PowerChute Network Shutdown with multiple sites

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PowerChute Network Shutdown with multiple sites
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 01:32 AM . Last Modified: ‎2024-03-06 01:36 AM

0 Likes
6
1808
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:32 AM . Last Modified: ‎2024-03-06 01:36 AM

PowerChute Network Shutdown with multiple sites

Is it possible to configure PowerChute Network Shutdown to work with multiple UPS that are in different sites? It seems that I would need to run an instance of PowerChute Network Shutdown in each site to get it working.

I have 3 sites, identical setups, 5 ESXi servers running off of 3000XL's.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-07-01 01:32 AM . Last Modified: ‎2024-03-06 01:35 AM

0 Likes
0
1808
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:32 AM . Last Modified: ‎2024-03-06 01:35 AM

So I'm going to need a seperate vMA for each APC UPS I want to manage??

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:32 AM . Last Modified: ‎2024-03-06 01:36 AM

0 Likes
0
1808
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:32 AM . Last Modified: ‎2024-03-06 01:36 AM

you should be able to but is this a clustering scenario or something? i ask because normally the client should be physically powered by the unit it is plugged into and it doesnt sound like what you have if they are located in different physical spots.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 01:32 AM . Last Modified: ‎2024-03-06 01:36 AM

0 Likes
0
1807
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:32 AM . Last Modified: ‎2024-03-06 01:36 AM

The servers in each site are clustered, but according to the documentation I am to install PCNS on the vMA server and not directly on the ESXi hosts....

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:32 AM . Last Modified: ‎2024-03-06 01:36 AM

0 Likes
0
1807
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:32 AM . Last Modified: ‎2024-03-06 01:36 AM

yes, that's correct.

take a look at this article and let me know if you have any further questions:

1.) go here http://www.apc.com/site/support/index.cfm/faq/

2.) search for FA159784

let me know if that helps you or not.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:32 AM . Last Modified: ‎2024-03-06 01:35 AM

0 Likes
0
1808
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:32 AM . Last Modified: ‎2024-03-06 01:35 AM

Well, it can be done but it is not a good idea after clarifying with one of the PCNS experts. You could install PCNS in a redundant configuration and have UPS at different sites but I am not sure why that'd be a good idea - that would cause shutdowns at sites that have not lost power or possible server crashes

The other option if running PCNS 2.2.4 (cannot be done with 3.X) is install multiple instances (3 instances max) but the instances would only shut down the host and VMs if the you wrote a script to do so. PCNS as an instance only tells the UPS to shutdown not the OS so the scripts would be needed. We don't advise this either.

In your scenario, we suggest installing a vMA on 1 host at each site and installing PCNS on each of those vMAs. Once the vMAs and PCNS have been installed, you can then use the directions and scripts from FA159784 (in the knowledge base) to shut down all the VMs and host at that particular site.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 01:32 AM . Last Modified: ‎2024-03-06 01:35 AM

0 Likes
0
1808
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:32 AM . Last Modified: ‎2024-03-06 01:35 AM

Thanks, that's what I was affraid of. I can't believe it won't support multiple configs.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 01:32 AM . Last Modified: ‎2024-03-06 01:35 AM

0 Likes
0
1809
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:32 AM . Last Modified: ‎2024-03-06 01:35 AM

So I'm going to need a seperate vMA for each APC UPS I want to manage??

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore