APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Posted: ‎2021-07-08 02:01 AM . Last Modified: ‎2024-02-29 10:22 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-07-08 02:01 AM . Last Modified: ‎2024-02-29 10:22 PM
I bought a Smart-UPS 2200 from a brother who has hardly used it, I has sensitivity issues because of the use of a generating set. I downloaded the PowerChute business edition software so I can adjust the sensitivity. The software is asking for Username and password which my brother never put in and I havent. How do i generate username and password? thank you.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-07-08 02:01 AM . Last Modified: ‎2024-02-29 10:22 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-07-08 02:01 AM . Last Modified: ‎2024-02-29 10:22 PM
Thanks, everything is done, from the display panel I also set to poor power input. The power is sable now.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-07-08 02:01 AM . Last Modified: ‎2024-02-29 10:22 PM
Hi,
When you install PowerChute Business Edition you are required to enter a user name and password. there is no default user name or password. If you do not know the user name and password that was entered when the software was installed you should uninstall the software and reinstall being sure to note the user name and password entered.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-07-08 02:01 AM . Last Modified: ‎2024-02-29 10:22 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-07-08 02:01 AM . Last Modified: ‎2024-02-29 10:22 PM
Thanks, everything is done, from the display panel I also set to poor power input. The power is sable now.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.