Problems running on a generator

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Problems running on a generator
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:20 PM . Last Modified: ‎2024-03-14 04:37 AM

0 Likes
7
1685
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:20 PM . Last Modified: ‎2024-03-14 04:37 AM

Problems running on a generator

Last week we had the pleasure of the power company disconnecting power from 9am to 3pm.
During that time we ran our site on a 5600watt generator.

The one APC 2200XL with battery pack worked well. Only briefly at the start did it flick back and forth between "on battery" and "normal".
The other APC 2200XL and two APC 2200 and ten APC ES750VA all had problems living with the power from the generator. Every five to ten seconds they would switch between "on battery" and "normal".

I noted the voltage using the APC software was between 118 and 124 volts.

I tried connecting an APC Line conditioner LE1200 between the UPS and the power source. This made no difference.
Other equipment not connected to APC UPS's, like the Xerox 5655 Workstation Copier/FaxMachine/Printer had no problems with the power.

I need to solve this problem for next time the power goes out and we have to switch to the generator.
I could remove the UPS's but I fear damaging the equipment.

Any thoughts would be greatly appreciated.

ps
The generator is a Sears Craftsman 5600 watt
http://shopping.canoe.ca/shop/product--catId_1001973__locale_en__catCrumbIds_1001199-1001981-1001973...

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • generator
  • power
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:20 PM . Last Modified: ‎2024-03-14 04:36 AM

0 Likes
0
1684
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:20 PM . Last Modified: ‎2024-03-14 04:36 AM

A good thought but I am sure I was not overloading the generator. I measured the load on each UPS with a WattsUp PowerMeature (a real handy device) One of the APC 2200's has only 140 watts of power attached to it. I switched load to the generator in phases. On the first phase with only 1500 watts being used I noticed the UPS problems.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:20 PM . Last Modified: ‎2024-03-14 04:36 AM

0 Likes
0
1684
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:20 PM . Last Modified: ‎2024-03-14 04:36 AM

Slight mistake in this information. The APC 2200XL UPS is a 1.1KW, not 11KW, capacity. There is no problem since the actual rating is only 20% of the generator's capacity.

Reply

Link copied. Please paste this link to share this article on your social media post.

upsguy_apc
Commander upsguy_apc
Commander

Posted: ‎2021-06-28 10:20 PM . Last Modified: ‎2024-03-14 04:36 AM

0 Likes
0
1684
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:20 PM . Last Modified: ‎2024-03-14 04:36 AM

If you read the first post he had 14 UPS's on the generator.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:20 PM . Last Modified: ‎2024-03-14 04:36 AM

1 Like
1
1684
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:20 PM . Last Modified: ‎2024-03-14 04:36 AM

have you tried lowering the sensitivity on these units? the UPSs have a sensitivity setting that can be adjusted.

[here is some info on what sensitivity is|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=62]

to adjust it on a Smart UPS:

Press the voltage sensitivity button (rear panel). Use a pointed object (such as a pen) to do so. You can also change the sensitivity level through Powerchute software.

Notice the green sensitivity LED..

Brightly lit: UPS is set to high sensitivity (default).
Dimly lit: UPS is set to medium sensitivity.
Off: UPS is set to low sensitivity.

On the Back UPS ES 750 (if its a BE750BB), you will need to adjust this via powerchute personal edition. Once you configure that, you can adjust the setting. If its a BE750G, you can adjust it by doing the following:

1. Plug the Back-UPS into the utility power source. The Back-UPS will be in “Standby mode” (no indicators are lit).
2. Press the ON/OFF push button fully in for 10 seconds. The Online LED will begin glowing in a cyclical order: GREENAMBER-RED, indicating it is going into “Program mode”.
3. The Back-UPS will then indicate the current sensitivity, as shown in the Transfer Voltage and Sensitivity Adjustment table below.
4. To select the LOW sensitivity setting, press the ON/OFF push button until the LED begins flashing GREEN.
5. To select the MEDIUM sensitivity setting, press the ON/OFF push button until the LED begins flashing RED.
6. To select the HIGH sensitivity setting, press the ON/OFF push button until the LED begins flashing AMBER.
7. To exit Programming mode, once sensitivity is set, wait approximately 5 seconds, and all of the LED indicators will be
off (unlit).

if you have done this, and it still doesnt work, then the power is too dirty from the generator for the UPS and there isnt anything else to really try..you'd have to fix it on the generator end or get some UPSs that can accept a wider range of voltage (like a Double Online Conversion UPS depending on the severity of this issue)

Reply

Link copied. Please paste this link to share this article on your social media post.

upsguy_apc
Commander upsguy_apc
Commander

Posted: ‎2021-06-28 10:20 PM . Last Modified: ‎2024-03-14 04:36 AM

0 Likes
0
1684
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:20 PM . Last Modified: ‎2024-03-14 04:36 AM

The main problem I see is that you have 11kw of UPS on 5.6kw of generator. Even though you may no have the full load of 5.6kw on the UPS your may possibly be overdriving your generator and that could cause frequency and phase shift issues which could play all kinds of havoc on your UPS's.

UPS's use more current than they provide to your load so even though you may only see a sum of 5kw on all of your UPS's you could easily be putting 6-7kw of load of the generator.

my 2 cents. next time shed some load and see what happens. "shed load" aahhh screams the IT guy.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:20 PM . Last Modified: ‎2024-03-14 04:36 AM

0 Likes
0
1684
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:20 PM . Last Modified: ‎2024-03-14 04:36 AM

Good information. Much appreciated. I will try lowering the sensitivity on the UPS's

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:20 PM . Last Modified: ‎2024-03-14 04:36 AM

0 Likes
0
1685
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:20 PM . Last Modified: ‎2024-03-14 04:36 AM

A good thought but I am sure I was not overloading the generator. I measured the load on each UPS with a WattsUp PowerMeature (a real handy device) One of the APC 2200's has only 140 watts of power attached to it. I switched load to the generator in phases. On the first phase with only 1500 watts being used I noticed the UPS problems.

Reply

Link copied. Please paste this link to share this article on your social media post.

RobRut
RobRut
Cadet

Posted: ‎2022-07-17 05:10 PM

In response to BillP
0 Likes
0
1427
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-07-17 05:10 PM

Thank you so much! I had a similar issue and lowered the sensitivity (based on your suggestion and instructions); now, all four Smart UPSs work great! I can't thank you enough!

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of