Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 01:19 AM . Last Modified: 2024-03-19 02:28 AM
Dear All
Based on electrical characteristics of UPS Galaxy 5000 - 60 KVA, load current is about 87A but in installation manual section 2.4 recommended downstream protection is 20A and 32A circuit breaker.(see two attached image)
Can we use a circuit breaker in about 80A?
please guide us.
Best regards,
Tohidi
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 01:19 AM . Last Modified: 2024-03-19 02:28 AM
Dear Angela,
Thank you for your reply. It was useful.
Now I have another question. Our UPS is Galaxy 5000 - 60 KVA and we have only one load with 70A.
Can we use one output breaker with 80A (for example NS80H MA 80A schneider compact circuit breaker)?
Best regards,
Tohidi
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 01:19 AM . Last Modified: 2024-03-19 02:28 AM
Hello,
I asked our EMEA support on this. Here is what I received:
I don't see any issue with an 80A circuit Breaker so long as they use 35mm² Cable. That would comply with European norms.
The 20A and 32A circuit breaker seems to refer to the largest MCB on the sub-circuits.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 01:19 AM . Last Modified: 2024-03-19 02:28 AM
Dear Angela
Thank you for your reply.
60 KVA UPS can provide 87A in output.
Why we can not use circuit breaker more than 20A and 32A.
Best regards,
Tohidi
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 01:19 AM . Last Modified: 2024-03-19 02:28 AM
Hi,
Here is some further information I can share:
When we talk about circuit breaker more than 20A and 32A., we are talking about the sub-circuits. We make this recommendation to avoid having the UPS going into bypass just because of a fault on one circuit. The main output breaker can be higher as long as there is sufficient discrimination.
You will find further information in this link:
http://www2.schneider-electric.com/documents/technical-publications/en/shared/electrical-engineering...
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 01:19 AM . Last Modified: 2024-03-19 02:28 AM
Dear Angela,
Thank you for your reply. It was useful.
Now I have another question. Our UPS is Galaxy 5000 - 60 KVA and we have only one load with 70A.
Can we use one output breaker with 80A (for example NS80H MA 80A schneider compact circuit breaker)?
Best regards,
Tohidi
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.