Recent replacement of batttery

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Recent replacement of batttery
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
139
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:09 AM . Last Modified: ‎2024-02-29 10:17 PM

0 Likes
6
2103
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:09 AM . Last Modified: ‎2024-02-29 10:17 PM

Recent replacement of batttery

I have a Model ES 550, and today I replaced the battery. The APC directions said to charge the battery for 18 hours, however when I connected the battery and turned it on, and then ran the "Parachute software", It said it was charged to 100% ? So I am confused ? Are the batteries shipped fully charged or is there something else going on with my UPS system ? Also when I plugged in the battery and hit the on push button, the light immediately turned green. Any help is appreciated.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Brad_C
Commander Brad_C
Commander

Posted: ‎2021-07-08 02:09 AM . Last Modified: ‎2024-02-29 10:16 PM

0 Likes
0
2103
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:09 AM . Last Modified: ‎2024-02-29 10:16 PM

On 17/5/2017 9:21 PM, Karla said:

So maybe there is a difference between the original battery Specifications, and the aftermarket replacement battery ?

That is quite probable. The batteries APC supplies have very low internal resistance. It is not uncommon for lesser specified batteries to have a higher internal resistance. The result is that the output voltage drops further on-load than the original batteries for the same discharge current. This would cause the UPS to think the battery was flat well before it actually is and shut down early.

This is going to sound stupid, but compare the weight of the two batteries. Often cheaper batteries with inferior specs are measurably lighter than better specified units. Less metal, cheaper to make, worse performance.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:09 AM . Last Modified: ‎2024-02-29 10:16 PM

0 Likes
0
2103
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:09 AM . Last Modified: ‎2024-02-29 10:16 PM

Hi Karla,

There will be a possibility that batteries might ship with 100% charged. Can you help me with the model and a serial number of the UPS which will be present on the white barcode label on the UPS as well as help me with the model and a serial number of the replacement battery, this will be on the white barcode label on the battery? Just want to check the manufactured date of the battery and UPS.

Regards,

Vinay

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:09 AM . Last Modified: ‎2024-02-29 10:16 PM

0 Likes
0
2103
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:09 AM . Last Modified: ‎2024-02-29 10:16 PM

My model number on the Barcode says: Model BE550R & Number 3B0734x04242, I am the original owner & purchased it new several years ago, not sure of the purchase date. The Battery is an Aftermarket, I tried to purchase the recommended battery from APC, but was told they are “Out of Stock” and did Not know availability. The Battery I ordered and purchased on 4/30/2017 from ATBATT.Com, information on replacement battery “Amstron (Sealed Lead Acid Battery)” AP 1270F2, 12 V, & 7.0 Ah, I don’t see a bar code on battery.

 

Any help is appreciated, Thank you.

 

  1. It has been charged for over 18 hrs now, and without load. I did a quick 40 second test by pulling the power to the AC cord of the UPS, and everything transferred and supplied load. The load was another laptop computer, which was only a couple of amps, but I need to verify actual Amps. The Parachute software reported that I only had like 8 minutes, which did Not seem like much time for just (1) laptop computer load ?? The software when AC was restored reported that it was charging, and it was at 91 %. Originally before test it reported it was at 100 % . I hope this helps.
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:09 AM . Last Modified: ‎2024-02-29 10:16 PM

0 Likes
0
2103
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:09 AM . Last Modified: ‎2024-02-29 10:16 PM

Thanks for the info. If it says as 8 minutes of runtime during on battery operation then it should be a load of 225 watts as per the runtime graph.

Link: http://www.apc.com/products/runtimegraph/runtime_graph.cfm?base_sku=BE550R&chartSize=large

You can verify the load information through the Powerchute software. If the load information is less than 225 watts then there might be an issue with the battery. Please verify the load information through the Powerchute and let me know if it is showing as 225 watts or lesser than that?

Regards,

Vinay

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:09 AM . Last Modified: ‎2024-02-29 10:16 PM

0 Likes
0
2103
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:09 AM . Last Modified: ‎2024-02-29 10:16 PM

MY AC Load is a Lap top computer, the plug in power supply says that it is 19 volts at 4.6 amps, or 87 Va, or aprox. 90 watts. Thank you for the chart, I have saved it for future reference. I am also Not sure of the Volt-amps available from the BE550R, I thought it was a 550 watt-hr UPS ? Anyhow If I have less than 100 watts which would be normal for my usage, then I assume you would divide the 550 watts by say a 100 watts (load) and that should give you the time expected on the battery or aprox. 5.5 Hours, but I only get about 8 minutes ? Also I just realized I am not calculating the Volt Amps of the battery which is rated as 12 Volts & 7.0 Amps or 84 Va (battery), so I guess I would divide 84 Va by 100 watts which would be .84 hours or aprox 50 minutes, but again I only get about 8 minutes? I think the UPS is now working with the New battery but just not sure about the time thing, I guess I will try a different load maybe smaller and see how long it lasts. Thanks for your help

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:09 AM . Last Modified: ‎2024-02-29 10:16 PM

0 Likes
0
2103
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:09 AM . Last Modified: ‎2024-02-29 10:16 PM

I just took another look at the chart, and realizing its a discharge curve, which I wasn't really thinking about at the time, so silly me. But anyhow using the chart it says a 100 watt load should last for 28 minutes, and again when I actually tested it, I only got about 8 minutes. So maybe there is a difference between the original battery Specifications, and the aftermarket replacement battery ?

Reply

Link copied. Please paste this link to share this article on your social media post.

Brad_C
Commander Brad_C
Commander

Posted: ‎2021-07-08 02:09 AM . Last Modified: ‎2024-02-29 10:16 PM

0 Likes
0
2104
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:09 AM . Last Modified: ‎2024-02-29 10:16 PM

On 17/5/2017 9:21 PM, Karla said:

So maybe there is a difference between the original battery Specifications, and the aftermarket replacement battery ?

That is quite probable. The batteries APC supplies have very low internal resistance. It is not uncommon for lesser specified batteries to have a higher internal resistance. The result is that the output voltage drops further on-load than the original batteries for the same discharge current. This would cause the UPS to think the battery was flat well before it actually is and shut down early.

This is going to sound stupid, but compare the weight of the two batteries. Often cheaper batteries with inferior specs are measurably lighter than better specified units. Less metal, cheaper to make, worse performance.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore