APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-28 08:44 AM . Last Modified: ‎2024-03-17 11:50 PM
Hello,
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-28 08:44 AM . Last Modified: ‎2024-03-17 11:50 PM
OK, perfect. I will add AP9630 NMC in my cart, I have already bought SMT-1500IC.
Thank you.
Miguel
PS: Maybe SmartConnect capabilities was unnecessary because redundant with AP9630
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-28 08:44 AM . Last Modified: ‎2024-03-17 11:50 PM
Hi,
SmartConnect is designed to communicate with the Schneider Electric Cloud to allow you to monitor the Smart-UPS and provides notifications. SmartConnect is not designed as a management tool. If you would like to configure the UPS remotely and command outlet groups on and off you will need to install a network management card. The AP9630 allows for monitoring and management of the UPS via the local network.
On 8/27/2018 4:51 PM, Miguel said:- to power on/off remote devices: the devices connected in group 1 must be managed together or separately ?
To power on/off the outlet groups you will connect to the NMC. The NMC allow the ability to turn on/off just group 1 or if command the main then all outlets are turned on/off. The groups have delays and those setting are also configure through the NMC.
On 8/27/2018 4:51 PM, Miguel said:I have a IP relay box already but sometimes mine hangs. I would like to use SMT1500IC to reset the power of the relaybox without access to my local computer.
As an example: if you connect the IP relay to group 1 and the local computer to the main you could power cycle group 1 to get it back on line. This would not affect the main so the local computer will remain up.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-28 08:44 AM . Last Modified: ‎2024-03-17 11:50 PM
OK, perfect. I will add AP9630 NMC in my cart, I have already bought SMT-1500IC.
Thank you.
Miguel
PS: Maybe SmartConnect capabilities was unnecessary because redundant with AP9630
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.