Novice question: I bought a used Smart-UPS 2200XL several years ago thinking it might be useful. But it appears to require 3-phase power. Is this correct?
I'm in Australia, so it's 230 volt.
Regards,
David
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:01 AM . Last Modified: 2024-03-18 02:55 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:01 AM . Last Modified: 2024-03-18 02:55 AM
Thanks for the info. It has indeed been resolved, and the future for the device is that of the proverbial boat anchor![]()
Regards,
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:01 AM . Last Modified: 2024-03-18 02:55 AM
Hi David, I'm sure you've already resolved this, but just in case you haven't, the APC Smart UPS 2200VA and 3000VA models in Australia require a dedicated 15Amp 230V Single Phase circuit.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:01 AM . Last Modified: 2024-03-18 02:55 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:01 AM . Last Modified: 2024-03-18 02:55 AM
Thanks for the info. It has indeed been resolved, and the future for the device is that of the proverbial boat anchor![]()
Regards,