Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Re: UPS: Lost the local network management interface-to-UPS communication

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Re: UPS: Lost the local network management interface-to-UPS communication
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5027
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
rickn._apc
Crewman rickn._apc
Crewman

Posted: ‎2021-07-01 06:29 AM

0 Likes
15
3090
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-01 06:29 AM

Re: UPS: Lost the local network management interface-to-UPS communication

This was originally posted on APC forums on 11/18/2014


Hi,

My name is Rick and I was looking through the forums and found the same issue I've been experiencing with my UPS/NMC Card. We have SMT700 and SMT1000 units with an AP9630 NMC card. There are no serial cables etc plugged into the units, just the network cable.

I had updated the NMC Firmware from V5.1.3 up to V6.2.0 on 2 of the devices.

2 days later we started to experience the same issue, the NMC card will restart for no reason and we receive the same error message.

After communicating with the APC Chat group, they said that the firmware on the UPS unit itself will need to be updated. They were at : (UPS 05.0 (ID17). Updating the UPS firmware is not an option because of the remote locations and having to remote the load from the unit.

What are the different firmware options available for the NMC card? Is V6.0.6 or V.6.1.1 available somewhere?

Thanks


Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 06:29 AM

0 Likes
0
3082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-01 06:29 AM

This reply was originally posted by Angela on APC forums on 12/1/2014


Hi Rick,

You can downgrade the firmware via FTP (or a manual method) and then format it if you want to downgrade.

What I am seeing is the task that handles the INI file upload failsafe'd on 3 of them in the same way. And it looks to be like it could be memory related because they all show low memory at some point. I know you uploaded the INI file to all of them so that is a note I made. One shows that SNMP task failsafe'd but also shows low memory. I also see that they all seemed to have restarted about ~2 days after you configured them and uploaded the INI.

At this point, I don't have a magic answer. I think this is memory related. Can we monitor it for one more round now that the INI has been uploaded and see what you get? If it does not do it any more in the next few days, it may be a memory issue after the INI file upload.

See Answer In Context

Reply
Replies 15
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 06:29 AM

0 Likes
0
3082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-01 06:29 AM

This reply was originally posted by Angela on APC forums on 11/18/2014


Hi Rick,

I branched your discussion because it is likely a different problem, just same symptom. Your units are also newer and would not be affected by a connected USB or serial cable. And you do not have another accessory installed. Can you let me take a look at your logs like I asked the other post (Instructions here-> http://www.schneider-electric.com/support/index?page=content&country=US〈=en&locale=en_US&id=FA156131)? The full dump file would be preferable.

v6.2.0 is recommended and an older version likely will not help. If I review everything and it does appear to be the best option if I do come to the conclusion about the UPS firmware, I can provide it to you. Though, I have not seen any issues with the older UPS firmware causing this on new NMC firmware so I am hesitant to think that is our only option at this time.

Reply
rickn._apc
Crewman rickn._apc
Crewman

Posted: ‎2021-07-01 06:29 AM

0 Likes
0
3082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-01 06:29 AM

This was originally posted on APC forums on 11/19/2014


Hi,

I was able to get the following files: Config, Data,Debug,Dump and Event Files.

They are attached.

Thanks

Rick


Attachments
mtb01mps02.zip
Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 06:29 AM

0 Likes
0
3082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-01 06:29 AM

This reply was originally posted by Angela on APC forums on 11/19/2014


Hi Rick,

I took a look at the logs, thank you. Yes, the Network Management Card interface is rebooting for what seems to be no good reason (shown by the Network Interface restarted events). As part of the few standard messages you receive after a restart, whether expected or not, you'll see UPS:Restored the local network management interface-to-UPS communication. I don't see any lost communication between management interface and UPS in your logs.

When I look at the dump and debug logs, for both v5 and when it was upgraded to v6, it is rebooting because of a similar issue with a particular task. Upgrading the UPS may help because the task that is reporting it is crashing when it reboots is the task that handles all of the events that come from the UPS. I also see at some point it rebooted due to the watchdog mechanism, explained here -> Why does my Network Management Card report warmstarts and coldstarts? | FAQs | Schneider Electric US - though, those seem to be when you were still on the older firmware.

If I were you, on at least one of the devices, I'd consider starting fresh with a card and formatting it (which will wipe ALL settings from it, including TCP/IP settings). If you don't have a way to reconfigure the TCP/IP settings remotely, we may want to at least start with a reset to defaults then. Alternatively, we can try downgrading one of the cards, just to try, but I am not confident in that being the solution. And because the task that reports it is crashing is the UPS event handler, I don't think it is a terrible idea to possibly plan to upgrade the UPS in the future, if not for thus, but to take advantages of any bug fixes the UPS updates provide.

I'll provide v6.1.1 firmware in an attachment to this post but please be advised it has bugs of its own, many of which are resolved in  6.2.0. But, if it does clear up with downgrading, then that could help in the investigation.

Attachments
apc_hw05_aos611_sumx611_bootmon102.exe.zip
Reply
rickn._apc
Crewman rickn._apc
Crewman

Posted: ‎2021-07-01 06:29 AM

0 Likes
0
3082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-01 06:29 AM

This was originally posted on APC forums on 11/20/2014


Hi Angela,

As for the Watchdog feature, I asked our network monitoring service how often they POLL the card and its every 5 mins. Then every 1-3 mins if it does not get response.

90 % of these devices are at remote locations, so if we format the card, will it at least boot up on DHCP?

After the card is reformatted, I was thinking of a quicker way to get the card configured for our network, Radius Server, Email Servers for Warnings etc. Is it possible to download the clean Config.ini file from the reformatted card, make the changes for our setup and then upload the file and reboot?

Do you have a list of commands you can do at the FTP prompt?

Do you have the 6.1.1 firmware?

Thank you very much for the help.

Rick


Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 06:29 AM

0 Likes
0
3082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-01 06:29 AM

This reply was originally posted by Angela on APC forums on 11/20/2014


Hi Rick,

Yes, the default for this model of card on this firmware is to boot up and do DHCP so if you have a DHCP server and can look up the IP maybe by the MAC address, you'll be fine. The MAC address is shown under About->Network in the interface.

Yes, you can do what you're asking on the config.ini file. You can also download a config.ini right before you format it as well as a backup and re-upload that or modify it upon upload.

What FTP client are you going to use - Windows Command Prompt FTP? I had a list of commands in our knowledge base but now I can't find it. Once I know the client, we can probably find a list online. You should just need to do some basic ones like get and put to download and upload respectively. There are also a few like bin to enable binary transfer mode and hash for hashmark printing before you start transferring files.

Here are some instructions on uploading/downloading a config.ini (and it also covers mass upload/download of config.ini's)-> How can I mass configure an Network Management Card (NMC) or NMC embedded product? | FAQs | Schneide...

Make sure you view this post outside of the "inbox" on this site because I did attach the firmware file to my previous post. When you're in "inbox" you won't be able to see it.

Let me know if you have any questions before proceeding.

P.S. the way you'll need to format if you're remote is to issue the format command via Telnet or SSH and then you'll need to type yes to confirm, then reboot to apply it and yes to confirm the reboot.

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 06:29 AM

0 Likes
0
3082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-01 06:29 AM

This reply was originally posted by Angela on APC forums on 11/26/2014


Hi Rick,

Can you get me those same log files you did last time again to see if it's any different? I am on vacation this week so I hope it'll be OK if I look at them early next week? I am especially interested in debug.txt and dump.txt with event.txt.

Thanks smile

Reply
rickn._apc
Crewman rickn._apc
Crewman

Posted: ‎2021-07-01 06:29 AM

0 Likes
0
3082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-01 06:29 AM

This was originally posted on APC forums on 11/26/2014


Hi Angela,

I saved off the config file, did the FORMAT command on 5 different unit and then re-applied the configuration. However, today I seen that the NMC has restarted again. Is there anything else you can think of to try? How would I down grade the firmware if needed?

Thanks

Reply
rickn._apc
Crewman rickn._apc
Crewman

Posted: ‎2021-07-01 06:29 AM

0 Likes
0
3082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-01 06:29 AM

This was originally posted on APC forums on 11/26/2014


Hi,

I've attached the logs for 4 different units that restarted.

Thanks

Attachments
622ConfigFiles.zip
Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 06:29 AM

0 Likes
0
3083
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-01 06:29 AM

This reply was originally posted by Angela on APC forums on 12/1/2014


Hi Rick,

You can downgrade the firmware via FTP (or a manual method) and then format it if you want to downgrade.

What I am seeing is the task that handles the INI file upload failsafe'd on 3 of them in the same way. And it looks to be like it could be memory related because they all show low memory at some point. I know you uploaded the INI file to all of them so that is a note I made. One shows that SNMP task failsafe'd but also shows low memory. I also see that they all seemed to have restarted about ~2 days after you configured them and uploaded the INI.

At this point, I don't have a magic answer. I think this is memory related. Can we monitor it for one more round now that the INI has been uploaded and see what you get? If it does not do it any more in the next few days, it may be a memory issue after the INI file upload.

Reply
rickn._apc
Crewman rickn._apc
Crewman

Posted: ‎2021-07-01 06:30 AM

0 Likes
0
3082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-01 06:30 AM

This was originally posted on APC forums on 12/3/2014


Hi,

The restart has happened again on 2 NMC devices.

I did upload the files you normally ask for.

If we have to download, how do you do it via FTP?

Rick


Attachments
UPSDump_Dec0203.zip
Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 06:30 AM

0 Likes
0
3082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-01 06:30 AM

This reply was originally posted by Angela on APC forums on 12/3/2014


If it is easier to try downgrading for your situation (rather than updating the UPS), follow the NMC2 FTP downgrade instructions here -> How do I upgrade the firmware on an APC Network Management Card (NMC) or NMC embedded device (Rack P...

Though, because of what I see in the dump file, I do not think upgrading one of the UPSs is a terrible idea and would be a good test. UPS related processes/tasks are failsafe'ing and it could be because there is an issue with it or because something else is eating up the memory it needs.I haven't seen this specific type of scenario before.

Reply
rickn._apc
Crewman rickn._apc
Crewman

Posted: ‎2021-07-01 06:30 AM

0 Likes
0
3082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-01 06:30 AM

This was originally posted on APC forums on 12/19/2014


Hi Angela,

I've installed 6.1.1 on 3 test devices and we're still having the issue of the NMC rebooting.

Would you happen to have the 5.1.3 firmware?

That what these devices had before we did the update. The only reason we updated the firmware was to get the feature of getting the model of the UPS unit. Everything else was working fine before.

 

Thanks

Reply
rickn._apc
Crewman rickn._apc
Crewman

Posted: ‎2021-07-01 06:30 AM

0 Likes
0
3082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-01 06:30 AM

This was originally posted on APC forums on 12/19/2014


Hi,

The reboots are really just annoying because we receive the notification and a trouble ticket is created. Another thing is knowing that the NMC is unstable.

Our SNMP monitoring service does not pick up the reboots .

One other thing is when we try to access the NMC via a Browser, it seems to cause the reboot so then we need to wait the 2-3 mins for it to come back up.

I'll read the articles and see what we will do.

 

Thanks

Reply
rickn._apc
Crewman rickn._apc
Crewman

Posted: ‎2021-07-01 06:30 AM

0 Likes
1
3082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-01 06:30 AM

This was originally posted on APC forums on 12/19/2014


Hi Again,

I read the article about the concerns on doing a firmware download.

The biggest concern is losing some settings because of the database change, correct?

I have all the original 5.1.3 config files so reformatting the device and reapplying the config file is no big deal.

 

My biggest concern is after the downgrade we will lose connection to the device. it wont boot up at all.

We have DHCP at the locations so the UPS will at least we'll have an IP address.

What I'm thinking is

1) Format device with 6.1.1 to clear all configuration

2) Apply 5.1.7

3) Maybe format again with 5.1.7 (Not sure If I need to do this)

4) Upload original 5.1.3 config file

 

Do you see any problems?

 

Thanks

Reply
J-E-1984
Ensign J-E-1984
Ensign

Posted: ‎2022-09-13 09:22 AM

In response to rickn._apc
0 Likes
0
1957
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2022-09-13 09:22 AM

Good Afternoon,

 

By any chance, did you ever reach a solution?  Our organization has the same problem: Network Cards rebooting without reason.

 

We replicated the issue in a lab, confirmed it is happening on all deployed units, and currently APC is investigating the issue.

 

Did you have anything you tried that worked?  As a note, our devices are doing this on multiple firmware revisions... So I doubt that is causing the issue.

 

  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc