Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

Right Sizing of UPS

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Right Sizing of UPS
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Javier_RA_apc
Crewman Javier_RA_apc
Crewman

Posted: ‎2021-06-28 08:49 AM . Last Modified: ‎2024-03-17 11:47 PM

0 Likes
2
656
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:49 AM . Last Modified: ‎2024-03-17 11:47 PM

Right Sizing of UPS

Hi all,

I've been introduced with a really small installation where a SMX3000HV + APC9630 was installed.

Watching at the UPS status, I see that the max Output Watts has been 13%, and Output Efficiency is always 'load too low'.

There's an added issue with the space where the rack is installed, where the temperature represents an issue, there's no AC unit and the air flow does not seem to be enough, especially during the 'warm' months of summer!

I'm considering switching to a lower model, need to be short depth (again because of the rack location), so I was thinking of a SMX2200HVNC or a SMX1500RMI2UNC (BPUs are also much lower the smaller the model is).

Now the question:

SMX1500RMI2UNC output is 1.2KWatts
SMX3000HV output is 2.7KWatts
If my current 'Output Watts' is 13%, am I doing right these calculations?

Current output = 2,7*100/13 = 0,35KWatts
Output in 1500 = 0,35*100/1,2 = 29%
My 'Current Output' with SMX1500RMI2UNC will be aprox. 30%, which still leaves room for growth. And will be saving 2U and lots of BPUs (184 vs 133 BTU/h) 🙂

Looking forward to your comments, observations and corrections!

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Javier_RA_apc
Crewman Javier_RA_apc
Crewman

Posted: ‎2021-06-28 08:50 AM . Last Modified: ‎2024-03-17 11:47 PM

0 Likes
0
656
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:50 AM . Last Modified: ‎2024-03-17 11:47 PM

On 9/9/2018 7:40 PM, voidstar said:

Make sure you're okay with reduced runtime (~35 minutes) or add batteries to compensate.

Most of the times 35 min should be fine, considering we don't expect working if there's a larger outage. Also adding external batteries would bring more BPUs, and one of the things I want to alleviate is the heat in the rack.

Thank you for your response!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 08:50 AM . Last Modified: ‎2024-03-17 11:47 PM

0 Likes
0
656
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:50 AM . Last Modified: ‎2024-03-17 11:47 PM

Calculations seem good. Just a note: load-too-low isn't an indicator of a problem; rather it's just why the UPS doesn't report efficiency. Getting the load up to 30% will help with detecting bad batteries during self-test and calibrating the runtime estimation during discharges. Make sure you're okay with reduced runtime (~35 minutes) or add batteries to compensate.

Reply

Link copied. Please paste this link to share this article on your social media post.

Javier_RA_apc
Crewman Javier_RA_apc
Crewman

Posted: ‎2021-06-28 08:50 AM . Last Modified: ‎2024-03-17 11:47 PM

0 Likes
0
657
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:50 AM . Last Modified: ‎2024-03-17 11:47 PM

On 9/9/2018 7:40 PM, voidstar said:

Make sure you're okay with reduced runtime (~35 minutes) or add batteries to compensate.

Most of the times 35 min should be fine, considering we don't expect working if there's a larger outage. Also adding external batteries would bring more BPUs, and one of the things I want to alleviate is the heat in the rack.

Thank you for your response!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of