Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
Powershute Business Edition Auto Discovery - Does Not Pick Up UPS
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-3001:44 AM. Last Modified: 2024-03-1112:32 AM
Powershute Business Edition Auto Discovery - Does Not Pick Up UPS
Hi All,
I have two Smart UPS 5000 RM with Network Management cards installed, I can browse to both cards through a web browser with no issues.
When I install the PowerShute Buisness edition software (latest version) it does not discover either of the devices, the server I have installed the software on is on the same subnet as the devices - see below. When I manually enter the IP addresses of the UPS devices it still says it cannot discover them.
What am I doing wrong? I have installed the PowerShute software on both a x64 Windows 2008 R2 and x64 Win 7 SP1 machines with the same result.
UPS IP #1: 10.7.100.241/16
UPS IP #2: 10.7.100.242/16
Server IP: 10.7.100.6/16
Telnet and HTTP connections to the management cards are fine...
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-3001:44 AM. Last Modified: 2024-03-1112:32 AM
If you're using a network management card, you do not use Powerchute network shutdown. Powerchute business edition communicates over usb or serial where as a network management card communicates over the network. You would need to download powerchute network shutdown if you would like to gracefully shutdown your servers. This can be downloaded from our website under software/firmware
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-3001:44 AM. Last Modified: 2024-03-1112:32 AM
If you're using a network management card, you do not use Powerchute network shutdown. Powerchute business edition communicates over usb or serial where as a network management card communicates over the network. You would need to download powerchute network shutdown if you would like to gracefully shutdown your servers. This can be downloaded from our website under software/firmware
This is a heading
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.