Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2902:40 AM. Last Modified: 2024-03-1303:23 AM
Problem with Galaxy 3000
Hello everyone.
I had a problem with my Galaxy system.
when performing test, the system changed from battery operation to normal operation but the EMI Board blew up completly. Several varistor were damaged.
My question is about if it is necessary (or even mandatory) to put the neutral in the input, and if this may be cause for the EMI boatd to blow? The manual says that it is recommended to have a Wye transfo (but no mandatory). The system has no transfo neither the input nor the output. Is it also necessary to check the phase sequence?
Besides, for monitoring the Galaxy 3000 from a DCS, what options do I have?