Ok ... I have an older PC that performs environmental supervision for a remote site.
It runs XP Professional SP3 with all security patches.
I just upgraded from an older version of PowerChute to the latest PowerChute V9.1.0, and aquired a newer SmartUPS 1500
PowerChute does not recognize the UPS
USB connection seems OK as when I plug the UPS in to the PC with the PC running,
the UPS is recognized as an HID-type device - named: "American Power Conversion USB UPS"
This device gets removed from Device manager when I unplug the USB cable
I checked Microsoft update and it asserts no newer device driver is available for the device
When I launch the web interface for the PowerChute (Business Edition) Agent s/w via: http://127.0.0.1:3052
the interface tells me the device is not connected.
When I go to Server Shutdown --> System Settings --> Device Communications Port
It only offers COM1 or COM3 - not a USB type connection....
What have I done wrong?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 04:08 AM . Last Modified: 2024-03-05 10:25 PM
You need to uninstall the PowerChute Agent and reinstall it. I assume that the newer Smart-UPS you are using is either a SMT or SMX model and those models have a different communication protocol than older Smart-UPS did. By uninstalling and reinstalling PowerChute will recognize the newer Smart-UPS and establish communications.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 04:08 AM . Last Modified: 2024-03-05 10:25 PM
You need to uninstall the PowerChute Agent and reinstall it. I assume that the newer Smart-UPS you are using is either a SMT or SMX model and those models have a different communication protocol than older Smart-UPS did. By uninstalling and reinstalling PowerChute will recognize the newer Smart-UPS and establish communications.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 04:09 AM . Last Modified: 2024-03-05 10:25 PM
Thanks Bill ... The unit I am using is a few years old it is a Model DLA1500 ....
I don't know which communications protocol it uses, so I'll uninstall/reinstall and report back ....
Thanks!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 04:09 AM . Last Modified: 2024-03-05 10:25 PM
Thanks Bill that fixed it!
I might suggest to the programming team they they create a "search for UPS" option within powerchute,
or prompt during upgrade-installs to ask if user would like to uninstall old version first
(either as part of install, or warn of circumstances where-in user might want to manually uninstall prior to installation of new version)
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.