RS232 comm alarm detected [140B-00A0] alert

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • RS232 comm alarm detected [140B-00A0] alert
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
netadmins
Crewman netadmins
Crewman

Posted: ‎2023-05-11 05:14 AM

0 Likes
1
1442
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-05-11 05:14 AM

RS232 comm alarm detected [140B-00A0] alert

We have a new Smart-UPS Ultra 5-20 kW APC unit that is just a few weeks old and are receiving the following message.

 

Critical - RS232 comm alarm detected [140B-00A0].

 

There is no RS232 port on the unit and nothing plugged into the console port on the front of the unit. We were getting constant emails as it goes from detected to cleared over and over so I had to disable this alert from email.

 

Can you please help us understand what this means and how to fix it?

Attachments
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
netadmins
Crewman netadmins
Crewman

Posted: ‎2023-05-30 05:12 AM

0 Likes
0
1361
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-05-30 05:12 AM

I finally got a response back from Schneider support. They suggested to put the unit in bypass mode and follow the steps in this article to remove the intelligence module.

 

This was their response.

After reviewing the logs our next steps in order to solve this issue would be to please check IM connector (Refer to Modular Ultra Intelligence Module SRYLIM for removal and installation guide) and please after removing please take pictures in order to validate that pins are not bent or damaged.

https://download.schneider-electric.com/files?p_enDocType=User+guide&p_File_Name=SY1_IM_990-6502_EN....

In order to perform this is necessary to put the unit in Maintenance Bypass. In order to receive assertive instructions for this procedure I would advise to please reach us out while near the unit in the following phone number:

Phone: 800-800-4272, option 4, then option 2 

 

Once the unit was back online and completed the self test the SR232 Comm alert was cleared.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
netadmins
Crewman netadmins
Crewman

Posted: ‎2023-05-30 05:12 AM

0 Likes
0
1362
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-05-30 05:12 AM

I finally got a response back from Schneider support. They suggested to put the unit in bypass mode and follow the steps in this article to remove the intelligence module.

 

This was their response.

After reviewing the logs our next steps in order to solve this issue would be to please check IM connector (Refer to Modular Ultra Intelligence Module SRYLIM for removal and installation guide) and please after removing please take pictures in order to validate that pins are not bent or damaged.

https://download.schneider-electric.com/files?p_enDocType=User+guide&p_File_Name=SY1_IM_990-6502_EN....

In order to perform this is necessary to put the unit in Maintenance Bypass. In order to receive assertive instructions for this procedure I would advise to please reach us out while near the unit in the following phone number:

Phone: 800-800-4272, option 4, then option 2 

 

Once the unit was back online and completed the self test the SR232 Comm alert was cleared.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore