PowerChute Shutdown rules

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PowerChute Shutdown rules
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:27 AM . Last Modified: ‎2024-02-20 04:43 AM

0 Likes
3
4095
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:27 AM . Last Modified: ‎2024-02-20 04:43 AM

PowerChute Shutdown rules

Hi Support,

Good day. I'm using APC Smart UPS 2200 and I have 2 ESXi hosts (physical servers), with the following model:

1) Dell PowerEdge R610

2) Dell PowerEdge R420

As I know, we can set the shutdown rules in PowerChute, such like to let the Servers continue operate for maximum of 3600 seconds (1 hour) if there are any power failure detected.

There are few concerns that I need to figure out for this:

1) Is it possible to set shutdown rule to start powering off my VMs once the battery status is less than 30% or something?

2) If we can only set the shutdown rules based on time, how do I calculate whether my ESXi hosts can last for more than 1 hour?

Thank you.

Best regards,

Kong

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:27 AM . Last Modified: ‎2024-02-20 04:43 AM

0 Likes
0
4093
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:27 AM . Last Modified: ‎2024-02-20 04:43 AM

Hi,

Sorry I forgot you were using PowerChute Business Edition. I the future when starting a new thread it is helpful to list the version of PowerChute being used along with the UPS model. 

To configure PowerChute Buiness Edition go to Configuration - Shutdown Settings and set At runtime limit to 30 minutes. When the UPS has less than 30 minutes of runtime remaining it will start the shutdown process. 

LWc%2Bn1sNEZj4d0WXu4TPHw%3D%3D.pngLWc%2Bn1sNEZj4d0WXu4TPHw%3D%3D.png

To prevent the system from restarting before the time needed to restart and power down go to Configuration - Outlet Sequence and set UPS Outlets (main outlet group) Minimum Battery Runtime Required Before Outlet Group Turns On to 1800 seconds.  Again I recommend including the power up time along with the power down time to prevent the system from not having the available runtime to restart and then power back down.

I am basing the times on the system needing 15 minutes to power down and 10 minutes to power up with an added 5 minutes for safety. 

To see the systems runtime go to Smart-UPS 2200 and select UPS status. Runtime remaining will be listed. 

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:27 AM . Last Modified: ‎2024-02-20 04:43 AM

0 Likes
0
4093
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:27 AM . Last Modified: ‎2024-02-20 04:43 AM

Hi,

On 8/7/2017 2:16 AM, kong said:

1) Is it possible to set shutdown rule to start powering off my VMs once the battery status is less than 30% or something?

You cannot configure to shutdown based on percentage however you can configure to shutdown with there is a certain amount of runtime remaining. Open the PCNS web interface, go to Configure Events - Runtime Remaining Below Threshold and enter the time remaining on battery you would like the shutdown to start. Example: the UPS reports there is 1 hour of runtime available. The servers and VMs require 15 minutes to power down and 10 minutes to power up. You should set the Runtime Remaining Below Threshold to start the shutdown when there is 30 minutes of runtime available. 15 to power down 10 to start up and an extra 5 for safety. You should also configure the NMC not to restore power until there is 30 minutes of available runtime. By not restoring AC until there is 30 minutes of runtime you will be covered so that the battery will be charged enough to shut the systems down in the event of a second power loss.

On 8/7/2017 2:16 AM, kong said:

2) If we can only set the shutdown rules based on time, how do I calculate whether my ESXi hosts can last for more than 1 hour?

The NMC calculates the load and will report the available runtime. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:27 AM . Last Modified: ‎2024-02-20 04:43 AM

0 Likes
0
4093
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:27 AM . Last Modified: ‎2024-02-20 04:43 AM

Hi Bill,

My UPS doesn't have NMC, only connected using RJ45 on UPS and serial on server. I'm using PCBE Agent for configuring shutdown rules.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:27 AM . Last Modified: ‎2024-02-20 04:43 AM

0 Likes
0
4094
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:27 AM . Last Modified: ‎2024-02-20 04:43 AM

Hi,

Sorry I forgot you were using PowerChute Business Edition. I the future when starting a new thread it is helpful to list the version of PowerChute being used along with the UPS model. 

To configure PowerChute Buiness Edition go to Configuration - Shutdown Settings and set At runtime limit to 30 minutes. When the UPS has less than 30 minutes of runtime remaining it will start the shutdown process. 

LWc%2Bn1sNEZj4d0WXu4TPHw%3D%3D.pngLWc%2Bn1sNEZj4d0WXu4TPHw%3D%3D.png

To prevent the system from restarting before the time needed to restart and power down go to Configuration - Outlet Sequence and set UPS Outlets (main outlet group) Minimum Battery Runtime Required Before Outlet Group Turns On to 1800 seconds.  Again I recommend including the power up time along with the power down time to prevent the system from not having the available runtime to restart and then power back down.

I am basing the times on the system needing 15 minutes to power down and 10 minutes to power up with an added 5 minutes for safety. 

To see the systems runtime go to Smart-UPS 2200 and select UPS status. Runtime remaining will be listed. 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of