Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
Raise the voltage at which the UPS activates?
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-0104:00 AM. Last Modified: 2024-03-0510:31 PM
Raise the voltage at which the UPS activates?
Hello - Is there a way to configure the PowerChute software so that the battery backup will engage when the voltage drops below 100V? In the software the highest voltage is 88V. I'm running an Backup-UPS Pro 1500. Thanks.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-0104:00 AM. Last Modified: 2024-03-0510:31 PM
Your UPS should have a voltage transfer range setting you can adjust. All of the settings for that come from the UPS and not the software itself. The software just gives you an interface to change the settings on the UPS.
Also, this UPS has automatic voltage regulation (AVR). To prevent using your UPS battery, the AVR is designed to kick in when you have voltages below 120V (or whatever the nominal voltage is). When the transformer is no longer able to boost the voltage to an acceptable level, then the UPS transfers to battery. Higher than 88V, the AVR will kick in and boost your voltage and save battery life.
Per the user's guide:
Online Input Voltage Range 88 - 139V
Automatic Voltage Regulation (94-107V) +11.5% (boost)
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-0104:00 AM. Last Modified: 2024-03-0510:31 PM
Your UPS should have a voltage transfer range setting you can adjust. All of the settings for that come from the UPS and not the software itself. The software just gives you an interface to change the settings on the UPS.
Also, this UPS has automatic voltage regulation (AVR). To prevent using your UPS battery, the AVR is designed to kick in when you have voltages below 120V (or whatever the nominal voltage is). When the transformer is no longer able to boost the voltage to an acceptable level, then the UPS transfers to battery. Higher than 88V, the AVR will kick in and boost your voltage and save battery life.
Per the user's guide:
Online Input Voltage Range 88 - 139V
Automatic Voltage Regulation (94-107V) +11.5% (boost)
(126-141V) -11/5% (trim)