Protected Object This object on the APC Management Web Server is protected.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Protected Object This object on the APC Management Web Server is protected.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:41 AM . Last Modified: ‎2024-03-13 01:32 AM

0 Likes
9
39339
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:41 AM . Last Modified: ‎2024-03-13 01:32 AM

Protected Object This object on the APC Management Web Server is protected.

Hi friends

We just got a new SMART-UPS RT 5000 XL up and running (partially). I am not on site with the device but I have a guy I can coordinate to.

He managed to connect via serial and configure a static IP, subnet, gateway, etc.

However, when I try to connect to the IP in a browser it gives the above error message (seen in attachment too).

Some forums advised to change the home.htm in the address bar to logout.htm but it didn't work (this is for when other users might still be logged in).

He reconnected via serial and opened the SSH port so now I can fiddle around with that, but I am not familiar enough with it to go messing around.

I've also managed to import the device to InfraStruXure manager but it shows up as unknown. When I try to connect to the device via ISX manager it says that someone might already be logged in. (second attachment)

We have also rebooted the device/management card.

Just wondering if anyone is familiar with the error and knows of anything I can try to try and resolve this. This error stops us from getting to the login page so we are unable to configure anything via the webpage.

Thanks in advance.

Daniel

Attachments
Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Joszue
Crewman Joszue
Crewman

Posted: ‎2021-11-11 08:48 AM . Last Modified: ‎2021-11-11 08:49 AM

In response to BillP
0 Likes
3
38635
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-11-11 08:48 AM . Last Modified: ‎2021-11-11 08:49 AM

Hi everybody,

 

I had the same problem and got around it using PuTTY with the Telnet protocol.

 

Using the 'web' command here is the result:

 

apc>web
E000: Success
Http: disabled
Https: disabled
Http Port: 5031
Https Port: 443
Minimum Protocol: TLS1.1

 

As you can see Web access was disabled.

 

You can enable it by typing:

 

web -h enable (for http access) or

web -s enable (for https access)

 

And you can use web ? for more options.

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:41 AM . Last Modified: ‎2024-03-13 01:32 AM

0 Likes
0
39288
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:41 AM . Last Modified: ‎2024-03-13 01:32 AM

Hi Daniel,

 

I would suggest try to log into your NMC using an Internet browser using http:// rather than https://

http://XX.XXX.XXX.XX instead of https://XX.XXX.XXX.XX

 

The image you have attached (protected Object)

 

 

Normally means that HTTPS is enabled.

Once you have gained access to your card follow Configuration > network > web > access

Here in the web settings you can enable HTTP

If you cannot gain access, can you log into your card using TelNet?

 

Kindest Regards,

Richard…

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:41 AM . Last Modified: ‎2024-03-13 01:32 AM

0 Likes
4
39288
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:41 AM . Last Modified: ‎2024-03-13 01:32 AM

Hey Richard

Thanks for your response!

Ok so I just tried http and unfortunately that doesn't work. I get the same error as before.

I tried to connect via Telnet using putty but got the below message. I get similar errors for Raw and RLogin. SSH seems to let me in though. Can I enable http via SSH?

=================

PuTTY Fatal Error

Network error: Connection refused.

=================

Much appreciated.

Daniel

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-29 04:41 AM . Last Modified: ‎2024-03-13 01:32 AM

0 Likes
0
39289
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:41 AM . Last Modified: ‎2024-03-13 01:32 AM

Whoever set up the card probably disabled insecure protocols like http and telnet. I would try connecting via https:// or reset the card to defaults via SSH.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:41 AM . Last Modified: ‎2024-03-13 01:32 AM

0 Likes
0
39289
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:41 AM . Last Modified: ‎2024-03-13 01:32 AM

I checked that with the guy that set it up but he said he wasn't prompted to disable anything. He wouldn't have done so without me saying as he was operating under my instruction in regards to installing and configuring the device. Quite odd. Might give Schneider a call again tomorrow to see if anyone over the phone knows.

Thanks for your help so far everyone.

Daniel

Reply

Link copied. Please paste this link to share this article on your social media post.

Joszue
Crewman Joszue
Crewman

Posted: ‎2021-11-11 08:48 AM . Last Modified: ‎2021-11-11 08:49 AM

In response to BillP
0 Likes
3
38636
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-11-11 08:48 AM . Last Modified: ‎2021-11-11 08:49 AM

Hi everybody,

 

I had the same problem and got around it using PuTTY with the Telnet protocol.

 

Using the 'web' command here is the result:

 

apc>web
E000: Success
Http: disabled
Https: disabled
Http Port: 5031
Https Port: 443
Minimum Protocol: TLS1.1

 

As you can see Web access was disabled.

 

You can enable it by typing:

 

web -h enable (for http access) or

web -s enable (for https access)

 

And you can use web ? for more options.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

viquar22
viquar22
Cadet

Posted: ‎2024-02-22 02:16 PM

In response to Joszue
0 Likes
0
17138
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-02-22 02:16 PM

Works for me, thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

Garcia25716
Garcia25716
Cadet

Posted: ‎2025-05-15 04:50 PM

0 Likes
0
5823
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-15 04:50 PM

ok its asking to reboot or restart it?  how do I do that?

Reply

Link copied. Please paste this link to share this article on your social media post.

karlmash
Crewman karlmash
Crewman

Posted: ‎2025-06-27 05:12 AM

In response to Joszue
0 Likes
1
4587
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-27 05:12 AM

 

Hi, I'm trying to reenable the HTTP port using a Telnet connectionas unable to connect through web browser after setting to HTTPS and also unable to get the hyperterminal connection to the console port to work.

 

I've tried a few variations of the 'Web' command but can't get it to work, keep getting 'E102 Parameter Error'.

 

Can you help me with this?

 

Screenshot 2025-06-27 130446.png

Reply

Link copied. Please paste this link to share this article on your social media post.

karlmash
Crewman karlmash
Crewman

Posted: ‎2025-07-01 02:22 AM

In response to karlmash
0 Likes
0
4536
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-07-01 02:22 AM

Sorted this now.

 

I hadn't noticed that the -S was a capital.

 

Command to turn on http was:

 

     web -S http

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore