Hi,
We have two Smart UPS 2200VA SUA2200RMI2U (http://www.apc.com/resource/include/techspec_index.cfm?base_sku=sua2200rmi2u&tab=models)
We downloaded Powerchute Businesss Edition SFPCBE911, and installed it on a Centos7 machine, the applications starts but we're getting "lost communication error", we tested with USB and Serial the same error appears.
Here is the log file:
USB:
2015-02-08 17:09:53,192 [main] INFO - [application.PicardApplication] JVM pid: 2248
2015-02-08 17:09:53,269 [main] INFO - [application.PicardApplication] Created thePermanentStorage
2015-02-08 17:09:53,286 [main] INFO - [AgentHSM.AgentHsm] Unable to retrieve previous Device SerialNumber from Permanent Storage
2015-02-08 17:09:53,288 [PcbeHSM-EventDispatcher] INFO - [AgentHSM.AgentHsm] State Change InitialState -> ActiveState
2015-02-08 17:09:53,379 [main] INFO - [MicrolinkSlaveConfigData.MicrolinkSlaveConfigurationData] Version: 28(478BBE5058DD9A153D78BFA1EB2B6F67)
2015-02-08 17:09:53,379 [main] INFO - [MicrolinkSlave.MicroLinkSlaveComponent] USING USB for UPS Comms
2015-02-08 17:09:53,383 [main] INFO - [application.PicardApplication] Registering components interested in UPS Data
2015-02-08 17:09:57,089 [MicroLinkSlaveHSM-EventDispatcher] WARN - [microlink.MicroLinkSlaveHSM] State Change INITIAL -> ACTIVE
2015-02-08 17:09:57,089 [MicroLinkSlaveHSM-EventDispatcher] ERROR - [microlink.USBTranslator] USBTranslator.openDevice() - Failed: com.apcc.components.MicrolinkSlave.protocols.usb.DeviceOpenException: Device ID reference is null
2015-02-08 17:09:57,089 [PcbeHSM-EventDispatcher] INFO - [application.PicardApplication] stateTransitionNotify signal=XXX_TO_NO_COMM
2015-02-08 17:09:57,090 [main] INFO - [application.PicardApplication] Main thread mode = blocking
2015-02-08 17:09:57,094 [PcbeHSM-EventDispatcher] INFO - [AgentHSM.AgentHsm] State Change ActiveState -> INIT_COMM_STATE
2015-02-08 17:09:57,094 [M11ComponentManagerThread] INFO - [application.PCBE_M11ComponentManager] Starting M11
2015-02-08 17:09:57,097 [main] INFO - [application.PicardApplication] Application has Finished Starting
2015-02-08 17:09:57,123 [M11ComponentManagerThread] ERROR - [Shutdowner.Shutdowner] Can't find NativeShutdownSupport library
2015-02-08 17:09:58,506 [USB_UPS_DetectTimer] INFO - [usb.USBDeviceTranslator] power device is open
2015-02-08 17:10:00,009 [MicroLinkSlaveHSM-EventDispatcher] WARN - [microlink.MicroLinkSlaveHSM] State Change ACTIVE -> COMM_LOST
2015-02-08 17:10:03,014 [MicroLinkSlaveHSM-EventDispatcher] INFO - [usb.USBDeviceTranslator] Closing power device
2015-02-08 17:10:03,015 [PcbeHSM-EventDispatcher] INFO - [AgentHSM.AgentHsm] State Change INIT_COMM_STATE COMMS_LOST_WAIT_FOR_M11_START
2015-02-08 17:10:03,015 [MicroLinkSlaveHSM-EventDispatcher] INFO - [usb.USBDeviceTranslator] power device is open
-----------------------------------
SERIAL DB9
2015-02-08 16:29:13,699 [main] INFO - [MicrolinkSlave.MicroLinkSlaveComponent] USING Serial port /dev/ttyS0 for UPS Comms
2015-02-08 16:29:13,703 [main] INFO - [application.PicardApplication] Registering components interested in UPS Data
2015-02-08 16:29:13,845 [MicroLinkSlaveHSM-EventDispatcher] WARN - [microlink.MicroLinkSlaveHSM] State Change INITIAL -> ACTIVE
2015-02-08 16:29:13,846 [main] INFO - [application.PicardApplication] Main thread mode = blocking
2015-02-08 16:29:13,846 [M11ComponentManagerThread] INFO - [application.PCBE_M11ComponentManager] Starting M11
2015-02-08 16:29:13,846 [PcbeHSM-EventDispatcher] INFO - [application.PicardApplication] stateTransitionNotify signal=XXX_TO_NO_COMM
2015-02-08 16:29:13,846 [main] INFO - [application.PicardApplication] Application has Finished Starting
2015-02-08 16:29:13,849 [PcbeHSM-EventDispatcher] INFO - [AgentHSM.AgentHsm] State Change ActiveState -> INIT_COMM_STATE
2015-02-08 16:29:13,873 [M11ComponentManagerThread] ERROR - [Shutdowner.Shutdowner] Can't find NativeShutdownSupport library
2015-02-08 16:29:16,797 [MicroLinkSlaveHSM-EventDispatcher] WARN - [microlink.MicroLinkSlaveHSM] State Change ACTIVE -> COMM_LOST
2015-02-08 16:29:24,659 [PcbeHSM-EventDispatcher] INFO - [AgentHSM.AgentHsm] State Change INIT_COMM_STATE -> COMMS_LOST_WAIT_FOR_M11_START
2015-02-08 16:30:47,207 [M11ComponentManagerThread] WARN - [Shutdowner.Shutdowner] Event Consumer registered (Shutdowner)
2015-02-08 16:31:52,866 [M11ComponentManagerThread] INFO - [Device.MicroLinkDeviceTranslator] added MicroLinkOutletSystem data model to DataModelRegistry
-------------
Other errors
com.apcc.components.MicrolinkSlave.Exceptions.CommunicationException: MicroLink engine has not been inited yet.
2015-02-08 16:33:49,473 [qtp26831131-48] ERROR - [DataModels.AbstractCollectionDataModel] Problem retrieving usage data from uL slave com.apcc.components.MicrolinkSlave.Exceptions.CommunicationException: MicroLink engine has not been inited yet.
2015-02-08 16:33:49,473 [qtp26831131-48] ERROR - [DataModels.AbstractCollectionDataModel] Problem retrieving usage data from uL slave com.apcc.components.MicrolinkSlave.Exceptions.CommunicationException: MicroLink engine has not been inited yet.
What does mean "[M11ComponentManagerThread] ERROR - [Shutdowner.Shutdowner] Can't find NativeShutdownSupport library", we didn't find any answer from the web.
thanks in advance.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:43 PM . Last Modified: 2024-03-14 04:05 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:43 PM . Last Modified: 2024-03-14 04:05 AM
Hi Bill,
A big thank to you for your reply, I did try apcupsd and it worked like a charm.
thanks again.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:43 PM . Last Modified: 2024-03-14 04:06 AM
Hi,
PowerChute Business Edition is not support on CentOS. We currently support Redhat Enterprise and SuSE Enterprise. You should look at APCUPSD with CentOS. I have not personally tested CentOS with APCUPSD but from reviewing APCUPSD mail archive it appears that many other do use the app.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:43 PM . Last Modified: 2024-03-14 04:05 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:43 PM . Last Modified: 2024-03-14 04:05 AM
Hi Bill,
A big thank to you for your reply, I did try apcupsd and it worked like a charm.
thanks again.