Hello,
I have a RT 10000XL with 7 battery packs. It performed a self check yesterday and reported fine.
Today, it just turned off the output power and I couldn't even access the web interface. I could ping the IP address, no LEDs were lit but the coolers were running.
After turning it off on the breaker and waiting for some time, It eventually turned on again with a battery fault indication.
Can someone tell me what caused the power off?
Thank you.


Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:38 AM . Last Modified: 2024-03-18 04:16 AM
Hi,
Please provide the event and data logs from the network card.
The information provided show that the UPS failed a self-test but most likely that test was run when the UPS started so would not be the cause of the drop. The information also shows that the batteries where in a discharged state momentarily. This could be caused by week batteries or the load. What is the load percentage?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:38 AM . Last Modified: 2024-03-18 04:16 AM
Hi,
Please provide the event and data logs from the network card.
The information provided show that the UPS failed a self-test but most likely that test was run when the UPS started so would not be the cause of the drop. The information also shows that the batteries where in a discharged state momentarily. This could be caused by week batteries or the load. What is the load percentage?
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.