Problem with Smart-UPS 1500RM, showing insufficent runtime available

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Problem with Smart-UPS 1500RM, showing insufficent runtime available
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:03 AM . Last Modified: ‎2024-03-13 11:31 PM

0 Likes
3
1415
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:03 AM . Last Modified: ‎2024-03-13 11:31 PM

Problem with Smart-UPS 1500RM, showing insufficent runtime available

Hi our Smart- UPS 1500 which is about 5 yrs old had a new battery fitted in August & seemed to be ok since.... it runs our email server as well as a couple of switches & runs at around 48-50% load.

In the last few days we have had some weird power surges etc (Sping storms down here) yesterday afternoon at about 5pm we had a power surge which caused the UPS to shutdown the mail server, I checked the logs & it appears that it cycles through having insufficient runtime see below:


12/10/10 16:16:06 Sufficient Runtime Available
12/10/10 16:09:06 Insufficient Runtime Available
12/10/10 16:09:05 Communication Established
12/10/10 16:09:05 Monitoring Started
12/10/10 16:01:33 Monitoring Stopped
12/10/10 16:00:28 Insufficient Runtime Available
12/10/10 16:00:28 Power Restored
12/10/10 16:00:23 Shutdown process started
12/10/10 16:00:23 Low Runtime Remaining
12/10/10 16:00:23 Power Failed
12/10/10 16:00:13 Insufficient Runtime Available
12/10/10 16:00:11 Sufficient Runtime Available
12/10/10 16:00:08 Insufficient Runtime Available
12/10/10 16:00:04 Sufficient Runtime Available
12/10/10 15:59:38 Insufficient Runtime Available
12/10/10 15:59:35 Sufficient Runtime Available
12/10/10 15:59:32 Insufficient Runtime Available
12/10/10 15:58:41 Sufficient Runtime Available
12/10/10 15:58:37 Insufficient Runtime Available
12/10/10 15:58:04 Sufficient Runtime Available



It shows a runtime of 5mins & battery 100% when I replaced the battery I did a calibration via the powerchute console & it ran for about 15mins before shutting down, should I do a manual calibration ie: stop the UPS service & pull the power?

Another anomaly I have noticed is that the event log times are 1hour behind, the server time is correct ie: Australian daylight savings time.

Thank you in advance
Michael

Message was edited by: cokebottle

Message was edited by: cokebottle

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:03 AM . Last Modified: ‎2024-03-13 11:31 PM

0 Likes
0
1414
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:03 AM . Last Modified: ‎2024-03-13 11:31 PM

Hi,
I have some issues with this UPS. I've bought original new APC battery, because UPS indicating, that battery has 0min remaining runtime, even if shows 100% charged. I've done couple runtime calibration and nothing helps. So I've bought new batteries and is the same! I don't know what is wrong, but I spent a lot money for the new batteries and is still not working.

Any ideas?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:03 AM . Last Modified: ‎2024-03-13 11:31 PM

0 Likes
0
1414
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:03 AM . Last Modified: ‎2024-03-13 11:31 PM

Thanks for that, I will do a maunal recal now that I know it is the correct way to do one, also will try to track down the serial cable... I installed the unit & shoved the cable away somewhere.....

Do you have any suggestions regarding the log entries being 1 hr behind the system time? running version 7 of the powerchute software & when I check for updates it says there is none.

Michael

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 01:03 AM . Last Modified: ‎2024-03-13 11:31 PM

0 Likes
0
1414
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:03 AM . Last Modified: ‎2024-03-13 11:31 PM

I can't say for sure about the logging dates, never really had to look at them closely before, but I will update to a later version & see what happens, I presumed because it found no updates it was already at the highest level, I guess I am just more sensitive to DST errors because my IPhone 4 has a bug with its alarm app not updating to DST GRRRR LOL

I will be doing a full shutdown & recal on Monday as I need to come in early & do it when nobody is in the office, we had two power outages yesterday for approx 30secs each 1 hr apart due to an accident in town which blacked out all the traffic lights in the bottom end of town for a couple of hours but it had no affect on us at all, I have disabled the software from shutting down the server for the moment so PHEW!

Michael

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 01:03 AM . Last Modified: ‎2024-03-13 11:31 PM

0 Likes
0
1415
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:03 AM . Last Modified: ‎2024-03-13 11:31 PM

Hi,
I have some issues with this UPS. I've bought original new APC battery, because UPS indicating, that battery has 0min remaining runtime, even if shows 100% charged. I've done couple runtime calibration and nothing helps. So I've bought new batteries and is the same! I don't know what is wrong, but I spent a lot money for the new batteries and is still not working.

Any ideas?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore