Powershute and SMC1000-2i

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Powershute and SMC1000-2i
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
113
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:25 AM . Last Modified: ‎2024-03-15 05:55 AM

0 Likes
6
1285
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:25 AM . Last Modified: ‎2024-03-15 05:55 AM

Powershute and SMC1000-2i

Hi,

I 've got an SMC1000-2i and I would need to able to add some delay when the electricity is back online. ( like to switch on the servers after 10 min that the electricity is back ) at the moment I'am writting this post, I cannot find it anymore ????

I'll try to connect powershute on your website and plug with the USB  cable, but the software says that it cannot connect to the SMC.

Is there the right way to do it ?

I don't have any network card on it..

How can I increase this value ?

Thanks in advance

BR, Stéphane

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • powershute
  • smc1000i
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:26 AM . Last Modified: ‎2024-03-15 05:54 AM

0 Likes
0
1285
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:26 AM . Last Modified: ‎2024-03-15 05:54 AM

Hi,

I am not familiar with NUT but impression is no. To configure a SMC to power on when the UPS has a minimum runtime you need to do so through software. PowerChute Business Edition version 10.x offers the ability.

The screenshot below is from PCBE 10.0.1 connected to SMC1500C

bSFdK7nq0%2FjznsluTLN1TQ%3D%3D.pngbSFdK7nq0%2FjznsluTLN1TQ%3D%3D.pngIf you need a Smart-UPS that can be configured to power on when the UPS has a minimum runtime without using software you should look at a SMT Smart-UPS. The SMT has configurable outlet via the LCD panel. 

See Answer In Context

Attachments
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:25 AM . Last Modified: ‎2024-03-15 05:55 AM

0 Likes
0
1285
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:25 AM . Last Modified: ‎2024-03-15 05:55 AM

Hello,

The SMC Smart-UPS is compatible with PowerChute Business Edition. You should connect the UPS back to the system and then run the PowerChute Business Edition installer. 

PowerChute Business Edition can be download from this link. https://www.apc.com/us/en/tools/download/software_comp.cfm?sw_sku=SFPCBE1001

 

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:25 AM . Last Modified: ‎2024-03-15 05:55 AM

0 Likes
0
1285
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:25 AM . Last Modified: ‎2024-03-15 05:55 AM

Hi,

Thanks for your reply.

I've downloaded the software and I've plugged via the USB, to laptop to the SMC1000-2i and while installing powerchute, the software is saying that there is no UPS attached ! ( And I can see a kind of battery on the "latptop / USB connections"

Am I doing something completely stupid ??

Thanks and regards,

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:25 AM . Last Modified: ‎2024-03-15 05:55 AM

0 Likes
0
1285
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:25 AM . Last Modified: ‎2024-03-15 05:55 AM

Hi,

What OS is the laptop running? If Windows please review Schneider Electric FAQ FA310907 and FA283181

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:26 AM . Last Modified: ‎2024-03-15 05:55 AM

0 Likes
0
1285
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:26 AM . Last Modified: ‎2024-03-15 05:55 AM

Hi,

Thanks for you reply. In fact, just to come back on the principe I am looking for.... AT the end, I wish to make sure that when the electricity comes back ( after a long cut...), to deliver the power to the servers after 10min or 20 min.. I planned to use the servers running Linux.. with NUT

And NUT offer this ( according to the config file ) I guess this is the instruction WAKEUP 600 for instance..

But, if you have an electricty cut...Servers are off.. If you are using PowerChute or NUT, How the server will know that it has to start after 600s ? If the software doesn't write INTO the UPS, how it knows this instruction, with NO servers started yet ?????

If you can enlight me, that will be great.. 🙂 Maybe that will help me to search in the right direction....

Thanks and regards,

Stéphane

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:26 AM . Last Modified: ‎2024-03-15 05:55 AM

0 Likes
0
1285
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:26 AM . Last Modified: ‎2024-03-15 05:55 AM

Hi,

Is there anybody who can explain to me how to make sure..that the UPS can deliver power to the servers, after  X minute of return power ?

This will avoid consequences of glitches.... and I don't want to get problems if a server start booting and suddently, another electricity cut arrives.. How this can be handle by software c???? when the UPS is down, no servers are running of course and a software cannot give this instruction to the UPS ?

How can I do that ?

Does PowerChute "write" on the UPS this instruction ??

Thanks for your help

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:26 AM . Last Modified: ‎2024-03-15 05:54 AM

0 Likes
0
1286
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:26 AM . Last Modified: ‎2024-03-15 05:54 AM

Hi,

I am not familiar with NUT but impression is no. To configure a SMC to power on when the UPS has a minimum runtime you need to do so through software. PowerChute Business Edition version 10.x offers the ability.

The screenshot below is from PCBE 10.0.1 connected to SMC1500C

bSFdK7nq0%2FjznsluTLN1TQ%3D%3D.pngbSFdK7nq0%2FjznsluTLN1TQ%3D%3D.pngIf you need a Smart-UPS that can be configured to power on when the UPS has a minimum runtime without using software you should look at a SMT Smart-UPS. The SMT has configurable outlet via the LCD panel. 

Attachments
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of