sua2200rm2u Network problems

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • sua2200rm2u Network problems
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 08:55 AM . Last Modified: ‎2024-03-12 01:32 AM

0 Likes
8
1419
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:55 AM . Last Modified: ‎2024-03-12 01:32 AM

sua2200rm2u Network problems

I finially got the network to talk.

I installed the PCNS (powerchute Network) app. When i set it up to connect to the NIC (typing in the username passwd and the passcode (all im sure are correct) it says it cannot connect and cannot register???.

Looking in the logs, it says the client connected to port 80 of the nic upon starting the computer.

Do i have a lemon or what am i missing>

TIA

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 08:55 AM . Last Modified: ‎2024-03-12 01:31 AM

0 Likes
0
1418
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:55 AM . Last Modified: ‎2024-03-12 01:31 AM

THANK YOU! It worked- it is now talking to the UPS hardware.... Now to the shutdown settings (i enabled server shutdown after 5 min(300 sec) of test outage but it didnt shutdown)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
Anonymous user
Not applicable

Posted: ‎2021-06-29 08:55 AM . Last Modified: ‎2024-03-12 01:32 AM

0 Likes
0
1418
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:55 AM . Last Modified: ‎2024-03-12 01:32 AM

Also, when i login to the APC NIC via web, almost everything says it cannot communicate with the ups like battery status, uptime, etc.

So same q- is it a lemon?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:55 AM . Last Modified: ‎2024-03-12 01:32 AM

0 Likes
0
1419
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:55 AM . Last Modified: ‎2024-03-12 01:32 AM

here is more info i came across FWIW:

I have 2 of them and i swapped the NIC and IT WORKS!!!! the server with the Network PowerChute sees the UPS NIC.

At the prompt of the working nic, when i exit i get "passthrough" vs exiting...

I hope there is a simple setting that i missed...

Thanks again.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:55 AM . Last Modified: ‎2024-03-12 01:32 AM

0 Likes
0
1419
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:55 AM . Last Modified: ‎2024-03-12 01:32 AM

Hi,

I'd start with telling us the specifics of the Network Management Card Model - something like AP9617/18/19 or AP9630/31.

What you described in your second post could be a firmware problem or communication problem. PowerChute won't work properly with it in this condition. I'd want to know what you see for the firmware and without knowing the model of the Network Management Card, I cannot suggest how to check with certainty. For most Network Management Cards in the web UI, you can check under Administration->General->About and let me know what you see for AOS and APP versions and names. If you have a newer one with green and white interface, you'll want to check under About->Network.

Once we validate the firmware, we can go from there in trying a few things like resetting the UPS communications or fixing the firmware.

When you said:

I have 2 of them and i swapped the NIC and IT WORKS!!!! the server with the Network PowerChute sees the UPS NIC.

Did you swap the same Network Mgmt Card to a different UPS or try a second Network Mgmt Card in the one UPS? I was unclear what you meant by "I have two of them" - whether them was a UPS or Management Card.

And not to worry about exiting passthrough mode, that is normal and means you're no longer interfacing with the Network Mgmt Card but rather the UPS is ready now if you knew how to directly talk to it for a special application.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:55 AM . Last Modified: ‎2024-03-12 01:32 AM

0 Likes
0
1419
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:55 AM . Last Modified: ‎2024-03-12 01:32 AM

This is what i have:

AP 9617

Version 372

With UPS "1" installed the card from ups "2" and it worked. i took the working card and moved it back to UPS "2" and the card worked there too.(it shows status of batteries, the client servers can register to this card, etc.) i have a third card i bought seperately - that card acts the same way as the "non working" card that came straight out of the UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:55 AM . Last Modified: ‎2024-03-12 01:32 AM

0 Likes
0
1419
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:55 AM . Last Modified: ‎2024-03-12 01:32 AM

OK thanks. Just a few other questions - the version 3.7.2, I need to know the application name it says - it should be something like sy or sumx for the application module name. We need to make sure it is compatible with the particular UPS. And all these UPSs are model SUA2200RM2U?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:55 AM . Last Modified: ‎2024-03-12 01:31 AM

0 Likes
0
1419
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:55 AM . Last Modified: ‎2024-03-12 01:31 AM

App module - sy3p or APC OS - aos. both are on the web page. I have 2 of these ups' and another one 1400. After finding the card works on both 2200's. I am now using it on the 1400 (and it works there too). The other card (same model of working card) is still  in the 2200 that they came in and still does not talk to the hardware. Thanks again.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:55 AM . Last Modified: ‎2024-03-12 01:31 AM

0 Likes
0
1419
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:55 AM . Last Modified: ‎2024-03-12 01:31 AM

No problem. Glad to help.

Your app module for a Smart-UPS product should be sumx. You're saying it is sy3p which is designed to talk to Symmetra 3 phase type UPSs.

This can be addressed easily with re-flashing the firmware with the correct version. I will attach the correct version you should have on the Network Management Cards for an AP9617/18/19 model management card installed inside of a Smart-UPS model UPS. Detailed instructions on upgrading/reflashing it are located here if you need it and running the .exe does not work-> How do I upgrade the firmware on an APC Network Management Card (NMC) or NMC embedded device (Rack P...

Attachments
apc_hw02_aos373_sumx372.exe.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:55 AM . Last Modified: ‎2024-03-12 01:31 AM

0 Likes
0
1419
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:55 AM . Last Modified: ‎2024-03-12 01:31 AM

THANK YOU! It worked- it is now talking to the UPS hardware.... Now to the shutdown settings (i enabled server shutdown after 5 min(300 sec) of test outage but it didnt shutdown)

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore