ESXi Host containing the Virtual Appliance doesn't shut down

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • ESXi Host containing the Virtual Appliance doesn't shut down
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-08 02:09 AM . Last Modified: ‎2024-02-29 10:16 PM

0 Likes
9
2973
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:09 AM . Last Modified: ‎2024-02-29 10:16 PM

ESXi Host containing the Virtual Appliance doesn't shut down

Hello,

In my configuration, there is a PCNS VA 4.2, two ESXi 6.5 Hosts and a vCenter 6.5

So far the configuration works, after the correct definition of a shared local user.

Except, the ESXi Host containing the PCNS VA is not shutting down.

Log:

05/15/2017    17:42:20    Shutting down physical machine that PowerChute is running on.
05/15/2017    17:42:19    Shutting down vCenter Server VM Host 10.0.10.50.
05/15/2017    17:42:19    Host 10.0.10.50 has successfully entered maintenance mode.
05/15/2017    17:42:17    Starting Maintenance Mode Task on Host 10.0.10.50.
05/15/2017    17:38:36    UPS critical event: On Battery resolved on Hosts 10.0.10.50, 10.0.10.51.
05/15/2017    17:38:36    Cannot connect to vCenter Server. PowerChute may not be able to issue commands to Virtual Machines or Hosts.
05/15/2017    17:38:36    UPS is no longer running on battery power or output power has been turned on.
05/15/2017    17:38:16    Maintenance Mode Task cancelled on Host 10.0.10.50 as VCSA VM is shutting down.
05/15/2017    17:38:15    Shutting down vCenter Server VM VMware vCenter Server Appliance.
05/15/2017    17:38:15    Exit maintenance mode on Host 10.0.10.50.
05/15/2017    17:38:15    Exit maintenance mode on Host 10.0.10.51.
05/15/2017    17:37:30    Shutting down VMs on Host 10.0.10.50.
05/15/2017    17:37:30    Starting Maintenance Mode Task on Host 10.0.10.50.
05/15/2017    17:37:30    Shutting down VMs on Host 10.0.10.51.
05/15/2017    17:37:30    Starting Maintenance Mode Task on Host 10.0.10.51.
05/15/2017    17:37:29    Shutdown sequence started on Hosts 10.0.10.50, 10.0.10.51 in response to UPS critical event: On Battery.
05/15/2017    17:37:29    UPS critical event: On Battery.
05/15/2017    17:35:29    UPS has switched to battery power.

10.0.10.50 is the Host that contains the vcenter and is shut down.

10.0.10.51 is the Host that contains the PCNS VA and is not shut down.

It is shutting the VA down, but not the host containing it.

I'm sure, that i defined the PCNS "running on VM", but i don't know how to verify it.

Can you assist me with that?

Thank you,

Max

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • esxi
  • pcns
  • va
  • vmware
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:10 AM . Last Modified: ‎2024-02-29 10:16 PM

0 Likes
0
2973
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:10 AM . Last Modified: ‎2024-02-29 10:16 PM

Max,

The .ini file should read isPCNSonVM = true

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:09 AM . Last Modified: ‎2024-02-29 10:16 PM

0 Likes
0
2973
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:09 AM . Last Modified: ‎2024-02-29 10:16 PM

Hi,

Seem that you have PCNS configured incorrectly.

On 5/16/2017 2:51 AM, Max said:

05/15/2017    17:42:20    Shutting down physical machine that PowerChute is running on.

To verify that PCNS is recognizing the proper host go to Host Protection page in the PCNS web interface and verify the host that PCNS is running on is labeled with the PCNS icon. See page 18 of the User's Guide for an example. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 02:09 AM . Last Modified: ‎2024-02-29 10:16 PM

0 Likes
0
2973
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:09 AM . Last Modified: ‎2024-02-29 10:16 PM

Hello,

Thanks for your answer.

In Host Protection I can see my two ESX Hosts, 1 labeled with the vcenter icon and the other one with the PCNS icon.

If the vcenter is down, both Hosts are unlabeled.

PCNS shuts the vcenter down before it shuts down itself.

Maybe that's the Problem?

Max

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:09 AM . Last Modified: ‎2024-02-29 10:16 PM

0 Likes
0
2973
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:09 AM . Last Modified: ‎2024-02-29 10:16 PM

Hi,

The shutdown process is

1 - VMs/Vapps are powered down

2 - vCenter server is powered down

3 - Hosts are powered down starting with any hosts that do not have PCNS or vCenter Server running on them. Then the host that has vCenter Server is powered down and finally the host that PCNS is running on is powered down. 

Please attach the error.log and VirtualizationFileStore.properties files that are in /opt/APC/PowerChute/group1 I would like to see if any errors where logged. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:10 AM . Last Modified: ‎2024-02-29 10:16 PM

0 Likes
0
2973
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:10 AM . Last Modified: ‎2024-02-29 10:16 PM

Hi,

How is your network set up? I see in the FileStoreProperties file 

10.240.7.150_VMs=Test4,Test5,Test3,Test6,vMA-6.5.0.0-4569350_OVF10
10.240.7.59_VMs=Test2,Test1

but you list 10.240.0.53 and 10.240.0.54 It looks like 10.240.7.150 might be 10.240.0.54 is that correct and that would that make 10.240.7.59 to equal 10.240.0.53?

Also, did you look at the error log? There are many entries for connection refused and no route to host. Connection refused looks like a permissions issue and no route to host would be a networking issue.  

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 02:10 AM . Last Modified: ‎2024-02-29 10:16 PM

0 Likes
0
2973
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:10 AM . Last Modified: ‎2024-02-29 10:16 PM

Hi,

ESX1 10.240.0.59

ESX2 10.240.0.150

PCNS VA 10.240.0.53

vCenter 10.240.0.54

The PCNS VA can always reach the other host to shut down, but not its own. Doesn't matter on which host the VA is placed (ESX1 or 2).

So I believe it's neither a network problem nor a rights problem.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:10 AM . Last Modified: ‎2024-02-29 10:16 PM

0 Likes
0
2973
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:10 AM . Last Modified: ‎2024-02-29 10:16 PM

Hi,

Please stop the PCNS service (service PowerChute stop) and edit the log4j2.xml that is in /opt/APC/PowerChute/group1 and put PCNS into debug mode (see FAQ FA230514 for assistance). After putting PCNS into debug mode rename error.log to saverror.log and rename eventlog.txt to saveventlog.txt. Also open VirtualizationFileStore.properties and delete any entries that may be in there and save the file. Then restart PCNS and run a shutdown test. Once the test is completed after PCNS has restarted stop PCNS and take it out of debug mode, make copies of eventlog.txt, error.log, and VirtualizationFileStore.properties and attach them to you post. Then restart PCNS. 

I will review the logs and file.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:10 AM . Last Modified: ‎2024-02-29 10:16 PM

0 Likes
0
2973
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:10 AM . Last Modified: ‎2024-02-29 10:16 PM

max,

Please attached the pcnsconfig.ini file that is in /opt/APC/PowerChute/group1. 

Thanks,

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 02:10 AM . Last Modified: ‎2024-02-29 10:16 PM

0 Likes
0
2973
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:10 AM . Last Modified: ‎2024-02-29 10:16 PM

Hi Bill,

I found the answer in the .ini file:

My first question:

I'm sure, that i defined the PCNS "running on VM", but i don't know how to verify it.

Can you assist me with that?

Was the correct question.

In the .ini file of me, the value was isPCNSonVM = false (but the image of the PCNS was next to the ESX Host in Host Protection)

(The Rest of the file was missing, because I copy pasted it from putty and forgot the other lines, because WinSCP wouldn't work)

Thanks for your assistance,

Max

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:10 AM . Last Modified: ‎2024-02-29 10:16 PM

0 Likes
0
2974
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:10 AM . Last Modified: ‎2024-02-29 10:16 PM

Max,

The .ini file should read isPCNSonVM = true

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.