PowerChute constantly sending Power Failed/Restored messages

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PowerChute constantly sending Power Failed/Restored messages
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
119
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 02:11 AM . Last Modified: ‎2024-03-05 11:51 PM

0 Likes
15
2760
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:11 AM . Last Modified: ‎2024-03-05 11:51 PM

PowerChute constantly sending Power Failed/Restored messages

Morning All,

We have a Smart-UPS 1500 connected to our SBS 2003 server and we have PowerChute Business Edition Version 9.0.1 monitoring it.

For the past month or so - either late at night or early morning we are getting "Power Failed on Agent " and "Power Restored on Agent

I have checked over PowerChute and everything is coming back as working fine, no abnormalities as I can see. And the Self-Test of the UPS comes back fine.

Is this something that is easily fixed?

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • PowerChute
  • powerchute_business_edition
  • smart-ups_1500
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 02:12 AM . Last Modified: ‎2024-03-05 11:50 PM

0 Likes
0
2759
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:12 AM . Last Modified: ‎2024-03-05 11:50 PM

Hmm, usually where it lists the UPS COM, MBL, CBL, etc versions you listed, it usually ends with (ID XX)

Anyways, I agree. It is most likely the latest already.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 15
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 02:11 AM . Last Modified: ‎2024-03-05 11:51 PM

0 Likes
0
2759
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:11 AM . Last Modified: ‎2024-03-05 11:51 PM

how do you know this is not a legit power event? i am just wondering why you think there is an issue here when the UPS is trying to tell you power failed. can you provide the full event and data log? if there is a possibility it is legit, i would suggest maybe try lowering the sensitivity so that your UPS is less sensitive to noise on the line (which could also cause the UPS to go to battery versus a blackout.

are you monitoring the UPS via USB or serial communications? the only other thing i can think of is that it if it is a "false alarm," that it could be due to the method you are using for monitoring.

unfortunately, Business Edition doesnt really offer customizing the notifications to set a delay or anything. the network management card products allow you to delay events which sounds like a good idea for you.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 02:11 AM . Last Modified: ‎2024-03-05 11:51 PM

0 Likes
0
2759
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:11 AM . Last Modified: ‎2024-03-05 11:51 PM

Hi Angela,

I've looked over the logs myself and nothing seems wrong regarding the power levels etc. but I've attached them regardless.

The main thing that points me to a possible problem is that this is the only time that something has even touched the UPS - and if they were legitimate power failures, I would expect something else to react even a little bit. I've looked over the logs briefly and can't see any problems such as abnormal voltages or anything like that, but I wouldn't turn down a second opinion!

We are monitoring it via USB also, which I have read can cause a couple of problems similar to what is happening here if they are indeed false alarms.

Attachments
DataLog.zip
EventLog.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 02:11 AM . Last Modified: ‎2024-03-05 11:50 PM

0 Likes
0
2759
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:11 AM . Last Modified: ‎2024-03-05 11:50 PM

OK - good points. I tend to agree but wasn't sure how much investigation you had done on the validity of the messages so far.

these logs appear to be something that i can't view in notepad - can you? if not, is it too much trouble to ask for a copy/paste into a text document from the web UI or whatever UI you are using?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 02:11 AM . Last Modified: ‎2024-03-05 11:50 PM

0 Likes
0
2759
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:11 AM . Last Modified: ‎2024-03-05 11:50 PM

I can open the data log fine so copied into a fresh text document and attached.

The Event Log I can't however so snipped an image of what it looks like in the agent and attached.

Attachments
DataLog2.txt.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 02:11 AM . Last Modified: ‎2024-03-05 11:50 PM

0 Likes
0
2759
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:11 AM . Last Modified: ‎2024-03-05 11:50 PM

thanks. are you able to access this particular UPS's agent directly via web browser. looks like you're using the PowerChute Business Edition Console (that purple window). i just want to make sure there is not any more events listed in the agent's log vs. what you just showed me.

you can access the agent  via https://:6547 or using HTTP on port 3052. let me know if the log shows any different events.

also, i see you are at 240v-250v - is this nominal voltage 240v at this site? or 230v? (I ask because I saw your location as UK). just curious what your UPS transfer voltages are set to because i was wondering if at 250v, its jumping to battery power briefly. i compared the data log times to the events and it seemed close to 250v at those times.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 02:11 AM . Last Modified: ‎2024-03-05 11:50 PM

0 Likes
0
2759
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:11 AM . Last Modified: ‎2024-03-05 11:50 PM

I've snipped the logs from the web agent rather than the desktop agent and attached to this post for you to look over - I can't see any differences myself.

Regarding your voltage question - 240v is the nominal for the site in question and the transfer voltages are:

High Transfer Voltage: 261 VAC

Low Transfer Voltage: 208 VAC

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 02:11 AM . Last Modified: ‎2024-03-05 11:50 PM

0 Likes
0
2758
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:11 AM . Last Modified: ‎2024-03-05 11:50 PM

I haven't tried lowering the sensitivity yet but will do it shortly and see if it repeats the process at all over the weekend - we didn't get any reports last night fortunately but whether it was one of those problems that fixes itself magically I'm not too sure!

Regarding the reason to transfer to battery; I couldn't see anything like that. Only the fact it lost power in the event log but no reason to it going to the battery.

I will let you know how I get on.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 02:11 AM . Last Modified: ‎2024-03-05 11:50 PM

0 Likes
0
2758
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:11 AM . Last Modified: ‎2024-03-05 11:50 PM

I agree. The only other thing I can think of that could cause this is dV/dT which means the change in voltage over time. if it is too quick, the UPS could go to battery as well. have you tried adjusting the sensitivity? we could see if lowering it a notch stops these from happening and then it'd tell me its some type of noise on the line or dV/dT.

i thought in PowerChute also that the UPS could report its last transfer to battery reason but on all my PowerChute lab devices, I can't seem to find it. You didn't see anything like that, did you? I am able to see this information via a Network Management Card which says something like Due to software command or UPS's test control for my UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 02:11 AM . Last Modified: ‎2024-03-05 11:50 PM

0 Likes
0
2758
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:11 AM . Last Modified: ‎2024-03-05 11:50 PM

Yeah, I am not sure why it wouldn't display in PowerChute but a Network Management Card shows it..

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 02:11 AM . Last Modified: ‎2024-03-05 11:50 PM

0 Likes
0
2759
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:11 AM . Last Modified: ‎2024-03-05 11:50 PM

Hello, I am having the same problem with a Smart UPS x2000. I am attaching a copy of the logs. It does not appear to be a legit power outage because none of the other UPS (3) are showing a loss in power. We have 2 x3000 and 1 older 2200 rm xl. None of these are showing the power failures. Any help would be greatly appreciated. These are all being monitored via serial connection to separate machines.

3/7/13 04:38:08 Power Restored
3/7/13 04:38:07 Power Failed
3/7/13 02:51:01 Power Restored
3/7/13 02:51:00 Power Failed
3/7/13 01:20:36 Power Restored
3/7/13 01:20:35 Power Failed
3/6/13 23:56:10 Power Restored
3/6/13 23:56:09 Power Failed
3/6/13 20:07:18 Power Restored
3/6/13 20:07:17 Power Failed

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 02:11 AM . Last Modified: ‎2024-03-05 11:50 PM

0 Likes
0
2758
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:11 AM . Last Modified: ‎2024-03-05 11:50 PM

Have you tried to adjust the power quality/sensitivity settings a notch or two? Also, are those UPSs on the same or different circuits? Because if they are different circuits, it doesn't really help me that the other UPSs don't react this way since its a different circuit. It could be a quick sag or something on the line also when a particular attached device draws high current momentarily.

What is your UPSs firmware version?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 02:12 AM . Last Modified: ‎2024-03-05 11:50 PM

0 Likes
0
2758
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:12 AM . Last Modified: ‎2024-03-05 11:50 PM

Yes they are all on dedicated circuits. I have switched it to another circuit as well and had the same issue. I did just change the sensitivity to low and have not had an issue since.

Here are the settings for the UPS:

Firmware: UPS 01.9/COM 01.6

1019_line settings.png

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 02:12 AM . Last Modified: ‎2024-03-05 11:50 PM

0 Likes
0
2758
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:12 AM . Last Modified: ‎2024-03-05 11:50 PM

OK good to know - and on the UPS firmware information, did you see an ID listed anywhere, like (ID 17) or similar? That will help me verify the exact UPS type right from the firmware information. My educated guess is that your ID is 10 and if so, you already have the latest version of firmware for your UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 02:12 AM . Last Modified: ‎2024-03-05 11:50 PM

0 Likes
0
2758
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:12 AM . Last Modified: ‎2024-03-05 11:50 PM

I do not see that anywhere.... I am looking at the data through the APC console. The UPS is brand new so I think it is at the highest firmware.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 02:12 AM . Last Modified: ‎2024-03-05 11:50 PM

0 Likes
0
2760
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:12 AM . Last Modified: ‎2024-03-05 11:50 PM

Hmm, usually where it lists the UPS COM, MBL, CBL, etc versions you listed, it usually ends with (ID XX)

Anyways, I agree. It is most likely the latest already.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of