Purchased multiple Smart-UPSes, one has ancient manuf. date and battery is already past replace date?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Purchased multiple Smart-UPSes, one has ancient manuf. date and battery is already past replace date?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
TanerH
Crewman TanerH
Crewman

Posted: ‎2023-10-03 11:15 PM

0 Likes
3
1255
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-10-03 11:15 PM

Purchased multiple Smart-UPSes, one has ancient manuf. date and battery is already past replace date?

Hello,

I just purchased three Smart-UPS devices - one 750C and two 1500C's.  While the 750C and one of the 1500C's had reasonable manufacture dates, the other 1500C has a manuf. date of "Aug 19, 2016", and states "replace battery by "May 27, 2021". (!!)

 

These were all purchased via the "APC Store" on Amazon (cf. https://www.amazon.com/stores/page/127BCCE4-EDD6-4FE9-AC3D-8E1531BED572 ).

 

I also noticed that during initial boot, the setup wizard did not ask me for the current date (whereas the other 1500C and the 750C did ask me, one was almost spot-on, the other was off by a month-ish). 

 

Can anyone either reassure me that this battery will actually last ~4-5 years (which is what the 750C and the other 1500C says - "replace by April 2028"), or do you suggest I contact APC(?) about this in some way? 

I feel like I might have somehow gotten a refurb or something?  Sort of disappointing.

Thanks,

 

-Taner

Labels
  • Labels:
  • Smart-UPS & Symmetra LX-RM
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
TanerH
Crewman TanerH
Crewman

Posted: ‎2023-10-06 01:06 AM

0 Likes
0
1229
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-10-06 01:06 AM

I actually ended up contacting APC support and resolving this (for the most part).

Based on the unit's serial number, it was actually manufactured in 2022, even though the unit self-reports as 2016 for some reason.

The battery was actually manufactured in 2023, and so it's brand new.

I had to go through a few "brain dead reset" procedures for the UPS, and unplugged/replugged the Battery (or just used the battery disconnect on the back - much easier) in order to correctly set the "battery start date".  The reason I needed to do several was because the input would "time out" as I was scrolling from some date in 2016 and trying to reach 2023 (it goes ONE DAY AT A TIME).  So I had to do it in 3 steps.  For some weird reason, this unit would only ask me once for the "new date" after telling it "yes" to "is this a new battery?" after reconnecting it.  I had to do a Brain-Dead reset after each to slowly progress things.

Now, the unit is all green in SmartConnect and correctly reports a sane battery replace date.

I am still mildly concerned that the unit is reporting a 2016 manufacture date, and also curious why it claims it's on the latest firmware when they OTHER 1500C just updated to a new version.  I'm still waiting to hear back from APC support on that.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
LarryK
Lt. Commander LarryK
Lt. Commander

Posted: ‎2023-10-05 10:42 AM

0 Likes
0
1242
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-10-05 10:42 AM

Despite being the "APC" page, various organizations sell the devices and Amazon ships them.

You'd have to take this question up with the actual seller. 

Reply

Link copied. Please paste this link to share this article on your social media post.

TanerH
Crewman TanerH
Crewman

Posted: ‎2023-10-06 01:06 AM

0 Likes
0
1230
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-10-06 01:06 AM

I actually ended up contacting APC support and resolving this (for the most part).

Based on the unit's serial number, it was actually manufactured in 2022, even though the unit self-reports as 2016 for some reason.

The battery was actually manufactured in 2023, and so it's brand new.

I had to go through a few "brain dead reset" procedures for the UPS, and unplugged/replugged the Battery (or just used the battery disconnect on the back - much easier) in order to correctly set the "battery start date".  The reason I needed to do several was because the input would "time out" as I was scrolling from some date in 2016 and trying to reach 2023 (it goes ONE DAY AT A TIME).  So I had to do it in 3 steps.  For some weird reason, this unit would only ask me once for the "new date" after telling it "yes" to "is this a new battery?" after reconnecting it.  I had to do a Brain-Dead reset after each to slowly progress things.

Now, the unit is all green in SmartConnect and correctly reports a sane battery replace date.

I am still mildly concerned that the unit is reporting a 2016 manufacture date, and also curious why it claims it's on the latest firmware when they OTHER 1500C just updated to a new version.  I'm still waiting to hear back from APC support on that.

Reply

Link copied. Please paste this link to share this article on your social media post.

CourtKPrin
Crewman CourtKPrin
Crewman

Posted: ‎2023-10-16 03:12 PM

0 Likes
0
1189
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-10-16 03:12 PM

I had a similar issue with a SCL500RM1UNC purchased via CDW this month. The serial number didn't match what the sticker or box showed. The NMC showed an old manufacturer date (2018?) for the UPS too. I contacted support, tried the factory reset of the NMC, but ended with an RMA. I'm guessing there are some manufacturing issues.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore