Regarding Power Threshold Alert on PDU APC AP8853

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Regarding Power Threshold Alert on PDU APC AP8853
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Related Products
product field
Schneider Electric
NetShelter Rack PDU Accessories
product field
Schneider Electric
APC Home Solutions

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
EArohitsingh
Crewman EArohitsingh
Crewman

Posted: ‎2024-08-19 12:46 AM

0 Likes
1
1326
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-19 12:46 AM

Regarding Power Threshold Alert on PDU APC AP8853

Hi.

 

I was using APC AP8853. Is there any way to 

  • check and notify via email if power utilization of PDU exceeds certain threshold? If yes, what steps should I follow?
  • check and notify via email if power utilization per socket of PDU exceeds certain threshold? If yes, what steps should I follow?


Any help would be beneficial. Thanks! 

 

Moreover, if there is any better and smarter alternative to APC AP8853 in industry as per latest trends, then please let us know.

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
  • Tags:
  • alert
  • english
  • notification
  • pdu
  • power
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
dpierce4776
Lt. Commander dpierce4776
Lt. Commander

Posted: ‎2024-08-20 06:13 AM

0 Likes
0
1280
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-20 06:13 AM

To configure load thresholds
1. To configure load thresholds for the device, phases, or banks, make a selection from the
Configuration > RPDU > Device and Phase and Bank drop-down menu. To configure load
thresholds for outlets, click Configuration and then click an outlet.
2. Set Overload Alarm, Near Overload Warning, and Low Load Warning thresholds. You
can specify thresholds to one decimal point.
3. Click Apply to save your settings.

 

You will also need to set up your email notifications

Use Simple Mail Transfer Protocol (SMTP) to send email to up to four recipients when an event
occurs. To use the email feature, you must define the following settings:
• The IP addresses of the primary and, optionally, the secondary Domain Name System (DNS)
servers.
• The IP address or DNS name for the SMTP Server and From Address.
• The email addresses for a maximum of four recipients.
• You can use the To Address setting of the recipients option to send email to a text-based
screen.
Path: Configuration > Notification > Email > Server
This screen lists your primary and secondary DNS servers and displays the following fields:
From Address: The contents of the From field in email messages sent by the RPDU:
• In the format user@ [IP_address] (if an IP address is specified as Local SMTP Server)
• In the format user@domain (if DNS is configured and the DNS name is specified as Local
SMTP Server) in the email messages.
NOTE: The local SMTP server may require that you use a valid user account on the server for
this setting. See the server documentation.
SMTP Server: The IPv4/ IPv6 address or DNS name of the local SMTP server.
NOTE: This definition is required only when the SMTP server is set to Local.
Port: The SMTP port number, with a default of 25. The range is 25, 465, 587, 2525, 5000 to
32768.
Authentication: Enable this if the SMTP server requires authentication.
User Name, Password, and Confirm Password: If your mail server requires authentication,
enter your user name and password here. This performs a simple authentication, not SSL/TLS.
Use SSL/TLS: Select when encryption is used.
• Never: The SMTP server does not require nor support encryption.
• If Supported: The SMTP server advertises support for STARTTLS but doesn't require the
connection to be encrypted. The STARTTLS command is sent after the advertisement is given.
• Always: The SMTP server requires the STARTTLS command to be sent on connection to it.
• Implicitly: The SMTP server only accepts connections that begin encrypted. No STARTTLS
message is sent to the server.
Require CA Root Certificate: This should only be enabled if the security policy of your
organization does not allow for implicit trust of SSL/TLS connections. If this is enabled, a valid root
CA certificate must be loaded onto the RPDU for encrypted emails to be sent.
File Name: This field is dependent on the root CA certificates installed on the RPDU and whether
or not a root CA certificate is required.
Metered Rack PDU AP88•• User Guide
124 990-5568R-001
Path: Configuration > Notification > Email > Recipients
Specify up to four email recipients. Click on a name to configure the settings.
Generation: Enables (default) or disables sending email to the recipient.
To Address: The user and domain names of the recipient. To use email for paging, use the email
address for the recipient’s pager gateway account (for example, myacct100@skytel.com). The
pager gateway will generate the page.
To bypass the DNS lookup of the IP address of the mail server, use the IP address in brackets
instead of the email domain name, e.g., use jsmith@[xxx.xxx.x.xxx] instead of
jsmith@company.com. This is useful when DNS lookups are not working correctly.
Language: The language which the email notification will be sent in. This is dependent on the
installed language pack (if applicable).
Port: The SMTP port number, with a default of 25. The range is 25, 465, 587, 2525, 5000 to
32768.
Format: The long format contains name, location, contact, IP address, serial number of the
device, date and time, event code, and event description. The short format provides only the event
description.
Server: Select one of the following methods for routing email:
• Local: This is through the site-local SMTP server. This recommended setting ensures that the
email is sent using the site-local SMTP server. Choosing this setting limits delays and network
outages and retries sending email for many hours. When choosing the Local setting you must
also enable forwarding at the SMTP server of your device and set up a special external email
account to receive the forwarded email. Check with your SMTP server administrator before
making these changes.
• Recipient: This is the SMTP server of the recipient. The RPDU performs an MX record look-up
on the recipients email address and uses that as its SMTP server. The email is only sent once
so it could easily be lost.
• Custom: This setting enables each email recipient to have its own server settings. These
settings are independent of the settings given under “SMTP Server” above.
Path: Configuration > Notification > Email > SSL Certificates
Load a mail SSL/TLS certificate on the Rack PDU for greater security. The file must have an
extension of .crt or .cer. Up to five files can be loaded at any given time.
When installed, the certificate details also display here. An invalid certificate will display “n/a” for all
fields except File Name.
Certificates can be deleted using this screen. Any email recipients using the certificate should be
manually modified to remove reference to this certificate.
Path: Configuration > Notification > Email > Test
Send a test message to a configured recipient.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore