Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Rack Organization - SURT20KRMXLT-TF5, SURT192RMXLBP2, APTF20KW01

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Rack Organization - SURT20KRMXLT-TF5, SURT192RMXLBP2, APTF20KW01
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-07 11:18 PM . Last Modified: ‎2024-03-01 12:03 AM

0 Likes
4
1380
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:18 PM . Last Modified: ‎2024-03-01 12:03 AM

Rack Organization - SURT20KRMXLT-TF5, SURT192RMXLBP2, APTF20KW01

We've purchased the APC Smart-UPS RT 20KVA RM 208V (SURT20KRMXLT-TF5), 2 additional external battery packs (SURT192RMXLBP2), and a 20KVA Isolation Transformer (APTF20KW01).

The transformer is a beast (~250lbs), so my inclination is to rack it at the bottom of a 4 post rack that we have allocated for this installation. On top of it (on rails, of course), I was going to load the 3 battery packs and finally the UPS itself on the top.

I haven't had a chance to discuss with our electrical contractor who will be doing the install, but does this seem to be the logical organization of these components? I thought about potentially racking the transformer directly underneath the UPS unit to make the wiring runs slightly shorter, but I'm not sure if there is a real benefit there.

Is there a recommended configuration for these components?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-07-07 11:18 PM . Last Modified: ‎2024-03-01 12:03 AM

0 Likes
0
1380
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:18 PM . Last Modified: ‎2024-03-01 12:03 AM

We're in the Carribean so each floor is steel reinforced concrete that is (if I recall) 12 inches thick, but I am waiting to hear back to confirm that.

You're absolutely right about the rack - the leveling feet are pretty meager. We'll have to see how that pans out.

The battery packs have 8 batteries each that are individually servicable, but we'll be having the APC partner in-country doing our regular maintenance, so I'll leave it to them to do things the Right Way™

Thanks again for your feedback.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-07 11:18 PM . Last Modified: ‎2024-03-01 12:03 AM

0 Likes
0
1380
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:18 PM . Last Modified: ‎2024-03-01 12:03 AM

APC recommends installing the transformer at the bottom of the rack (page 11 of the PDF). They also say the UPS must be installed above the batteries (page 4 of the PDF).

Depending on the loading capacity of your rack and what type of floor it is on, this combination may or may not exceed the maximum allowable weight in the rack. I get 1700 lbs for the equipment you list - 640 for the UPS, 400 each for the 2 battery frames, 260 for the transformer.

If you have multiple racks, an option would be to put some equipment in the bottom of one rack and the rest in an adjoining rack. Here is a picture of how I did this with a Symmetra RM - the UPS is on the left with the transformer above (it is a much smaller plug-in transformer, while yours is hard-wire) and the two XR battery frames are on the right. Note that sometimes a battery pack extension cable is needed if the XR packs are not directly under the UPS. If you plan for a side-by-side installation, verify the battery pack cable length and/or the availability of an APC extension cable before ordering.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-07 11:18 PM . Last Modified: ‎2024-03-01 12:03 AM

0 Likes
0
1380
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:18 PM . Last Modified: ‎2024-03-01 12:03 AM

Terry,

Thanks for the reply. I'm a bit embarassed that the information was staring back at me from the manual.

The rack we are using has a 3000lb stationary weight capacity, so we're good there. We are on the second floor though, so I'll be sure to discuss with the engineer before we load it up.

Thanks again.

Reply

Link copied. Please paste this link to share this article on your social media post.

Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-07 11:18 PM . Last Modified: ‎2024-03-01 12:03 AM

0 Likes
0
1380
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:18 PM . Last Modified: ‎2024-03-01 12:03 AM

A number of supposedly high-capacity racks have embarassingly small feet or casters which concentrate the floor loading onto very small points. If you look at the picture of my rack that I linked in by first reply, you can see what I mean. In my case, the "floor" under the rack is actually 2 sheets of high-density 3/4" plywood glue-laminated together, laid over 4x4 cribbing which is perpendicular to the floor joists. However, these cabinets are in my [spare] residential dining room with a regular wood floor, so if you are in an office building this will be less critical. But check just to make sure.

The other concern with heavy stuff higher up in racks is that it moves the center of gravity higher. I doubt your rack is going to tip over if you slide something like a 2RU server out the front of the cabinet laughing, but you should check to see what method is used for servicing the batteries. I doubt the whole unit slides out (instead, there are likely removable battery packs within the chassis) but if you do something like replace all of the batteries at once, you have a 640 lb UPS up near the center of the rack and mostly-empty space between it and the 260 lb transformer at the bottom of the rack, which could get "interesting".

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-07 11:18 PM . Last Modified: ‎2024-03-01 12:03 AM

0 Likes
0
1381
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:18 PM . Last Modified: ‎2024-03-01 12:03 AM

We're in the Carribean so each floor is steel reinforced concrete that is (if I recall) 12 inches thick, but I am waiting to hear back to confirm that.

You're absolutely right about the rack - the leveling feet are pretty meager. We'll have to see how that pans out.

The battery packs have 8 batteries each that are individually servicable, but we'll be having the APC partner in-country doing our regular maintenance, so I'll leave it to them to do things the Right Way™

Thanks again for your feedback.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore