Problem with an AP5717 and AP5201

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Problem with an AP5717 and AP5201
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 07:01 AM . Last Modified: ‎2024-03-18 12:59 AM

0 Likes
9
2415
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:01 AM . Last Modified: ‎2024-03-18 12:59 AM

Problem with an AP5717 and AP5201

Last night we had to power off our rooms. Since everythign has powered back on I can't get my APC console working.

If I plug a monitor, keyboard and mouse into the AP5201, it works fine. The AP5717 doesn't work though. It appears to be stuck in standby. I've tried restarting it all. Everything appears ok. I have to be missing something really simple. Any ideas?

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 07:02 AM . Last Modified: ‎2024-03-18 12:58 AM

0 Likes
0
2415
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:02 AM . Last Modified: ‎2024-03-18 12:58 AM

One of them has PS2. I can go over and try that in a few.

That is correct about the login screen. It won't show that even. Only when I plug in the external monitor.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:02 AM . Last Modified: ‎2024-03-18 12:59 AM

0 Likes
0
2415
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:02 AM . Last Modified: ‎2024-03-18 12:59 AM

What LED indicators do you see and what's on the screen? Basically, why do you say it's stuck in standby - what is telling you that?

I know you said you've tried restarting it all but I am wondering the specific order. I would power off the AP5201 KVM and the AP5717 Rack LCD and then go ahead and turn on the Rack LCD first and then the KVM and see if that changes everything.

Lastly, if you press the exit button once to auto-adjust - any change? And if you press the menu button, can you tell me the display firmware? i.e. 6.8 or similar.

Thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:02 AM . Last Modified: ‎2024-03-18 12:59 AM

0 Likes
0
2415
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:02 AM . Last Modified: ‎2024-03-18 12:59 AM

The indicator I get is the power button on the LCD lighting up orange.

I went over and powered both off and brought them back in the order you suggested. LCD followed by the KVM. Still no luck. On the LCD I got a message saying it was turning the LCD on. then No Input.

When I push Exit or Menu, nothing happens.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:02 AM . Last Modified: ‎2024-03-18 12:59 AM

0 Likes
0
2416
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:02 AM . Last Modified: ‎2024-03-18 12:59 AM

Hm, OK, and since this KVM is PS/2 only, you are using the black DB-15 to VGA PS/2 cable (and not the supplied green DB-15 to VGA PS/2 one with adapters)?

Can you verify the black DB-15 connection on the Rack LCD end too?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:02 AM . Last Modified: ‎2024-03-18 12:58 AM

0 Likes
0
2416
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:02 AM . Last Modified: ‎2024-03-18 12:58 AM

That's correct. Black DB15 on the console to a VGA & PS/2 end on the KVM.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:02 AM . Last Modified: ‎2024-03-18 12:58 AM

0 Likes
0
2416
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:02 AM . Last Modified: ‎2024-03-18 12:58 AM

Can you let me know on that Rack LCD display version firmware I asked for? Also, with the external monitor, what resolution do you have displayed when it works fine there? And what Hz?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:02 AM . Last Modified: ‎2024-03-18 12:58 AM

0 Likes
0
2416
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:02 AM . Last Modified: ‎2024-03-18 12:58 AM

Have you tried to directly connect the AP5717 to one of these servers and bypass the AP5201? (If your servers do not have PS/2, you could try with the green USB cable that came with the AP5717 if you have it still - AP5717->940-5202 cable part number ->server).. If anything, my thought is an issue with the AP5201 since it is on an older platform.

Also, when you power cycle the AP5201, even the 640x480 log in screen for the KVM itself does not show? Hmm..

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:02 AM . Last Modified: ‎2024-03-18 12:58 AM

0 Likes
0
2416
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:02 AM . Last Modified: ‎2024-03-18 12:58 AM

Strange..

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:02 AM . Last Modified: ‎2024-03-18 12:58 AM

0 Likes
0
2416
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:02 AM . Last Modified: ‎2024-03-18 12:58 AM

I have a 1024*768 at 75 MHz running and another at 1024*768 at 60 MHz that both show on a separate monitor plugged in to the KVM with no problems.

I can't get the firmware. Exit and Menu aren't doing anything.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:02 AM . Last Modified: ‎2024-03-18 12:58 AM

0 Likes
0
2416
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:02 AM . Last Modified: ‎2024-03-18 12:58 AM

One of them has PS2. I can go over and try that in a few.

That is correct about the login screen. It won't show that even. Only when I plug in the external monitor.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore