PowerChute Network Shutdown (PCNS) Installation problem on windows

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PowerChute Network Shutdown (PCNS) Installation problem on windows
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 07:47 PM . Last Modified: ‎2024-03-07 02:00 AM

0 Likes
9
2005
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:47 PM . Last Modified: ‎2024-03-07 02:00 AM

PowerChute Network Shutdown (PCNS) Installation problem on windows

Hello,
I have a problem installing PCNS on Windows. I tried Windows 7, Windows Server 2008 and Windows Vista.
I used the latest Version 2.2.4 of PCNS.

I try to install the software with options "single installation", "install for a single ups".
After entering all needed information, the software tries "Registering with Management Card(s)".
This happens very fast and i can see the client ip in the web interface of the management card.

The problem: After registering, the software trie "Verifying communication with Management Card(s)".
Here the installation process hangs. After a minute comes an error: "Cannot communicate with the Management Card".

I turned my firewall off and i have connected the client directly to the NMC to avoid a network error or something
blocking any port, but the error occurs again.

How can i install PCNS on Windows and establish a connection to the NMC?
Please help me.
Leuaner

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:47 PM . Last Modified: ‎2024-03-07 01:59 AM

0 Likes
0
2004
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:47 PM . Last Modified: ‎2024-03-07 01:59 AM

Glad we were able to help you out. If you need further assistance please let us know.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
Anonymous user
Not applicable

Posted: ‎2021-06-30 07:47 PM . Last Modified: ‎2024-03-07 02:00 AM

0 Likes
0
2004
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:47 PM . Last Modified: ‎2024-03-07 02:00 AM

Yes, I've disabled it and restarted the service.
I also turned of the avast! Antivirus service before a restart of PowerChute Network Shutdown Group 1.

Thanks.
Any ideas?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:47 PM . Last Modified: ‎2024-03-07 02:00 AM

0 Likes
0
2004
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:47 PM . Last Modified: ‎2024-03-07 02:00 AM

can you tell me what UPS model this is and what NMC firmware it is? I know its an AP9606 NMC so for the firmware on that, check under help, about on the web UI for the AP9606 and then in the AP9606, where you found the 603.I or whatever is where the UPS model will be - oh I see you said somethin about Smart UPS 1500 - is that SUA1500, a black tower model or rackmount?

another thing that sometimes causes issues is typos with the subnet masks, gateways, and network adapter binding order.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 07:47 PM . Last Modified: ‎2024-03-07 02:00 AM

0 Likes
0
2004
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:47 PM . Last Modified: ‎2024-03-07 02:00 AM

Yip tower model.
SUA1500I

subnet and gateway seem fine. Have checked on both ends.
How do you mean by network adapter binding order?

I'm also testing with VMware vMA and the pcns version for it.
Can see by the attached image pcnsOnvMAConfigurationWizardConnectionLog.png that the pcns is not receiving from the nmc.

Any ideas?

Message was edited by: lethalduck

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:47 PM . Last Modified: ‎2024-03-07 02:00 AM

0 Likes
0
2004
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:47 PM . Last Modified: ‎2024-03-07 02:00 AM

i didnt not realize you were using PCNS 3.0 which you originally stated 2.2.4. your case has been escalated internally at APC which I saw and unfortunately i believe that the AP9606 was mistakenly reported as supported by PCNS 3.0 when it isnt really (which we will update the documentation). thus, i think APC support will be posing to you a solution internally to remedy this.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 07:47 PM . Last Modified: ‎2024-03-07 02:00 AM

0 Likes
0
2004
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:47 PM . Last Modified: ‎2024-03-07 02:00 AM

I've had a similar problem.
nmc AP9606 with 601.3.I
pcns 2.2.4 currently on XP sp3 running under my admin account.
Firewall off, antivirus off.
Although firewall ports look fine.
See pcnsWinXpNoComms.png
Can't connect to nmc 192.168.0.70
See pcnsWinXpNoComms1.png
Have checkd user, passw and passphrase are all the same on nmc and pcns.
Have checked default gateway, netmast, DHCP server are all correct on both nmc and pcns.
When pcns is installed it adds it's IP to the nmc Smart-UPS 1500 -> PowerChute -> Configured IP Addresses, so there is obviously some form of communications occurring.
Can ping the pcns machine from the nmc using the pcns machine mane and the correct IP is returned. visa versa is also file.
Ideas?

Message was edited by: lethalduck

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:47 PM . Last Modified: ‎2024-03-07 01:59 AM

0 Likes
0
2004
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:47 PM . Last Modified: ‎2024-03-07 01:59 AM

have you tried to disable the firewall completely and restart the PCNS service, just as a test?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:47 PM . Last Modified: ‎2024-03-07 01:59 AM

0 Likes
0
2004
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:47 PM . Last Modified: ‎2024-03-07 01:59 AM

Hello Leuaner,

During the installation of PCNS it will ask you for a username, password and the authentication phrase. Would you happen to know if you have changed the authentication phase on the network management card? The default authentication phrase is admin user phrase. Can you re-type the phrase on the software installation and on the network management card? To change the phrase on the card you need to login to the card and click on UPS-PowerChute-Configuration.

Make sure as well that the PC and the NMC can see each other. Also, prior to changing the authentication phrase it would help if you could check if you have other PCNS clients communicating on the same card. If you will change the authentication phrase on the card and you have clients listening to it, you'll loose communication with it.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 07:47 PM . Last Modified: ‎2024-03-07 01:59 AM

0 Likes
0
2004
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:47 PM . Last Modified: ‎2024-03-07 01:59 AM

Hello,

I solved the problem partially.
I have updated the management card to the last version v5.1.3 and downloaded th e latest
PCNS v2.2.4. Now i can establish a connection from my Windows server 2008 computers
with firewalls turned off.
With my Windows 7 desktop pc i only get a connection if i turned my anti virus software
"trend micro office scan" off. The firewall is turned off too.

I only need the PCNS for my 2008 servers, so i didn't make more tries with my pc.

Thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:47 PM . Last Modified: ‎2024-03-07 01:59 AM

0 Likes
0
2005
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:47 PM . Last Modified: ‎2024-03-07 01:59 AM

Glad we were able to help you out. If you need further assistance please let us know.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of