Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Problem with Powerchute

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Re: Problem with Powerchute
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5027
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
thomasgeorgem_apc
thomasgeorgem_apc
Cadet

Posted: ‎2021-07-01 03:20 AM

0 Likes
3
198
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:20 AM

Problem with Powerchute

This was originally posted on APC forums on 6/3/2013


Hi,

I have a brand new APC SUA1500I smart UPS. It is connected to a DELL PowerEdge SC440 server.

I have installed and configured the PowerChute Agent, Server and Console as instructed. Set the shutdown time as 'shut down after one minute'

The shutdown was performed perfectly as expected when I tested by turning off the main power to UPS.

But the problem is after turning on the main power to UPS, If I try to start the server it does not turn on.

Also, the LEDs on UPS front panel keep on blinking one by one.

Can anybody assist?

thank you,

Thomas

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 03:20 AM

0 Likes
0
198
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:20 AM

This reply was originally posted by Bill on APC forums on 6/7/2013


Thomas,

When PowerChute shuts down the system it also sends a shutdown signal to the UPS. The UPS will wait a few minutes and then on into sleep mode for roughly 9 minutes and then power down completely. If power is restored when the UPS is in sleep mode it should turn itself back on and begin power the server. If it is not doing that then there is an issue with the UPS.

Again, once the server is off PowerChute is no longer running and cannot control the UPS or the server.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 03:20 AM

0 Likes
0
198
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:20 AM

This reply was originally posted by Bill on APC forums on 6/3/2013


Thomas,

When all of the LEDs are blinking in sequence (top to bottom) that means the UPS is in sleep mode. The UPS will not provide power to the server when in sleep mode. Be sure the UPS is connected to good AC power source. The On line LED should be lit and the battery charge LEDs should be lit. See knowledge base document FA156545 for more information concerning Smart-UPS LEDs http://www.apc.com/site/support/index.cfm/faq/

BTW, the server not powering up has nothing to do with PowerChute. Since the server is powered off the software cannot run / is not running.

Reply

Link copied. Please paste this link to share this article on your social media post.

thomasgeorgem_apc
thomasgeorgem_apc
Cadet

Posted: ‎2021-07-01 03:20 AM

0 Likes
0
198
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:20 AM

This was originally posted on APC forums on 6/7/2013


Hi Bill,

Thank you for the reply. The problem is happening only after a shutdown through powerchute.

To confirm this I tested the UPS by manually shutting down the server when UPS is on battery.

Then turned on the main power and started the server. this time it worked fine.

Also tested after connecting to a different, good Ac power and still the result is same as before.

For your Info, I am using USB cable - 940-0272A.

please advise.

thank you,

Thomas

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 03:20 AM

0 Likes
0
199
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:20 AM

This reply was originally posted by Bill on APC forums on 6/7/2013


Thomas,

When PowerChute shuts down the system it also sends a shutdown signal to the UPS. The UPS will wait a few minutes and then on into sleep mode for roughly 9 minutes and then power down completely. If power is restored when the UPS is in sleep mode it should turn itself back on and begin power the server. If it is not doing that then there is an issue with the UPS.

Again, once the server is off PowerChute is no longer running and cannot control the UPS or the server.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc