On the online specs for the APC 100kW Modular Power Distribution Unit, Isolation Transformer, 480:208V, 72 Poles, MBP, 1 Subfeed (part no. PDPM100G6F-M) it states that:
Maximum Line Current per phase: 159A
Maximum Input Current per phase: 146A
and then on the single line diagram it states that the nominal current is 165A
link to specs: http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=PDPM100G6F-M
link to SLD (page 3 for fpds): http://www.apcmedia.com/salestools/KCHY-85VEFD_R2_EN.pdf
Can someone explain what the difference is between all 3 of these terms?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:10 AM . Last Modified: 2024-03-19 01:06 AM
I suspect its some bad technical editing. I'd just ensure your MIB is 175A and you should be fine.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:10 AM . Last Modified: 2024-03-19 01:06 AM
I suspect its some bad technical editing. I'd just ensure your MIB is 175A and you should be fine.