Question: ACPA4000 compressor cycling and noise dampening

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Question: ACPA4000 compressor cycling and noise dampening
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 03:12 AM . Last Modified: ‎2024-02-14 10:30 PM

0 Likes
2
871
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:12 AM . Last Modified: ‎2024-02-14 10:30 PM

Question: ACPA4000 compressor cycling and noise dampening

Hi.
I have a question regarding our NetworkAIR ACPA4000.We just installed this in our small server room. We just relied on fans before - i know not a good idea, so I have very little experience with cooling. The unit cools the room quite quickly so I think it has more than enough capacity. My question is the compressor seems to run for about 10 minutes then the compressor stops and the fan continues, but only for 1 minute then the compressor runs again for approx 10 minutes, then off for 1 min, and it continually cycles like this. Is this normal behavior for these units? As I mentioned I have nothing to compare this to. We have the set point at 63 degrees with the max dead band of 3 degrees. We tried various combinations of set point, dead band and low and high fan , which have not had any effect. The only reason this is an issue is the unit is quite loud ( we have both the supply and exhaust piped to our office plenum), and when the unit transitions from compressor on and off the noise is more annoying - if it ran continually i think the noise would become more of a constant background noise that a person could become accustomed too. So to summarize, is the compressor on for 10 min off for 1 min cycle normal or is there some configuration issue? Second is there some way to dampen the air flow noise without restricting the airflow?

Any advice would be appreciated.
thanks

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 03:13 AM . Last Modified: ‎2024-02-14 10:30 PM

0 Likes
0
871
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:13 AM . Last Modified: ‎2024-02-14 10:30 PM

Hi
Thanks for the advice, i called and the tech explained that it is most likely that the cooler is not getting enough of a heat load on the intake, so the compressor shuts down. The room layout restricts us to much of what we can do, so I am going to have to be creative in directing the heat from the rack to the cooler. I pretty much have the placement of the cooler backwards to what I probably need. I was more concerned with the placement of the hoses for the condenser I did not give much thought to the air flow to and from the unit itself.

thanks again
Dave

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 03:12 AM . Last Modified: ‎2024-02-14 10:30 PM

0 Likes
0
871
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:12 AM . Last Modified: ‎2024-02-14 10:30 PM

Hi,

Sorry for the delay. I've sent an email to our cooling tech support team and hope to have something for you later today.

Update:

They asked that you call into them and speak to them regarding this:

888-695-6500

Thanks

Message was edited by: The Notorious K.M.P.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 03:13 AM . Last Modified: ‎2024-02-14 10:30 PM

0 Likes
0
872
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:13 AM . Last Modified: ‎2024-02-14 10:30 PM

Hi
Thanks for the advice, i called and the tech explained that it is most likely that the cooler is not getting enough of a heat load on the intake, so the compressor shuts down. The room layout restricts us to much of what we can do, so I am going to have to be creative in directing the heat from the rack to the cooler. I pretty much have the placement of the cooler backwards to what I probably need. I was more concerned with the placement of the hoses for the condenser I did not give much thought to the air flow to and from the unit itself.

thanks again
Dave

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore