Repeated Smart UPS 2200 and 3000XL failures

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Repeated Smart UPS 2200 and 3000XL failures
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
138
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:45 PM . Last Modified: ‎2024-03-14 11:45 PM

0 Likes
4
1255
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:45 PM . Last Modified: ‎2024-03-14 11:45 PM

Repeated Smart UPS 2200 and 3000XL failures

I am the Site Manager of a remote astronomical observatory. Included in our array of many different models of APC UPS's are four 3000XL's and one 2200 rack mounted units. In the last few years, 4 out of 5 of these have gone belly up - one just today - and all due to the same basic problem similar to what is stated in another thread. The basic symptom is that at some point the unit quits working, never to be switched on again. When you do try to power it up, you get a short beep, hear the relays switch on for a moment, and the LEDs flicker. In each case, when we opened the units up, we found almost the exact same destroyed components on the motherboard:

One or more complete rows of the power transistors (8 per row) attached to the 4 large heat sinks are completely fried (melted);
The nearby capacitors in these rows are usually melted as well;
R38, R43, and R166 resistors are fried;
and one or more of the following transistors are physically blown apart: Q29,Q30, Q31,Q32, Q33.

Obviously since 4 out of 5 of our units failed in the same manner, there is a serious design flaw here! Be that as it may, does anyone have available a schematic for the 3000XL? All of these unites are now out of warranty and presumably I can repair these myself by replacing components - only using higher load ratings this time. I can go into it blind by ordering similar parts, but it would be a lot easier if I had the basic electronic road map to go by . . . .

Oh and by the way, if you happen to be around at the time of "meltdown," you will smell the results.


Thanks.

Message was edited by: gratingengine

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:45 PM . Last Modified: ‎2024-03-14 11:44 PM

0 Likes
0
1255
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:45 PM . Last Modified: ‎2024-03-14 11:44 PM

Hi all, when I used to service electronics there was some successes replacing these power mosfets (RFPxxxx's etc) but these days a suspect unit that has this level of failure is sent to recycling as usually the connected equipment and the tasks it is providing are much more expensive than a replacement UPS with warranty, given that the suspect UPS might fail again.

So I am not much help, one thing I seem to recall is that the UPS is at risk of power inverter catastrophic failure when the batteries are weak, voltage drops and current spikes.

Schematics are proprietary and not available.


:-( My avatar passed away last Saturday, 01:00GMT, while on duty, we really miss her.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:45 PM . Last Modified: ‎2024-03-14 11:45 PM

0 Likes
0
1255
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:45 PM . Last Modified: ‎2024-03-14 11:45 PM

Just wanted to chime in and say we just had a SU2200XLNET fail similar to the OP's description.  I'm guessing the unit is 10-15 years old, S/N WS9939018786

At first I thought it was just Q33 that was blown apart, but upon further inspection, 3 of the 4 rows of heat sinked power transistors were blown open.

Data points: The UPS had been regulating a utility overvoltage condition for the past few days (this is quite common with our local utility), and the batteries were approaching 2 years of service (possibly weak battery at that point, we usually replace them at the 2 year mark)

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-28 09:45 PM . Last Modified: ‎2024-03-14 11:44 PM

0 Likes
0
1255
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:45 PM . Last Modified: ‎2024-03-14 11:44 PM

Can you provide the exact model #s and serial #s from the units?

Additionally, can you describe the load that is attached to each of the units and expand on the environment that the units are used in (input power, temperature, plug and receptacle types, etc.)?

Did you ever have any of our PowerChute software installed or a Network Management Card so that we can observe logs? All of this information will help with finding out what the issue was with the failures you have described.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:45 PM . Last Modified: ‎2024-03-14 11:44 PM

0 Likes
0
1255
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:45 PM . Last Modified: ‎2024-03-14 11:44 PM

I was just about to post with the same type of problem that I have with a Smart UPS 2200. The model number is SUA2200 and the S/N is JS0544029315. The unit went out of warranty in 2007. The end user told me that it just started smoking one day, so they unplugged it and asked me to see if I could do anything to fix it. I opened it up and found 7 of the 12 power transistors burned beyond recognition. I haven't noticed any other burned components, but then I haven't cleaned the board yet to see what lies under the black residue left by the smoke.

I was wondering if anyone has had any success fixing this type of failure, and if so, I was wondering if all of the power transistors are the same P/N. Any info would be appreciated.

slinger

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:45 PM . Last Modified: ‎2024-03-14 11:44 PM

0 Likes
0
1256
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:45 PM . Last Modified: ‎2024-03-14 11:44 PM

Hi all, when I used to service electronics there was some successes replacing these power mosfets (RFPxxxx's etc) but these days a suspect unit that has this level of failure is sent to recycling as usually the connected equipment and the tasks it is providing are much more expensive than a replacement UPS with warranty, given that the suspect UPS might fail again.

So I am not much help, one thing I seem to recall is that the UPS is at risk of power inverter catastrophic failure when the batteries are weak, voltage drops and current spikes.

Schematics are proprietary and not available.


:-( My avatar passed away last Saturday, 01:00GMT, while on duty, we really miss her.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore