0 Likes
10
1705
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 06:05 AM . Last Modified: ‎2024-03-19 12:21 AM

Runtime 1 Minute

Hello.  I have a Symmetra 40K that recently started showing 1 minute runtime.  It has 16 batteries which are all good.  There are 4 power modules which all show On & OK in the GUI.  The Output VA at n+0 is L1=044   L2=043  and L3=024.  I was wondering if a self-test oor Run-time calibration will help the UPS to properly reflect its runtime?  Or am I missing some statistic that can shed light on the 1 minute runtime?

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 06:06 AM . Last Modified: ‎2024-03-19 12:21 AM

0 Likes
0
1705
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 06:06 AM . Last Modified: ‎2024-03-19 12:21 AM

Thank you.

I definitely think we have a battery problem, perhaps one bad pair or module - I am not sure. I think you'll need service unfortunately or someone to come check these batteries. Let me know if you need help with how to go about that.

I looked in the data log. On March 5, the UPS did a self test at about 9:30 and the entry for the same time in the data log indicates a large battery capacity drop - from 100% to 55% which is certainly not normal at all.

Also, on March 11 (yesterday), did you remove or reseat a battery module? I see an entry in the log indicating number of batteries decreased/increased which is indicative of someone removing/reinstalling - if not, this is also an indicator of battery problems. At this time, the battery capacity also dropped 20% and also charged back up slowly.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 10
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 06:05 AM . Last Modified: ‎2024-03-19 12:21 AM

0 Likes
0
1705
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 06:05 AM . Last Modified: ‎2024-03-19 12:21 AM

How old are the 16 batteries?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 06:05 AM . Last Modified: ‎2024-03-19 12:21 AM

0 Likes
0
1705
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 06:05 AM . Last Modified: ‎2024-03-19 12:21 AM

Well the batteries have been in the UPS for about 8 months now.  On the front of each battery it says "Batteries Charged 6-17-13."

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 06:05 AM . Last Modified: ‎2024-03-19 12:21 AM

0 Likes
0
1705
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 06:05 AM . Last Modified: ‎2024-03-19 12:21 AM

Hello again. Upon researching, this is normally indicative of batteries that need to be replaced. It is also likely that the UPS has recently gone through a deep/complete discharge - is that the case? This is the only way the runtime would adjust to 1 minute.

My other question is - when did the runtime start reporting as 1 minute? By reading what you said, I thought the development was recent, like the last few days but I just want to verify specifically. Since they are only 8 months old, I'd be a little concerned and suggest that a Field Service Engineer inspect the batteries to understand if for some reason, they have failed prematurely and 1 minute is accurate or if a runtime calibration is worth it.

Depending on what you want to do, you could potentially try a runtime calibration on the UPS and see how long it actually runs on battery. By design, the Runtime Calibration should abort if there are any larger problems with the UPS.

We could also review your UPS Network Management Card logs if you want and have them available. Instructions here -> How can I download Event, Data, Configuration, and Debug files from my Network Management Card? | FA...

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 06:05 AM . Last Modified: ‎2024-03-19 12:21 AM

0 Likes
0
1705
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 06:05 AM . Last Modified: ‎2024-03-19 12:21 AM

I'm not exactly sure when the runtime started reporting 1 minute.  I reviewed the event logs and didn't see anything that stood out as to why the runtime went to 1 minute.  So Scheiner Electric reviewing event/data logs and debug files is a free service you'll provide to customers with your equipment?

I'm going to go ahead and capture the logs.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 06:06 AM . Last Modified: ‎2024-03-19 12:21 AM

0 Likes
0
1705
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 06:06 AM . Last Modified: ‎2024-03-19 12:21 AM

Yes - we can definitely look at your Network Management Card logs for free - I might not be able to give an answer based on them but it is certainly worth a look. We will also provide free phone tech support regardless of service or warranty status. The only time that comes into play is for parts or Field Service Engineer dispatch. We also offer a "Time and Materials" if you required someone out there and wanted to pay out of pocket for a Field Service dispatch.

For your situation, I only need config.ini, data.txt, and event.txt. Debug files are not needed.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 06:06 AM . Last Modified: ‎2024-03-19 12:21 AM

0 Likes
0
1705
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 06:06 AM . Last Modified: ‎2024-03-19 12:21 AM

Okay.  I have the files needed.  Will I send them directly to you or will I submit them via Schneider's Support Center?  Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 06:06 AM . Last Modified: ‎2024-03-19 12:21 AM

0 Likes
0
1705
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 06:06 AM . Last Modified: ‎2024-03-19 12:21 AM

You can attach them here. When typing your reply, make sure you are not replying from your "inbox" rather than going to the full view of the thread and select "use advanced editor" to attach the files. You can remove any private info like IP addresses, etc. I just want to see the UPS events/data log and any UPS settings.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 06:06 AM . Last Modified: ‎2024-03-19 12:21 AM

0 Likes
0
1705
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 06:06 AM . Last Modified: ‎2024-03-19 12:21 AM

Angela

The files are attached.  Thanks.

Attachments
event.txt.zip
config.ini.zip
data.txt.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 06:06 AM . Last Modified: ‎2024-03-19 12:21 AM

0 Likes
0
1706
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 06:06 AM . Last Modified: ‎2024-03-19 12:21 AM

Thank you.

I definitely think we have a battery problem, perhaps one bad pair or module - I am not sure. I think you'll need service unfortunately or someone to come check these batteries. Let me know if you need help with how to go about that.

I looked in the data log. On March 5, the UPS did a self test at about 9:30 and the entry for the same time in the data log indicates a large battery capacity drop - from 100% to 55% which is certainly not normal at all.

Also, on March 11 (yesterday), did you remove or reseat a battery module? I see an entry in the log indicating number of batteries decreased/increased which is indicative of someone removing/reinstalling - if not, this is also an indicator of battery problems. At this time, the battery capacity also dropped 20% and also charged back up slowly.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 06:06 AM . Last Modified: ‎2024-03-19 12:21 AM

0 Likes
0
1705
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 06:06 AM . Last Modified: ‎2024-03-19 12:21 AM

Thank you so much for reviewing the logs.  Yes, yesterday I did take a power module out to see if there was any other indication of the battery service date.  I'll turn to our maintenance provider to see about a field rep coming out.  In the beginning I thought it may be something I could fix since the UPS is on emergency power anyway.  Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore