Recommended Placement of UPS Temperature Sensors

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Recommended Placement of UPS Temperature Sensors
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 02:26 AM . Last Modified: ‎2024-03-05 11:22 PM

0 Likes
2
3059
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:26 AM . Last Modified: ‎2024-03-05 11:22 PM

Recommended Placement of UPS Temperature Sensors

Hi All,

Just wondering if anyone has any experience or recommendation on where to place our UPS temperature sensors. We just bought a APC 9631 network management card with the environmental sensor capability so we can configure PowerChute for a temp based shutdown.

Our datacenter looks like this:

Two rows of racks.

The back row has a Symmetra PX 40K UPS and three battery cabinets.
The front row has three IBM server racks with two APC In-Row A/C cooling racks in between.

So basically we have a cool aisle up front and then a hot aisle between the two rows of racks. Where would you recommend we place the sensors? In the front of the IBM server racks where the cool air is being pulled in, or the back where the hot air is being sent? Does it make a difference?

Thanks!

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-07-01 02:26 AM . Last Modified: ‎2024-03-05 11:22 PM

0 Likes
0
3059
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:26 AM . Last Modified: ‎2024-03-05 11:22 PM

As far as the servers are concerned, you'd want to put your AP9631 temperature probe(s) halfway up the front face of your server racks. Your APC InRow AC's will also have Supply Air Sensors that similarly should have be placed on the front of the server racks so they can remotely regulate the air temp entering the servers. I am wondering how your UPS is being cooled though, if you saying that all your InRow cooling is directed at the faces of the IBM server racks, and you have a hot aisle in between your Server racks and the PX-40/Battery cabinets it sounds like you could be in a situation where wrap around heat from the hot aisle will be drawn around or over the top of the UPS into its front face, and also cause heating of the batteries...which are sitting on the hot aisle ?

Dave

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 02:26 AM . Last Modified: ‎2024-03-05 11:22 PM

0 Likes
0
3059
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:26 AM . Last Modified: ‎2024-03-05 11:22 PM

I am personally thinking it should go in the area most representative of the room temperature so you get the most accurate reading of what's going on in that room to determine when your servers should shutdown due to a temperature violation.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 02:26 AM . Last Modified: ‎2024-03-05 11:22 PM

0 Likes
0
3060
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:26 AM . Last Modified: ‎2024-03-05 11:22 PM

As far as the servers are concerned, you'd want to put your AP9631 temperature probe(s) halfway up the front face of your server racks. Your APC InRow AC's will also have Supply Air Sensors that similarly should have be placed on the front of the server racks so they can remotely regulate the air temp entering the servers. I am wondering how your UPS is being cooled though, if you saying that all your InRow cooling is directed at the faces of the IBM server racks, and you have a hot aisle in between your Server racks and the PX-40/Battery cabinets it sounds like you could be in a situation where wrap around heat from the hot aisle will be drawn around or over the top of the UPS into its front face, and also cause heating of the batteries...which are sitting on the hot aisle ?

Dave

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore