PowerChute Network Shutdown and Microsoft Hyper-V

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
BillP
Administrator Administrator
Administrator
0 Likes
1
1040

PowerChute Network Shutdown and Microsoft Hyper-V

This question was originally posted by Michael on APC forums on 11/6/2019


Hi guys

Usually I work with VMware environments and I really like the PowerChute Network Shutdown appliance for VMware because you can do all the fancy stuff like shutting down or powering up VMs in a certain order.

So a while ago a customer asked me if I could help out with Hyper-V and I told him yes for sure. After installing the Software on each of the two Windows Server 2012 R2 Hypervisor hosts I connected both to the UPS. When I opened the management gui of PowerChute Network Shutdown I was suprised though because I could not find the section "host protection" and "vm priorizitation".

I know that there is also Microsoft System Center Virtual Machine Manager (SCVMM) which is more a less like VMware vCenter BUT the customer does not have this.

Questions

1) The situation I mentioned above, is this accurate, so is it true that with Hyper-V I do not have these capabilities?

2) Is there a difference if we would use SCVMM and PowerChute Network Shutdown in terms of more capabilities?

3) If we do not have the same capabilities in general how do you resp. APC advice people with Microsoft Hyper-V to properly shut down VMs in a certain order and start them up again?

Thank you very much for your help

 

 


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
1040

Re: PowerChute Network Shutdown and Microsoft Hyper-V

This reply was originally posted by Bill on APC forums on 11/7/2019


Hi,

On 11/6/2019 8:57 AM, Michael said:

1) The situation I mentioned above, is this accurate, so is it true that with Hyper-V I do not have these capabilities?

Correct.

On 11/6/2019 8:57 AM, Michael said:

2) Is there a difference if we would use SCVMM and PowerChute Network Shutdown in terms of more capabilities?

Not that includes VM prioritization.

On 11/6/2019 8:57 AM, Michael said:

3) If we do not have the same capabilities in general how do you resp. APC advice people with Microsoft Hyper-V to properly shut down VMs in a certain order and start them up again?

 Microsoft offers an FAQ that provides a scripting method. https://gallery.technet.microsoft.com/scriptcenter/Shutdown-AllVmsInRightOrder-1b7431d7

If you run a search on "script shutdown virtual machine hyper-v" you will find many other articles. 

See Answer In Context

1 Reply 1
BillP
Administrator Administrator
Administrator
0 Likes
0
1041

Re: PowerChute Network Shutdown and Microsoft Hyper-V

This reply was originally posted by Bill on APC forums on 11/7/2019


Hi,

On 11/6/2019 8:57 AM, Michael said:

1) The situation I mentioned above, is this accurate, so is it true that with Hyper-V I do not have these capabilities?

Correct.

On 11/6/2019 8:57 AM, Michael said:

2) Is there a difference if we would use SCVMM and PowerChute Network Shutdown in terms of more capabilities?

Not that includes VM prioritization.

On 11/6/2019 8:57 AM, Michael said:

3) If we do not have the same capabilities in general how do you resp. APC advice people with Microsoft Hyper-V to properly shut down VMs in a certain order and start them up again?

 Microsoft offers an FAQ that provides a scripting method. https://gallery.technet.microsoft.com/scriptcenter/Shutdown-AllVmsInRightOrder-1b7431d7

If you run a search on "script shutdown virtual machine hyper-v" you will find many other articles.