Posted: 2025-02-24 03:05 AM . Last Modified: 2025-02-24 03:18 AM
I have an UPS with model number SRV3kri-e.
I purchased a Modbus card, SRVSMB001, to read data from the card —how can I read it? I have inserted the Modbus card into the intelligent slot and connected it to my PC using an RJ45 cable—what can I use to read it, and what steps should I take?
Does it need a firmware update?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-02-24 11:33 PM
Hello,
There is a separate Modbus card available for SRV UPS. This must be configured before use.
See the Modbus Card Installation Manual (EN 990-9286) for steps to configure the below settings.
1. ID = 9 (bits 1 and 4 are OFF on SW1)
2. Baud rate = 9600 (bit 1 is OFF and bit 2 is ON on SW2)
3. Parity check = No parity check, 1 stop bits (bit 3 is ON and bit 4 is OFF on SW2)
4. RS485 Resistance Configuration = Enable (bits 5, 6, 7, and 8 are ON on SW2)
The below manual explains how to connect the Modbus card to your presonal computer on page 5 then install the SNMP monitoring software to configure the modbus settings and view the modbus device
The modbus register map are as follows :
No need to update the firmware for this card
Regard,
Karim
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-02-24 11:33 PM
Hello,
There is a separate Modbus card available for SRV UPS. This must be configured before use.
See the Modbus Card Installation Manual (EN 990-9286) for steps to configure the below settings.
1. ID = 9 (bits 1 and 4 are OFF on SW1)
2. Baud rate = 9600 (bit 1 is OFF and bit 2 is ON on SW2)
3. Parity check = No parity check, 1 stop bits (bit 3 is ON and bit 4 is OFF on SW2)
4. RS485 Resistance Configuration = Enable (bits 5, 6, 7, and 8 are ON on SW2)
The below manual explains how to connect the Modbus card to your presonal computer on page 5 then install the SNMP monitoring software to configure the modbus settings and view the modbus device
The modbus register map are as follows :
No need to update the firmware for this card
Regard,
Karim
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of