Prevent batteries from draining during a EPO

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Prevent batteries from draining during a EPO
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 11:21 PM . Last Modified: ‎2024-02-15 12:03 AM

0 Likes
6
986
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 11:21 PM . Last Modified: ‎2024-02-15 12:03 AM

Prevent batteries from draining during a EPO

I work on a campus where we have about 80 units, mixed models of SMT, SRT, SMX, with network management 2 cards backing up POE switches to run our VoIP sets.  Administration wants the phones to stay up during a power outage long enough to evacuate a building. 

Each year they shut the power down for an entire day to perform maintenance on our high voltage distribution.  If I set the config. to shut the outlet groups off after X amount of minutes will the UPS continue to drain the battery to keep itself alive or will it go into a dormant state until it senses voltage on the input?

Looking for advice on the simplest way to keep my batteries from draining.

Thanks,

Curt

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 11:21 PM . Last Modified: ‎2024-02-15 12:03 AM

0 Likes
0
986
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 11:21 PM . Last Modified: ‎2024-02-15 12:03 AM

Excellent, thanks!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 11:21 PM . Last Modified: ‎2024-02-15 12:03 AM

0 Likes
0
986
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 11:21 PM . Last Modified: ‎2024-02-15 12:03 AM

Hi,

How do you plan to power the UPS down? Also, do the UPS have network management cards installed?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 11:21 PM . Last Modified: ‎2024-02-15 12:03 AM

0 Likes
0
986
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 11:21 PM . Last Modified: ‎2024-02-15 12:03 AM

Yup, they all have network management cards installed and are running the current firmware version.  I was hoping there was a way I could configure the unit to shut off after X number of minutes on battery power and then upload the ini file to each unit. However based on my findings it sound like I need to install multiple instances of PCNS to do so based on the number of units I have across campus. 

Since I don't have time to stand up and configure PCNS before we have our annual power shutdown I was going to try and upload an ini file with the one time shutdown parameters, unless someone threw out a better idea?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 11:21 PM . Last Modified: ‎2024-02-15 12:03 AM

0 Likes
0
986
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 11:21 PM . Last Modified: ‎2024-02-15 12:03 AM

Hi,

So do you want to power down server,s the UPS, or both? PCNS is designed to power down servers and it will send a signal to the configured NMC/UPS to power down. If you are looking to power down the UPS that can be accomplished through the NMC. You can also configure the NMC to power down the UPS and send a signal to PCNS clients telling them to power down. 

Depending on the NMC and firmware you could configure the outlet group/s to power off after being on battery for x amount of time. This would be found under Configuration, Outlet Groups, select the outlet groups and go to Load Shedding. If there are any PCNS client assigned to the Outlet group the NMC will send a signal telling the client that it should power down. The outlet group will wait the power off delay and then cut AC. 

Another option if using PCNS is to configure PCNS to start the shutdown process after being on battery for x amount of time and configure PCNS to send a shutdown signal to the outlet group / UPS. The outlet group will wait the power off delay and then cut AC. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 11:21 PM . Last Modified: ‎2024-02-15 12:03 AM

0 Likes
0
984
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 11:21 PM . Last Modified: ‎2024-02-15 12:03 AM

There are no servers behind these units, just POE switches so graceful shutdowns are not required.  I just want to shut the UPS down so the batteries don't drain over the 12 hour power outage.  If I configure the outlet groups to shut off would the UPS continue to drain the battery to keep itself up?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 11:21 PM . Last Modified: ‎2024-02-15 12:03 AM

0 Likes
0
984
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 11:21 PM . Last Modified: ‎2024-02-15 12:03 AM

Hi,

On 4/22/2019 11:49 AM, curt said:

I just want to shut the UPS down so the batteries don't drain over the 12 hour power outage.  If I configure the outlet groups to shut off would the UPS continue to drain the battery to keep itself up?

No. The UPS will cut power to the outlet group after the on battery delay and the power off delays have concluded. It will then go into sleep mode for 10 minutes. While in sleep mode the NMC will still be active i.e access to the UPS over the network will be available. After the 10 minutes the UPS cuts power to the NMC and waits for AC to be restored. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 11:21 PM . Last Modified: ‎2024-02-15 12:03 AM

0 Likes
0
987
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 11:21 PM . Last Modified: ‎2024-02-15 12:03 AM

Excellent, thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of