PowerChute Shutting down servers in a specific order
Hi,
I am wondering if there is a option to shut down servers in a specific order.
We have 6 servers. Two physical servers are connected and both servers run 2 virtual hyper-v servers.
I want to shut down the virtual servers first and then my 2 physical servers.
Is this possible and how?
UPS: Smart-UPS RT 2000 XL
Network Management Card 2
PowerChute Network Shutdown
- Labels:
-
Smart-UPS & Symmetra LX | RM
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:56 AM . Last Modified: 2024-03-12 01:31 AM
Hi,
You should install PCNS on each host and then configure each host to shutdown when UPS has been on battery for x minutes or when runtime remaining is x.
Example host A starts shutdown when UPS has 30 minutes of runtime remaining. Host B starts shutdown when UPS has 25 minutes of runtime remaining.
The users guide explains this beginning onpage 20 (PDF page 23)
Note: you cannot configure the order the VMs will be powered down in.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:56 AM . Last Modified: 2024-03-12 01:31 AM
Hi,
You should install PCNS on each host and then configure each host to shutdown when UPS has been on battery for x minutes or when runtime remaining is x.
Example host A starts shutdown when UPS has 30 minutes of runtime remaining. Host B starts shutdown when UPS has 25 minutes of runtime remaining.
The users guide explains this beginning onpage 20 (PDF page 23)
Note: you cannot configure the order the VMs will be powered down in.
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-29 08:56 AM . Last Modified: 2024-03-12 01:31 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:56 AM . Last Modified: 2024-03-12 01:31 AM
Hi Bill,
Thanks for your respond!
This will help me to configure the UPS.
Many thanks!
Tim