Question on Testing Individual Batteries

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Question on Testing Individual Batteries
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 12:27 PM . Last Modified: ‎2024-03-15 04:06 AM

0 Likes
4
1017
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:27 PM . Last Modified: ‎2024-03-15 04:06 AM

Question on Testing Individual Batteries

I need some help. I'm somewhat of a newbie to UPSs and batteries, and the boss has tapped me to become an expert (on the job training). We're working with mainly old/used SU2200RM3U units, and I'm finding myself having weekly battles with them to keep them all running properly. My main problem seems to be with the batteries. Is there a way to test individual batteries under load before I actually put them into a UPS? Also, what's the best way of finding out who the local UPS/battery expert in my town is, the phone book isn't really being all that helpful? Thanks for your time.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 12:28 PM . Last Modified: ‎2024-03-15 04:06 AM

0 Likes
0
1017
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:28 PM . Last Modified: ‎2024-03-15 04:06 AM

"48v nominal" is about as abstract as "2 x 4" lumber, which doesn't actually measure 2.00" by 4.00".

Take a DVM with 0.5% or better accuracy. For 48v battery, if new batteries reads less than 50.3v, return to supplier. Fully charged, the batteries should be >51.2v (after 24 hour rest). There's a relationship between resting state voltage and state-of-charge and the type of batteries used in UPS happen to be easily damaged by being left in less than fully charged conditions. If you read <50.3v, that battery pack has sat around in the warehouse too long and there's a good chance the performance is deteriorated. A new old stock battery that sat in a 80 degree warehouse for a year is not acceptable.

If you MUST stockpile extra batteries, top them off on a charger every 3-6 months or risk severely damaging them in storage. Hotter the temperature, more frequently you need to charge them.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Anonymous user
Not applicable

Posted: ‎2021-06-28 12:28 PM . Last Modified: ‎2024-03-15 04:06 AM

0 Likes
0
1017
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:28 PM . Last Modified: ‎2024-03-15 04:06 AM

Hello,

The UPS contains an RBC12 battery pack and the best way to determine if the battery is good, is by installing the the battery into the UPS and initiating a self test with a load attached. The UPS has hot-swappable batteries so the load does not need to be shutdown for replacement.
If you want to test the battery before installing in a UPS, you can hook a voltmeter to the contacts, make sure there is proper voltage. It should register 48V DC nominal.

Thank you.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 12:28 PM . Last Modified: ‎2024-03-15 04:06 AM

0 Likes
0
1019
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:28 PM . Last Modified: ‎2024-03-15 04:06 AM

Sorry,

I forgot to include the following link to locate an APC Reseller in your area that can provide local information about your APC UPS and the internal batteries. Thanks again:

http://www.apc.com/tools/locator/

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 12:28 PM . Last Modified: ‎2024-03-15 04:06 AM

0 Likes
0
1019
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:28 PM . Last Modified: ‎2024-03-15 04:06 AM

I need some help. I'm somewhat of a newbie to UPSs and batteries, and the boss has tapped me to become an expert (on the job training). We're working with mainly old/used SU2200RM3U units, and I'm finding myself having weekly battles with them to keep them all running properly. My main problem seems to be with the batteries. Is there a way to test individual batteries under load before I actually put them into a UPS? Also, what's the best way of finding out who the local UPS/battery expert in my town is, the phone book isn't really being all that helpful? Thanks for your time.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 12:28 PM . Last Modified: ‎2024-03-15 04:06 AM

0 Likes
0
1018
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:28 PM . Last Modified: ‎2024-03-15 04:06 AM

"48v nominal" is about as abstract as "2 x 4" lumber, which doesn't actually measure 2.00" by 4.00".

Take a DVM with 0.5% or better accuracy. For 48v battery, if new batteries reads less than 50.3v, return to supplier. Fully charged, the batteries should be >51.2v (after 24 hour rest). There's a relationship between resting state voltage and state-of-charge and the type of batteries used in UPS happen to be easily damaged by being left in less than fully charged conditions. If you read <50.3v, that battery pack has sat around in the warehouse too long and there's a good chance the performance is deteriorated. A new old stock battery that sat in a 80 degree warehouse for a year is not acceptable.

If you MUST stockpile extra batteries, top them off on a charger every 3-6 months or risk severely damaging them in storage. Hotter the temperature, more frequently you need to charge them.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore