Powerchute PRO and remote server shutdown

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Powerchute PRO and remote server shutdown
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
123
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 11:34 PM . Last Modified: ‎2024-03-12 12:45 AM

0 Likes
3
1083
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:34 PM . Last Modified: ‎2024-03-12 12:45 AM

Powerchute PRO and remote server shutdown

Welcome everyone.

I have two servers connected to one UPS, Smart 2200, both Windows Server 2012 R2 with all upgrades.

UPS power usage is about 9%, I believe it is enough.

Due to fact that the only solution APC offers in that situation is to buy additional network card (very expensive) I looked for other solutions.

I found brilliant solution to use CMD script to send shutdown command to second server via network, APC agent enables to execute CMD script via agent.

So I created script using: @START "" "c:\Windows\system32\shutdown.exe" /s /t 10 /m \\10.0.0.9 as my remote shutdown command.

Here comes funny part, both APC agent and server service logged as Admin with correct pass, all user/pass are correct on both servers.

Running "TEST" from config page gives NO effect, but running script from windows shell CORECTLY closes remote server.

Seems to me that agent have problems passing commands to remote computers.

Found some comments on net that this solution works on earlier operating systems.

Please analyze and explain.

Best Regards.

Mike

P.S. For all of You that may have doubts, of course I am using newest available 9.2 software.

Also it is shameful that great American company sold itself and is not APC anymore.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-29 11:34 PM . Last Modified: ‎2024-03-12 12:45 AM

0 Likes
0
1082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:34 PM . Last Modified: ‎2024-03-12 12:45 AM

Unfortunately even with administrator privileges Microsoft limits service's ability to interact with the desktop. Here's one person's workaround (link).

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:34 PM . Last Modified: ‎2024-03-12 12:45 AM

0 Likes
0
1082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:34 PM . Last Modified: ‎2024-03-12 12:45 AM

Hi,

Most likely the issue is with the permissions of the PowerChute Agent. See Schneider Electric FAQ FA159586

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 11:34 PM . Last Modified: ‎2024-03-12 12:45 AM

0 Likes
0
1082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:34 PM . Last Modified: ‎2024-03-12 12:45 AM

Welcome again.

APC Agent uses "Administrator" account to start/login , so I think all needed permissions are granted.

Once again, CMD file run in windows shell (also from Administrator account) executes correctly.

Run via TEST button from from APC Agent config page does nothing.

Also starting shutdown procedure does not execute cmd file.

What else can I check or do ?

BR

Mike

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-29 11:34 PM . Last Modified: ‎2024-03-12 12:45 AM

0 Likes
0
1083
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:34 PM . Last Modified: ‎2024-03-12 12:45 AM

Unfortunately even with administrator privileges Microsoft limits service's ability to interact with the desktop. Here's one person's workaround (link).

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of