PowerChute Network Shutdown VMA 4.2 does not shut down guests machines

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PowerChute Network Shutdown VMA 4.2 does not shut down guests machines
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
123
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 11:31 PM . Last Modified: ‎2024-03-12 12:48 AM

0 Likes
3
843
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:31 PM . Last Modified: ‎2024-03-12 12:48 AM

PowerChute Network Shutdown VMA 4.2 does not shut down guests machines

We've just finished configuring and attempted testing controlled shutdown of the guest machines on an esxi host.

It does not appear to be working for some reason.

We've configured the following conditions for the shutdown to occur.

1) On battery

2) Run time remaining is below threshold. (set to 3600 seconds)

* The UPS only has just over 1 hour run time remaining at its current load. (1 hr 9 min).

* When I tell the UPS to shut down powerchute clients, the host ends up just turning off without shutting down the guests (I suspect). However this tells me that the software is indeed working and connected to ESXi fine.

This is the log from the test case. (At 15:46:58 is when i pulled the power on the UPS to simulate an outage.)

12/12/2017 15:53:19 UPS critical event: RunTime Remaining: Below Threshold.
12/12/2017 15:53:19 The runtime remaining has dropped below the configured threshold while on Battery.
12/12/2017 15:52:49 UPS critical event: RunTime Remaining: Below Threshold resolved on Host 192.168.90.26.
12/12/2017 15:52:49 The runtime remaining back above configured threshold, or input power restored.
12/12/2017 15:52:19 UPS critical event: RunTime Remaining: Below Threshold.
12/12/2017 15:52:19 The runtime remaining has dropped below the configured threshold while on Battery.
12/12/2017 15:49:03 Shutting down Host 192.168.90.26.
12/12/2017 15:48:58 Shutdown sequence started on Host 192.168.90.26 in response to UPS critical event: On Battery.
12/12/2017 15:48:58 UPS critical event: On Battery.
12/12/2017 15:46:58 UPS has switched to battery power.
12/12/2017 15:39:48 Available runtime has been exceeded.
12/12/2017 15:39:20 PowerChute successfully opened TCP port 6547.
12/12/2017 15:39:20 PowerChute successfully opened TCP port 3052.
12/12/2017 15:39:20 PowerChute is attempting to open TCP port 3052.
12/12/2017 15:39:20 PowerChute is attempting to open TCP port 6547.
12/12/2017 15:39:19 PowerChute Network Shutdown version 4.2.0 monitoring started.
12/12/2017 15:39:18 Communication has been established.
12/12/2017 15:38:52 PowerChute successfully opened UDP port 3052.
12/12/2017 15:38:52 PowerChute is attempting to open UDP port 3052.
12/12/2017 15:16:14 Available runtime has been exceeded.

At no point did anything happen on the host or the guests at all. I left it for a solid 30 minutes but no changes. The UPS batteries just went down to 30 minutes remaining.

What could I have configured wrong?

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:31 PM . Last Modified: ‎2024-03-12 12:48 AM

0 Likes
0
841
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:31 PM . Last Modified: ‎2024-03-12 12:48 AM

Hi,

Is the host licensed? PCNS requires the host have one of these licenses Standard, Enterprise, Enterprise Plus

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:31 PM . Last Modified: ‎2024-03-12 12:48 AM

0 Likes
0
841
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:31 PM . Last Modified: ‎2024-03-12 12:48 AM

Hi,

On 12/12/2017 1:35 AM, Terry said:

When I tell the UPS to shut down powerchute clients, the host ends up just turning off without shutting down the guests (I suspect). However this tells me that the software is indeed working and connected to ESXi fine.

PowerChute will tell the host that it needs to power down. The host tells the VMs to power down. See Schneider Electric FAQ FA159688

On 12/12/2017 1:35 AM, Terry said:

At no point did anything happen on the host or the guests at all. I left it for a solid 30 minutes but no changes. The UPS batteries just went down to 30 minutes remaining.

That statement is contradictory to the earlier statement. Does the host not power down or are the VMs not powering down. The PowerChute logs indicates the host is being powered down.

12/12/2017 15:48:58 Shutdown sequence started on Host 192.168.90.26 in response to UPS critical event: On Battery.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-29 11:31 PM . Last Modified: ‎2024-03-12 12:48 AM

0 Likes
0
841
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:31 PM . Last Modified: ‎2024-03-12 12:48 AM

Hi Bill,

Those statements are indeed contradictory; they were two different test cases. (However upon reading what I posted I managed to make it clear as mud.)

To just test to see what would happen if i initiated a shutdown directly from the UPS, i logged into the UPS and initiated a shutdown, as per the following statement.

* When I tell the UPS to shut down powerchute clients, the host ends up just turning off without shutting down the guests (I suspect). However this tells me that the software is indeed working and connected to ESXi fine.

It did indeed work, although I'm fairly sure the guests did not shut down. (that itself would be a vmware issue as per your response).

The log that I posted however, was from testing via simulating loss of power to the UPS. (Pulling the cable).

The log does state that its shutting down the host but nothing happened for half an hour.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:31 PM . Last Modified: ‎2024-03-12 12:48 AM

0 Likes
0
842
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:31 PM . Last Modified: ‎2024-03-12 12:48 AM

Hi,

Is the host licensed? PCNS requires the host have one of these licenses Standard, Enterprise, Enterprise Plus

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of