Posted: 2023-01-13 04:21 AM . Last Modified: 2023-01-13 04:22 AM
APC 10KVA UPS alarming RBC health near end of life. What should I do?
Posted: 2023-01-18 04:11 AM
Hi @gmusanje ,
How old is your battery? You can see the battery installation date of your battery from the UPS display About menu. If the installation date is ~4 years, you will need to replace the batteries.
If the installation date is incorrect, you may have to update it by uninstalling your batteries then install again. A prompt will show up that it detects new batteries and set your new battery installation date. Once set, do a self-test from Test and Diagnostics menu. After that, check the battery installation date again on About tab if its now showing with correct dates.
Posted: 2023-01-18 04:17 AM
Hello,
Thank you for your response.
I installed my batteries on 1st September 2021 and after installation it showed my next battery replacement date as 03/03/2026.
Posted: 2023-01-18 05:09 AM
You may need to create a ticket to your local support for this for thorough checking, in this case. Please access www.apc.com and Contact Us under Support tab.
Posted: 2023-01-18 05:21 AM
Okay let me do that.
Thank you