Good day,
1st, thak you for providing this forumn. 2nd I am a newebee and sorry if I offend anyone up front and this is not how to post or use this thread.
I am trying to edit this shutdownvms.sh and wish to know the following;
1. Does anyone of the paramters listed or documented? I am speficially looking for the user and pwd parameter:
2. I have different esx 5.1i root passwords, how can I adjust for this inside of the script?
3. The following line: ups_vm="vSphere Management Assistant \(PW-LABVMAXAS\)" is this correct or should it be = ups_vm="PW-LABVMAXAS"
Thank you very much..
Sam
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 03:13 AM . Last Modified: 2024-03-05 11:07 PM
Sam,
You do not need to enter user names and passwords. PCNS 3.0.1 uses VIFPTARGET/vMATarget functionality provided by the vMA to store the ESXi host credentials. PCNS retrieves the credentials when connecting to the host to shut it down using the RCLI/Perl SDK. These credentials are actually stored in an XML file on the vMA. When you add a target host using the vifp addserver command a new accounts is created. We use the same file / grab the same info when running shutdownvms.sh
If you need help with adding host the the target list please review page 54 and 55 of this PDF
For question 3 you should enter ups_vm="PW-LABVMAXAS"
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 03:13 AM . Last Modified: 2024-03-05 11:07 PM
Sam,
You do not need to enter user names and passwords. PCNS 3.0.1 uses VIFPTARGET/vMATarget functionality provided by the vMA to store the ESXi host credentials. PCNS retrieves the credentials when connecting to the host to shut it down using the RCLI/Perl SDK. These credentials are actually stored in an XML file on the vMA. When you add a target host using the vifp addserver command a new accounts is created. We use the same file / grab the same info when running shutdownvms.sh
If you need help with adding host the the target list please review page 54 and 55 of this PDF
For question 3 you should enter ups_vm="PW-LABVMAXAS"