Required software to shutdown multiple servers with one UPS using USB cable

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Required software to shutdown multiple servers with one UPS using USB cable
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:57 AM . Last Modified: ‎2024-03-07 11:44 PM

0 Likes
4
2070
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:57 AM . Last Modified: ‎2024-03-07 11:44 PM

Required software to shutdown multiple servers with one UPS using USB cable

I have used APC equipment off and on for the past 10 years or so, but I must admit I'm not as familiar with the software as I used to be. I could've swore that APC software would allow you to shutdown any number of servers using only one UPS regardless of whether it had a network management card or not. But last time I went to set this up I was unable to install the software on any server that was not directly connected to the UPS (USB or Serial). It would error out saying it couldn't find any compatible UPS device. The UPS model in question is a SUA3000RM2U (Smart-UPS 30000) using a USB cable, no optional cards installed.

Is this configuration possible? Can I shutdown multiple computers/servers in case of power failure using only one UPS which is only managed via USB cable to a deidcated server? Or is the optional Network Management Card required? If it is possible, which version of the software do I need?

Thanks.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:57 AM . Last Modified: ‎2024-03-07 11:44 PM

0 Likes
0
2069
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:57 AM . Last Modified: ‎2024-03-07 11:44 PM

I have used APC equipment off and on for the past 10 years or so, but I must admit I'm not as familiar with the software as I used to be. I could've swore that APC software would allow you to shutdown any number of servers using only one UPS regardless of whether it had a network management card or not. But last time I went to set this up I was unable to install the software on any server that was not directly connected to the UPS (USB or Serial). It would error out saying it couldn't find any compatible UPS device. The UPS model in question is a SUA3000RM2U (Smart-UPS 30000) using a USB cable, no optional cards installed.

Is this configuration possible? Can I shutdown multiple computers/servers in case of power failure using only one UPS which is only managed via USB cable to a deidcated server? Or is the optional Network Management Card required? If it is possible, which version of the software do I need?

Thanks.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-30 06:57 AM . Last Modified: ‎2024-03-07 11:44 PM

0 Likes
0
2069
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:57 AM . Last Modified: ‎2024-03-07 11:44 PM

Phillip,

Unfortunately, you can not use both the Serial and USB cables simultaneously. It means that you can shutdown or manage only one Server at a time by using the cables that shipped with the UPS.

In order to shutdown two or multiple servers from a single Smart UPS, you need to purchase an additional accessory. Click here to know how can you monitor multiple servers with PowerChute software when using one Smart-UPS.

I hope that this helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 06:57 AM . Last Modified: ‎2024-03-07 11:44 PM

0 Likes
0
2069
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:57 AM . Last Modified: ‎2024-03-07 11:44 PM

Slizzy,

In order to achieve what you are looking to do, you can go about this in one of three ways.

1. Write a batch command file so that when your primary machine is about to begin its shutdown, it will send a command to the other machines to also begin a shutdown. Please note that APC provides the means for, but does not fully support, command scripts.

2. In order to shut down either 2 or up to 8 devices, you would need to purchase either a Serial Interface Expander (for 2 more serial ports for a total of 3), or a Share-UPS Interface Expander (for up to 8). Both setups would allow you to still utilize your primary smart-signaling port for advanced communication with the UPS. You would at that point install PowerChute Business Edition Agents on all communicating devices, and then the Server/Console portions on your centralized monitoring system. Please keep in mind that with PCBE Basic, you can only monitor a maximum of 5 machines with one instance of PCBE Server. When installing the Agent on each of the simple signaling ports (any of the other 7 on the Share-UPS), you will want to select "Interface Expander Basic" and the appropriate communication port to ensure that the software can communicate effectively with the UPS.

3. The final option is to install a Network Management Card (AP9617/8/9) into the SmartSlot of the UPS. This will allow you to remove all serial communication cables from your setup, and everything will be run over the network. You would install PowerChute Network Shutdown agents on each of the machines that are using the UPS as a physical power source. You would have to configure the Network card with TCP/IP settings prior to doing this. When you install the PCNS agent you will be required to enter the IP address of the pre-configured Network card so that it can verify communication. The only downside to this is that in this setup, it is assumed that your major network components do not drop or fail in response to a blackout or power problem. Most customers usually have their switch for this setup attached to the UPS for a power source just to ensure communication in the event the UPS has to transfer to battery.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:57 AM . Last Modified: ‎2024-03-07 11:44 PM

0 Likes
0
2069
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:57 AM . Last Modified: ‎2024-03-07 11:44 PM

Thanks for your advice. I'll have to go ahead and get the NMC for my customer. Scripting would be a good alternative but I'd rather spend the extra money to have a fully supported configuration and peace of mind. I've used the Share-UPS extender in the past but I thought it was done away with after the release of their Network Shutdown software. I thought you could use PNS to shutdown any machine when the UPS was managed by only one server using a USB/Serial connection. But now that I think about it this is probably the first time I've tried installing PNS in an environment where I didn't have a NMC.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:57 AM . Last Modified: ‎2024-03-07 11:44 PM

0 Likes
0
2070
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:57 AM . Last Modified: ‎2024-03-07 11:44 PM

I have used APC equipment off and on for the past 10 years or so, but I must admit I'm not as familiar with the software as I used to be. I could've swore that APC software would allow you to shutdown any number of servers using only one UPS regardless of whether it had a network management card or not. But last time I went to set this up I was unable to install the software on any server that was not directly connected to the UPS (USB or Serial). It would error out saying it couldn't find any compatible UPS device. The UPS model in question is a SUA3000RM2U (Smart-UPS 30000) using a USB cable, no optional cards installed.

Is this configuration possible? Can I shutdown multiple computers/servers in case of power failure using only one UPS which is only managed via USB cable to a deidcated server? Or is the optional Network Management Card required? If it is possible, which version of the software do I need?

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore