PCNS 4.2 With ESXi and Windows Servers + appliances

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PCNS 4.2 With ESXi and Windows Servers + appliances
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:33 PM . Last Modified: ‎2024-03-12 12:45 AM

0 Likes
4
564
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:33 PM . Last Modified: ‎2024-03-12 12:45 AM

PCNS 4.2 With ESXi and Windows Servers + appliances

Hi

I have several sites with various mixes of ESXi, MS Windows and an SAN appliance requiring scripted shutdown.  For a UPS that powers both ESXi servers (controlled by Central PCNS on dedicated MS Windows server, integrated with vCenter) and MS Windows servers (each with it's own PCNS installed, no Hyper-v / SCVMM) what are the considerations for this mixed environment? 

There are SAN appliances (requiring scripted shutdown) at sites with 

A) only ESXi servers;

B) only MS Windows Servers and;

C) neither ESXi nor MS Windows servers

I would prefer a consistent method to script shutdown the appliances and that needs to happen after the servers have shutdown.  How best to do this?

Or can I do the whole lot in a single method?

Thanks 

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:34 PM . Last Modified: ‎2024-03-12 12:45 AM

0 Likes
0
564
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:34 PM . Last Modified: ‎2024-03-12 12:45 AM

Thanks Bill

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:33 PM . Last Modified: ‎2024-03-12 12:45 AM

0 Likes
0
564
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:33 PM . Last Modified: ‎2024-03-12 12:45 AM

Hi,

On 12/13/2017 11:50 PM, Ed said:

I have several sites with various mixes of ESXi, MS Windows and an SAN appliance requiring scripted shutdown.  For a UPS that powers both ESXi servers (controlled by Central PCNS on dedicated MS Windows server, integrated with vCenter) and MS Windows servers (each with it's own PCNS installed, no Hyper-v / SCVMM) what are the considerations for this mixed environment? 

Your option are for the sites that have both Windows and ESXi you can install PCNS on the Windows server and configure to power down the ESXi host/s using vCenter or without vCenter. Another option is to install PCNS on the Windows servers and install the PCNS appliance on the host and configure fo single host or through vCenter. 

You should review Application Note 180, PowerChute Network Shutdown VMware User's Guide, and the Installation Guide.  

For the Windows server that are not paired with an ESXi host you should install on the individual server. 

For sites that only have ESXi you can install the PCNS appliance and again using vCenter or without vCenter.

For sites that do not run a compatible OS you will need to install PCNS on a compatible OS and script it to power down the SAN. Or you could configure PCNS at one of the other sites as Advanced and configure each UPS as needed. See Application Note 186

If you need assistance with a specific configuration you contact local technical support. They will assist you and or recommend a local specialist that can.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:34 PM . Last Modified: ‎2024-03-12 12:45 AM

0 Likes
0
564
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:34 PM . Last Modified: ‎2024-03-12 12:45 AM

Thanks Bill

Another clarification to you or anyone else who has the knowledge or can offer a guess

For the site that has only 1 SAN appliance, can I add that UPS to the PCNS for VMware running on a Windows Server in another site (cust wants to run the VMware PCNS on a Windows server rather than as an appliance) and have it still run the script to shutdown the remote SAN appliance on remote UPS event, i.e. there are no ESXi or Windows servers at this site, it's just the SAN appliance connected to a UPS.

If not, we'll have to put a supported OS at the site

Thanks for you prompt previous response.  I hope you can clarify this question

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:34 PM . Last Modified: ‎2024-03-12 12:45 AM

0 Likes
0
564
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:34 PM . Last Modified: ‎2024-03-12 12:45 AM

Hi,

You can install PCNS on Windows at one site and have it control a UPS connected to a storage device at another as outlined in Application Note 186. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:34 PM . Last Modified: ‎2024-03-12 12:45 AM

0 Likes
0
565
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:34 PM . Last Modified: ‎2024-03-12 12:45 AM

Thanks Bill

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now