Problem with firmware upgrade on ap9606

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Problem with firmware upgrade on ap9606
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 05:42 AM . Last Modified: ‎2024-03-08 02:03 AM

0 Likes
8
1449
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:42 AM . Last Modified: ‎2024-03-08 02:03 AM

Problem with firmware upgrade on ap9606

I recently upgraded the firmware on my ap9606 which is installed in a SmartUps SU5000RM. It was running version 301 (I think). I uploaded version aos326b.bin via an xmodem hyperterm sesion. The update seems to have taken as it now shows "Web/SNMP Management Card AOS v3.2.6.b" on the main screen when I log in via hyperterm or telnet in over the network.

My problem is that now the ap9606 seems to no long be communicating with the ups and the web interface is no longer working.

The only option after loging in as admin are -

1- Device Manager
2- Network
3- System
4- Logout

#1 when selected shows nothing
#2 will let me setup networking, which seems to work fine except there is no web login
#3 seems to have all the normal options available for setting up different things
1- User Manager
2- Identification
3- Date/Time
4- File Transfer
5- Tools
6- About System
#4 of course logs you out.

There is no information regarding the ups status or anything else about the ups itself. so I assume the AP9606 is not able to communicate with the ups anymore since it was upgraded to aos326b.bin. I used to see all the info regarding the ups itelf before upgrading.

After reading another thread on this site it seems like there should have been a sumx326.bin to go along with the aos326b.bin? There is no sumx326.bin anywhere on the apc website that I could find. The only file listed under firmware upgrades for the ap9606 was the aos326b.bin, nothing else. No instrunction (found them in the knowlege base), upload utilites or update notes or anything like that that are available with the ap9617 update.

I am guessing the ap9606 has lost communications with the ups because the existig version of the sumx file on the ap9606 is not compatable with the aos326b.bin update? I believe the aos file is the operating system and the sumx is the application, which would explain why I no longer have a web interface...

The usual steps of braindeading the ups and reseating the ap9606 have been tried with no change.

Any help would be much appreciated.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:42 AM . Last Modified: ‎2024-03-08 02:03 AM

0 Likes
0
1449
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:42 AM . Last Modified: ‎2024-03-08 02:03 AM

Hi,

as far as I can tell, you can use it with your silcon.

here is the link: ftp://ftp.apc.com/apc/public/hardware/webcard/firmware/security/v326b/

that has the AOS and the APP file for dp3e236a.

i dont have the actual release notes available for what exactly is fixed but that is the latest firmware this is supported for the AP9606. there are little bugs and fixes all of the time.

anyone looking at this, just make sure you have the AP9606 before you upgrade to this firmware.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
Anonymous user
Not applicable

Posted: ‎2021-06-30 05:42 AM . Last Modified: ‎2024-03-08 02:03 AM

0 Likes
0
1449
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:42 AM . Last Modified: ‎2024-03-08 02:03 AM

Thank you for that link. I wonder why there seems to be no reference to it on the APC website though...

Also, to upload this, is it exactly the same procedure as for the AOS file? I used the Xmodem method via a Hyperterm session to upload the AOS file. Does it automatically know where to put each file and what they are used for? I don't want to accidently make the management card unusable by uploading the sumx file when it is expecting an aos file instead.

Oh, and while I have your attention, what version of the Powerchute software should I run for basic shutdown of the PC's attached to this ups? I only need them to be signaled to shutdown over the network when there is an extended outage. I don't need any fancy features. I did load Powerchute Network Shutdown onto one PC and that is when I found out there seemed to be an issue with it and the older firmwhere on my managment card so I didn't play with to much. Is Network Shutdown actually able to shutdown the PC it is installed on or is its purpose only for communicating to other PC's on the network?

Thanks
Craig,

Message was edited by: cage-au

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 05:42 AM . Last Modified: ‎2024-03-08 02:03 AM

0 Likes
0
1449
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:42 AM . Last Modified: ‎2024-03-08 02:03 AM

SUMX file located here:


ftp://ftp.apc.com/apc/public/hardware/webcard/firmware/sumx/v326/

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 05:42 AM . Last Modified: ‎2024-03-08 02:03 AM

0 Likes
0
1449
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:42 AM . Last Modified: ‎2024-03-08 02:03 AM

I can answer one part now and the software part tomorrow when I'm not trying to shoot from the perverbial memory hip. Load the SumX via X-Modem. There are no directories within the flash of the card, so it's all stored on the "root" essentially. If there's a problem, re-flash the AOS afterwards.


I'll let you know about the software tomorrow, but PCNS 2.2.1 should work.

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 05:42 AM . Last Modified: ‎2024-03-08 02:03 AM

0 Likes
0
1449
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:42 AM . Last Modified: ‎2024-03-08 02:03 AM

From the installation guide for PCNS 2.2.1. (And should be for subsequent releases of the software):

For requirements:

"An APC Network Management Card (APC part number AP9617, AP9618, or AP9619) with a firmware revision of 1.1.0 or later OR an *APC Web/SNMP Card (APC part number AP9606).*"

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 05:42 AM . Last Modified: ‎2024-03-08 02:03 AM

0 Likes
0
1449
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:42 AM . Last Modified: ‎2024-03-08 02:03 AM

Thank you very much for your help. I have the firmwares succesfully updated and working now. Just need to install and configure PSNS.

APC's official tech support where of little use in helping me with this firmware upgrade. Seems 90% of all companies these days outsource their tech support to offices in India where no one actaully knows much about the products they are supposed to be supporting.

Thanks again
Craig,E

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 05:42 AM . Last Modified: ‎2024-03-08 02:03 AM

0 Likes
0
1449
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:42 AM . Last Modified: ‎2024-03-08 02:03 AM

Sorry about your experience. But they are trained in the same manner that we here in the states are. They are an actual part of the APC-MGE company, not just outsourced people.

But I am official APC support...in fact, more official than they.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 05:42 AM . Last Modified: ‎2024-03-08 02:03 AM

0 Likes
0
1449
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:42 AM . Last Modified: ‎2024-03-08 02:03 AM

What if any benifits will i get if i update firmware from v3.0.1 to up-to-date and will it comunicate with silcon dp320e

Message was edited by: deeman13

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:42 AM . Last Modified: ‎2024-03-08 02:03 AM

0 Likes
0
1450
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:42 AM . Last Modified: ‎2024-03-08 02:03 AM

Hi,

as far as I can tell, you can use it with your silcon.

here is the link: ftp://ftp.apc.com/apc/public/hardware/webcard/firmware/security/v326b/

that has the AOS and the APP file for dp3e236a.

i dont have the actual release notes available for what exactly is fixed but that is the latest firmware this is supported for the AP9606. there are little bugs and fixes all of the time.

anyone looking at this, just make sure you have the AP9606 before you upgrade to this firmware.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore