Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Success Stories Corner

PowerChute constantly sending Power Failed/Restored messages

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PowerChute constantly sending Power Failed/Restored messages
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5022
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All
Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
delo_apc
Crewman delo_apc
Crewman

Posted: ‎2021-07-01 02:11 AM

0 Likes
15
1024
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 02:11 AM

PowerChute constantly sending Power Failed/Restored messages

This was originally posted on APC forums on 2/28/2013


Morning All,

We have a Smart-UPS 1500 connected to our SBS 2003 server and we have PowerChute Business Edition Version 9.0.1 monitoring it.

For the past month or so - either late at night or early morning we are getting "Power Failed on Agent " and "Power Restored on Agent

I have checked over PowerChute and everything is coming back as working fine, no abnormalities as I can see. And the Self-Test of the UPS comes back fine.

Is this something that is easily fixed?

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • PowerChute
  • powerchute_business_edition
  • smart-ups_1500
Reply
Share
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 02:12 AM

0 Likes
0
1023
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 02:12 AM

This reply was originally posted by Angela on APC forums on 3/8/2013


Hmm, usually where it lists the UPS COM, MBL, CBL, etc versions you listed, it usually ends with (ID XX)

Anyways, I agree. It is most likely the latest already.

See Answer In Context

Reply
Share
Replies 15
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 02:11 AM

0 Likes
0
1023
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 02:11 AM

This reply was originally posted by Angela on APC forums on 2/28/2013


how do you know this is not a legit power event? i am just wondering why you think there is an issue here when the UPS is trying to tell you power failed. can you provide the full event and data log? if there is a possibility it is legit, i would suggest maybe try lowering the sensitivity so that your UPS is less sensitive to noise on the line (which could also cause the UPS to go to battery versus a blackout.

are you monitoring the UPS via USB or serial communications? the only other thing i can think of is that it if it is a "false alarm," that it could be due to the method you are using for monitoring.

unfortunately, Business Edition doesnt really offer customizing the notifications to set a delay or anything. the network management card products allow you to delay events which sounds like a good idea for you.

Reply
Share
delo_apc
Crewman delo_apc
Crewman

Posted: ‎2021-07-01 02:11 AM

0 Likes
0
1023
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 02:11 AM

This was originally posted on APC forums on 2/28/2013


Hi Angela,

I've looked over the logs myself and nothing seems wrong regarding the power levels etc. but I've attached them regardless.

The main thing that points me to a possible problem is that this is the only time that something has even touched the UPS - and if they were legitimate power failures, I would expect something else to react even a little bit. I've looked over the logs briefly and can't see any problems such as abnormal voltages or anything like that, but I wouldn't turn down a second opinion!

We are monitoring it via USB also, which I have read can cause a couple of problems similar to what is happening here if they are indeed false alarms.

Attachments
DataLog.zip
EventLog.zip
Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 02:11 AM

0 Likes
0
1023
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 02:11 AM

This reply was originally posted by Angela on APC forums on 2/28/2013


OK - good points. I tend to agree but wasn't sure how much investigation you had done on the validity of the messages so far.

these logs appear to be something that i can't view in notepad - can you? if not, is it too much trouble to ask for a copy/paste into a text document from the web UI or whatever UI you are using?

Reply
Share
delo_apc
Crewman delo_apc
Crewman

Posted: ‎2021-07-01 02:11 AM

0 Likes
0
1023
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 02:11 AM

This was originally posted on APC forums on 2/28/2013


I can open the data log fine so copied into a fresh text document and attached.

The Event Log I can't however so snipped an image of what it looks like in the agent and attached.

Attachments
DataLog2.txt.zip
Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 02:11 AM

0 Likes
0
1023
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 02:11 AM

This reply was originally posted by Angela on APC forums on 2/28/2013


thanks. are you able to access this particular UPS's agent directly via web browser. looks like you're using the PowerChute Business Edition Console (that purple window). i just want to make sure there is not any more events listed in the agent's log vs. what you just showed me.

you can access the agent  via https://:6547 or using HTTP on port 3052. let me know if the log shows any different events.

also, i see you are at 240v-250v - is this nominal voltage 240v at this site? or 230v? (I ask because I saw your location as UK). just curious what your UPS transfer voltages are set to because i was wondering if at 250v, its jumping to battery power briefly. i compared the data log times to the events and it seemed close to 250v at those times.

Reply
Share
delo_apc
Crewman delo_apc
Crewman

Posted: ‎2021-07-01 02:11 AM

0 Likes
0
1023
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 02:11 AM

This was originally posted on APC forums on 3/1/2013


I've snipped the logs from the web agent rather than the desktop agent and attached to this post for you to look over - I can't see any differences myself.

Regarding your voltage question - 240v is the nominal for the site in question and the transfer voltages are:

High Transfer Voltage: 261 VAC

Low Transfer Voltage: 208 VAC

Attachments
Reply
Share
delo_apc
Crewman delo_apc
Crewman

Posted: ‎2021-07-01 02:11 AM

0 Likes
0
1022
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 02:11 AM

This was originally posted on APC forums on 3/1/2013


I haven't tried lowering the sensitivity yet but will do it shortly and see if it repeats the process at all over the weekend - we didn't get any reports last night fortunately but whether it was one of those problems that fixes itself magically I'm not too sure!

Regarding the reason to transfer to battery; I couldn't see anything like that. Only the fact it lost power in the event log but no reason to it going to the battery.

I will let you know how I get on.

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 02:11 AM

0 Likes
0
1022
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 02:11 AM

This reply was originally posted by Angela on APC forums on 3/1/2013


I agree. The only other thing I can think of that could cause this is dV/dT which means the change in voltage over time. if it is too quick, the UPS could go to battery as well. have you tried adjusting the sensitivity? we could see if lowering it a notch stops these from happening and then it'd tell me its some type of noise on the line or dV/dT.

i thought in PowerChute also that the UPS could report its last transfer to battery reason but on all my PowerChute lab devices, I can't seem to find it. You didn't see anything like that, did you? I am able to see this information via a Network Management Card which says something like Due to software command or UPS's test control for my UPS.

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 02:11 AM

0 Likes
0
1022
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 02:11 AM

This reply was originally posted by Angela on APC forums on 3/1/2013


Yeah, I am not sure why it wouldn't display in PowerChute but a Network Management Card shows it..

Reply
Share
joeker1086_apc
Ensign joeker1086_apc
Ensign

Posted: ‎2021-07-01 02:11 AM

0 Likes
0
1023
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 02:11 AM

This was originally posted on APC forums on 3/7/2013


Hello, I am having the same problem with a Smart UPS x2000. I am attaching a copy of the logs. It does not appear to be a legit power outage because none of the other UPS (3) are showing a loss in power. We have 2 x3000 and 1 older 2200 rm xl. None of these are showing the power failures. Any help would be greatly appreciated. These are all being monitored via serial connection to separate machines.

3/7/13 04:38:08 Power Restored
3/7/13 04:38:07 Power Failed
3/7/13 02:51:01 Power Restored
3/7/13 02:51:00 Power Failed
3/7/13 01:20:36 Power Restored
3/7/13 01:20:35 Power Failed
3/6/13 23:56:10 Power Restored
3/6/13 23:56:09 Power Failed
3/6/13 20:07:18 Power Restored
3/6/13 20:07:17 Power Failed

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 02:11 AM

0 Likes
0
1022
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 02:11 AM

This reply was originally posted by Angela on APC forums on 3/7/2013


Have you tried to adjust the power quality/sensitivity settings a notch or two? Also, are those UPSs on the same or different circuits? Because if they are different circuits, it doesn't really help me that the other UPSs don't react this way since its a different circuit. It could be a quick sag or something on the line also when a particular attached device draws high current momentarily.

What is your UPSs firmware version?

Reply
Share
joeker1086_apc
Ensign joeker1086_apc
Ensign

Posted: ‎2021-07-01 02:12 AM

0 Likes
0
1022
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 02:12 AM

This was originally posted on APC forums on 3/8/2013


Yes they are all on dedicated circuits. I have switched it to another circuit as well and had the same issue. I did just change the sensitivity to low and have not had an issue since.

Here are the settings for the UPS:

Firmware: UPS 01.9/COM 01.6

1019_line settings.png

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 02:12 AM

0 Likes
0
1022
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 02:12 AM

This reply was originally posted by Angela on APC forums on 3/8/2013


OK good to know - and on the UPS firmware information, did you see an ID listed anywhere, like (ID 17) or similar? That will help me verify the exact UPS type right from the firmware information. My educated guess is that your ID is 10 and if so, you already have the latest version of firmware for your UPS.

Reply
Share
joeker1086_apc
Ensign joeker1086_apc
Ensign

Posted: ‎2021-07-01 02:12 AM

0 Likes
0
1022
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 02:12 AM

This was originally posted on APC forums on 3/8/2013


I do not see that anywhere.... I am looking at the data through the APC console. The UPS is brand new so I think it is at the highest firmware.

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 02:12 AM

0 Likes
0
1024
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 02:12 AM

This reply was originally posted by Angela on APC forums on 3/8/2013


Hmm, usually where it lists the UPS COM, MBL, CBL, etc versions you listed, it usually ends with (ID XX)

Anyways, I agree. It is most likely the latest already.

Reply
Share
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc