Smart-UPS X 3000: Events 0x012C, 0x012A, 0x012B & 0x012D

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS X 3000: Events 0x012C, 0x012A, 0x012B & 0x012D
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
lutzn
lutzn
Cadet

Posted: ‎2022-09-01 02:16 PM

0 Likes
2
2274
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-01 02:16 PM

Smart-UPS X 3000: Events 0x012C, 0x012A, 0x012B & 0x012D

Hi,

 

it's about a Smart-UPS X 3000 (SMX3000RMHV2U) with two external battery SMX120RMBP2U.  Since last power outage this morning we get messages like these (they stopped this evening):

 

09/01/2022 17:44:11 Device UPS: A battery charger fault no longer exists. 0x012B
09/01/2022 17:44:11 Device UPS: The internal battery temperature no longer exceeds the critical threshold. 0x012D
09/01/2022 17:43:59 Device UPS: A battery charger fault exists. 0x012A

...

09/01/2022 15:39:19 Device UPS: A battery charger fault no longer exists. 0x012B
09/01/2022 15:39:15 Device UPS: A battery charger fault exists. 0x012A
09/01/2022 15:39:15 Device UPS: The internal battery temperature exceeds the critical threshold. 0x012C

 

Complete log is attached.

 

It seems as if everything is fine at the moment, but I saw the voltage go up to 140V (normally 130V) and the temperature go up to 41°C (normally ~33°C).  Currently it is 10°C higher than the last night.  And then there have been these messages...

Batteries are about 4 years old.  If we are advised to change battery, what battery should be replaced, how can we find out?  Or do we need to replace them all?

 

Can someone please tell me what that means, what we can or should do and how critical the situation is.

 

Thanks a lot!

- lutzn

 

 

event.txt

-----------

Network Management Card AOS v7.0.8
Smart-UPS & Matrix-UPS APP v7.0.8
NMC Serial Number: 5A1347T01526

Model: Smart-UPS X 3000
UPS Serial Number: AS1436144781
Firmware Revision: UPS 07.4 (ID1003)

Date Time Name Contact Location System IP
09/01/2022 20:40:54 apcA11588 Unknown Unknown 10.11.12.13

Date Time User Event Code
09/01/2022 17:44:11 Device UPS: A battery charger fault no longer exists. 0x012B
09/01/2022 17:44:11 Device UPS: The internal battery temperature no longer exceeds the critical threshold. 0x012D
09/01/2022 17:43:59 Device UPS: A battery charger fault exists. 0x012A
09/01/2022 17:43:58 Device UPS: A battery charger fault no longer exists. 0x012B
09/01/2022 17:43:39 Device UPS: A battery charger fault exists. 0x012A
09/01/2022 17:43:38 Device UPS: A battery charger fault no longer exists. 0x012B
09/01/2022 17:43:19 Device UPS: A battery charger fault exists. 0x012A
09/01/2022 17:43:19 Device UPS: A battery charger fault no longer exists. 0x012B
09/01/2022 17:42:59 Device UPS: A battery charger fault exists. 0x012A
[REPEATED EVERY FEW MINUTES...]
09/01/2022 15:40:00 Device UPS: A battery charger fault no longer exists. 0x012B
09/01/2022 15:39:40 Device UPS: A battery charger fault exists. 0x012A
09/01/2022 15:39:39 Device UPS: A battery charger fault no longer exists. 0x012B
09/01/2022 15:39:20 Device UPS: A battery charger fault exists. 0x012A
09/01/2022 15:39:19 Device UPS: A battery charger fault no longer exists. 0x012B
09/01/2022 15:39:15 Device UPS: A battery charger fault exists. 0x012A
09/01/2022 15:39:15 Device UPS: The internal battery temperature exceeds the critical threshold. 0x012C
[...]
09/01/2022 10:05:03 Device Environment: Restored the local network management interface-to-integrated Environmental Monitor (Universal I/O at Port 2) communication. 0x0344
09/01/2022 10:05:03 Device Environment: Restored the local network management interface-to-integrated Environmental Monitor (Universal I/O at Port 1) communication. 0x0344
09/01/2022 09:43:22 Device UPS: No longer on battery power. 0x010A
09/01/2022 09:43:21 Device UPS: On battery power in response to distorted input. 0x0109
09/01/2022 09:43:09 Device UPS: No longer on battery power. 0x010A
09/01/2022 08:11:23 Device UPS: On battery power in response to none. 0x0109
09/01/2022 08:11:23 Device UPS: Restored the local network management interface-to-UPS communication. 0x0101
09/01/2022 07:59:21 Device UPS: On battery power in response to distorted input. 0x0109

 

data.txt

----------

 Smart-UPS X 3000 Integrated EMU
Date Time Vmin Vmax Vout Iout %Wout %out FrqOut %Cap Vbat TupsC T1ambC %Hum1 T2ambC %Hum2
09/01/2022 21:25:57 220.41 225.45 225.08 2.88 16.49 21.64 50.00 100.00 132.69 +41.13 26.0
09/01/2022 21:10:57 220.48 225.69 223.84 2.91 16.75 21.75 50.00 100.00 132.66 +41.26 26.0
09/01/2022 20:55:58 221.39 226.33 223.36 2.91 16.85 21.84 50.00 100.00 132.63 +41.37 26.0
09/01/2022 20:40:58 220.03 225.52 222.09 2.91 16.71 21.64 50.00 100.00 132.59 +41.46 26.0
09/01/2022 20:25:58 219.02 226.17 224.28 2.88 16.73 21.68 50.00 100.00 132.59 +41.55 26.0
09/01/2022 20:10:58 219.19 226.33 222.89 2.91 16.64 21.65 50.00 100.00 132.56 +41.59 26.0
09/01/2022 19:55:57 220.02 232.72 226.19 2.88 16.64 21.75 50.00 100.00 132.56 +41.63 26.0
09/01/2022 19:40:57 226.06 231.39 229.80 2.84 16.74 22.01 50.00 100.00 132.56 +41.67 26.0
09/01/2022 19:25:57 223.88 232.33 228.03 2.88 16.84 21.95 50.00 100.00 132.56 +41.70 27.0
09/01/2022 19:10:57 223.09 233.19 227.42 2.88 16.76 21.90 50.00 99.96 132.56 +41.68 27.0
09/01/2022 18:55:57 229.20 235.03 231.09 2.84 16.86 22.14 50.00 99.78 132.56 +41.63 26.0
09/01/2022 18:40:57 229.25 234.11 231.98 2.84 16.71 22.17 50.00 99.62 132.59 +41.55 26.0
09/01/2022 18:25:57 228.95 234.06 232.00 2.84 16.80 22.14 50.00 99.43 132.63 +41.42 26.0
09/01/2022 18:10:57 225.02 232.39 231.19 2.88 16.83 22.20 50.00 99.26 132.66 +41.27 26.0
09/01/2022 17:55:56 227.11 233.23 231.58 2.84 16.69 22.07 50.00 99.09 132.69 +41.06 26.0
09/01/2022 17:40:56 226.08 233.66 231.44 2.84 16.65 22.01 50.00 100.00 130.53 +40.90 26.0
09/01/2022 17:25:56 220.34 232.78 232.03 2.84 16.79 22.19 50.00 100.00 130.50 +40.55 26.0
09/01/2022 17:10:56 224.94 232.83 229.28 2.88 16.82 22.05 50.00 99.98 130.50 +40.30 26.0
09/01/2022 16:55:57 222.64 231.38 230.05 2.84 16.79 22.02 50.00 99.83 130.47 +39.61 26.0
09/01/2022 16:40:57 228.75 233.34 231.00 2.88 16.82 22.15 50.00 99.67 130.41 +38.86 26.0
09/01/2022 16:25:57 227.05 234.70 231.55 2.84 16.73 22.07 50.00 99.52 130.38 +37.91 26.0
09/01/2022 16:10:57 226.61 234.48 232.48 2.88 16.82 22.30 50.00 99.36 130.28 +36.63 26.0
09/01/2022 15:55:56 228.22 232.55 230.95 2.84 16.81 22.11 50.00 99.21 130.19 +35.47 26.0
09/01/2022 15:40:56 226.84 232.02 231.84 2.84 16.86 22.14 50.00 99.05 131.50 +34.80 26.0
09/01/2022 15:25:56 228.00 233.56 229.97 2.88 16.89 22.22 50.00 98.88 136.78 +34.05 26.0
09/01/2022 15:10:56 227.31 232.34 231.45 2.84 16.75 22.16 50.00 98.27 137.69 +33.38 26.0
09/01/2022 14:55:57 224.98 232.31 228.61 2.88 16.87 22.01 50.00 97.66 138.56 +32.74 26.0
09/01/2022 14:40:57 224.55 229.55 227.19 2.88 16.95 21.99 50.00 97.04 139.47 +32.16 26.0
09/01/2022 14:25:57 218.63 229.86 228.94 2.88 16.78 21.96 50.00 96.43 140.31 +31.63 26.0
09/01/2022 14:10:56 219.52 231.92 220.92 2.91 16.78 21.44 50.00 95.81 141.13 +31.15 26.0
09/01/2022 13:55:57 224.53 233.50 229.81 2.84 16.78 21.98 50.00 95.20 141.84 +30.80 26.0
09/01/2022 13:40:57 225.33 232.88 230.91 2.88 16.93 22.29 50.00 93.61 142.28 +30.49 26.0
09/01/2022 13:25:57 225.27 233.72 226.69 2.91 17.03 22.07 50.00 91.55 142.06 +30.23 26.0
09/01/2022 13:10:57 220.94 233.59 229.50 2.88 16.91 22.18 50.00 89.49 139.91 +30.04 26.0
09/01/2022 12:55:56 221.45 229.20 227.81 2.88 16.84 21.93 50.00 87.42 137.66 +29.90 26.0
09/01/2022 12:40:56 222.41 232.06 223.42 2.91 16.81 21.72 50.00 85.35 136.31 +29.80 26.0
09/01/2022 12:25:56 222.39 234.52 226.16 2.88 16.82 21.81 50.00 83.30 135.25 +29.73 26.0
09/01/2022 12:10:56 223.34 234.36 223.47 2.91 16.92 21.71 50.00 81.21 134.28 +29.69 26.0
09/01/2022 11:55:56 223.05 232.63 232.23 2.84 16.99 22.23 50.00 79.15 133.38 +29.66 26.0
09/01/2022 11:40:56 226.08 233.45 231.03 2.88 17.02 22.27 50.00 77.08 132.53 +29.66 26.0
09/01/2022 11:25:56 222.19 233.39 231.92 2.88 16.95 22.24 50.00 75.02 131.72 +29.69 26.0
09/01/2022 11:10:56 224.56 232.80 228.13 2.84 16.73 21.82 50.00 72.98 130.94 +29.69 26.0
09/01/2022 10:55:56 223.70 231.72 229.92 2.84 16.83 21.98 50.00 70.90 130.22 +29.71 25.0
09/01/2022 10:40:56 220.78 228.77 227.73 2.88 17.01 21.96 50.00 68.81 129.47 +29.77 25.0
09/01/2022 10:25:56 218.89 226.08 223.05 2.91 16.92 21.74 50.00 66.77 128.72 +29.86 25.0
09/01/2022 10:10:56 218.47 226.80 224.22 2.91 16.92 21.82 50.00 64.70 127.91 +29.95 25.0
09/01/2022 09:55:56 0.00 223.05 220.70 2.91 16.64 21.40 50.00 62.68 126.91 +30.11
09/01/2022 09:40:56 0.00 0.00 230.97 2.81 16.31 21.72 49.98 61.92 119.84 +30.31
09/01/2022 09:25:56 0.00 0.00 230.95 2.81 16.38 21.87 49.99 67.64 120.63 +30.37
09/01/2022 09:10:56 0.00 0.00 230.95 2.81 16.51 21.89 49.98 73.48 121.44 +30.47
09/01/2022 08:55:56 0.00 0.00 230.95 2.84 16.57 22.00 49.98 78.77 122.13 +30.65
09/01/2022 08:40:56 0.00 0.00 230.97 2.84 16.52 21.95 49.99 83.79 122.75 +30.95
09/01/2022 08:25:56 0.00 0.00 230.97 2.81 16.51 21.88 49.98 89.11 123.50 +31.51
09/01/2022 08:06:22 0.00 227.27 230.92 2.84 16.47 21.90 49.99 94.65 124.00 +32.76 25.0
09/01/2022 07:51:22 217.36 229.73 223.03 2.78 16.53 20.69 50.00 100.00 129.81 +32.65 26.0
09/01/2022 07:36:22 221.66 229.23 225.72 2.78 16.62 20.95 50.00 100.00 129.81 +32.70 26.0

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 2
JonPro
Commander JonPro Commander
Commander

Posted: ‎2022-09-04 10:00 PM

0 Likes
1
2203
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-04 10:00 PM

Hi @lutzn 

 

Thank you for reaching out to the SE Community, my name is Jon and I will assist you with this query.  Apologies for the inconvenience this has caused you.  Is it okay for you to do a brain dead on your UPS and if the fault returns, kindly provide the 3-digit event code of the error via the LCD and the NMC debug files?

 

I have provided the guides below for you to follow.

 

Video: How to perform a cold start and brain dead on Smart-UPS 

Video: How can I download Event, Data, Configuration, and Debug files from my Network Management Car... 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

lutzn
lutzn
Cadet

Posted: ‎2022-09-13 01:36 AM

In response to JonPro
0 Likes
0
2158
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-13 01:36 AM

Hi!

 

I thank you very much for your answer.  I was on holiday.

 

We need to find a suitable time frame for the procedure you described.  This may take a few weeks because we have to take down some part of the infrastructure.

 

I will tell you the outcome when finished.

 

Thanks a lot!

-lutzn

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore