What is the APC part number for the 4-pin connector which mates with the EPO jack on the back of the UPS? The manual is crystal clear on how to wire the EPO switch connection, but there is no mention of the required connector's part number. If nothing else I would like to know the pin pitch dimension of this 4 conductor connector. I suspect I can buy a compatible connector on Amazon, probably a whole bag of them, for what APC will charge. It is absolutely frustrating that this connector was not supplied with the UPS in the first place. Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-02-25 12:16 AM
Hello,
The EPO is a part of LIT KIT( 0L1711A) with part number 730-0004-Z (terminal block 4 Pos srew),it should come in LIT package inside the unit from the factory as per the attached inventory ,you may need to check if this part is lost during unpacking but if you are confident that it is not available then you might contact your local CCC team to direct this claim to the factory in order to check if they can provide it to you or it is found with one of our service centers in your region
I had attached the terminal dimensions for references ,please do not outsource this connector out of Schneider until your can register a request with our support team to see the best alternatives to supply this part for you
Regards,
Karim
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-02-25 12:16 AM
Hello,
The EPO is a part of LIT KIT( 0L1711A) with part number 730-0004-Z (terminal block 4 Pos srew),it should come in LIT package inside the unit from the factory as per the attached inventory ,you may need to check if this part is lost during unpacking but if you are confident that it is not available then you might contact your local CCC team to direct this claim to the factory in order to check if they can provide it to you or it is found with one of our service centers in your region
I had attached the terminal dimensions for references ,please do not outsource this connector out of Schneider until your can register a request with our support team to see the best alternatives to supply this part for you
Regards,
Karim
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of